Main air vent location
Hello folks, I've got a bunch of mains that need venting and I'll be using B&J big mouths. I understand that it's recommended they be installed 12" before the end of main to protect them from water hammer. Several locations look basically like the photo below I'm wondering if I'd be ok doing it this way:
This I can do myself without paying someone to cut and thread in a Tee in the existing pipe. With the number of lines I have, this is significant savings. I should add that I don't have any water hammer, the boiler is operating at 1.5psi and the pipe will all be insulated.
Comments
-
-
Yes. 2 pipe all parallel flow mains.
0 -
-
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I'd run it like this. You will get the appropriate pitch for free if you do it this way, and it's plenty to protect you from the commonly overstated risk (in my view) of "damage from water"
Also note that Big Mouth vents provide a LOT of venting and may be overkill. They require quite a bit of steam to get heated enough to close compared to Gorton, for example, due to their rather massive…mass.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
If you have no water hammer and the rads heat fine, what is it you are fixing. Two pipe systems will vent into the condensate side through the steam trap. Maybe you don't need 'em?
Steward to 1923 Spanish revival near Chicago - 2 pipe steam 650 EDR shiny new Peerless 63-06
0 -
... aside from those being the skinniest steam pipes I've ever seen.
Steward to 1923 Spanish revival near Chicago - 2 pipe steam 650 EDR shiny new Peerless 63-06
0 -
Certainly appropriate to feed a single 2-pipe radiator however
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Thanks Jamie, I appreciate the sanity check. I'll be sure to keep things pitched for drainage.
0 -
-
Yep that's a lot of main!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
There's no hammer but the boiler needs to run for about 3 hours to get heat to these 2 rads which are at the end of a 270' main. I've rebuild the traps with Tunstall capsules which needed to be done but slows venting even more since they don't vent as quickly as the original trap elements. This system started out burning coal and nobody thought to add mains vents when it was converted.
1 -
-
Are you sure this is just ordinary 2 pipe steam? Many vapor systems needed to vent the mains in to the returns through crossover traps and have the only vent to the atmosphere be at the boiler near the boiler return trap.
0 -
I can't say what it was in 1910 when it was coal fired. The mains vent into the returns through appropriately sized F&T traps. The layout of the building (long but not tall with rads, in some places, on the same level as the boiler) necessitates pumped returns with vented tanks. There are some gravity returns that are vented at the boiler feed tank. No sign of a boiler return trap ever having been installed. Regardless it's 2 pipe now with regular pressuretrols, standard radiator valves and thermostatic traps etc. I'm sure it worked great when some forgotten soul would light the coals at 5am so by 8 all the air had worked its way though the traps and the system stayed under pressure until the boss went home.
0 -
Thinking on this a bit more, I wonder if those condensate returns are a bit problematic? They may have been okay to be that skinny when new, but how clear are they now. And the apparent lack of pitch makes me think they may be nearly full of water a lot of the time (and thus corrosion products).
Have you opened any of these lines and tried to blow through them (with compressed air)? I have some unpitched dry returns i suspect of constraining my venting on certain radiators.
Steward to 1923 Spanish revival near Chicago - 2 pipe steam 650 EDR shiny new Peerless 63-06
0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 75 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 394 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements