Boiler short cycling?
Dianapagu
Dianapagu Member Posts: 15
edited October 31 in THE MAIN WALL
Hi All,
Im the past ive found the experts on this forum very helpful. Hoping again for that knowledge. As the weather starts to get colder its that time for the boiler to turn back on. In the past we've had our issues like not turning on completely leading to a replacement of the ignition box and pilot. This was 2 years ago. This time around we think its short cycling since it does turn on for a 1-2 min run and then it beeps calling for heat , turns on for a under a 1min then off/on all until the thermostat reaches its temperature.
This is a Williamson boiler to a one pipe system , steam gas boiler. We had someone come by to take a look but they didnt feel confident. Still suggest the ignition box ,pilot and gas valve be replaced
So im wondering does this somewhat sound correct. Trying to research short cycling on steam boiler and get lots other trouble shooting suggesting before having to do a complete replacement. I tired uploading the video but its too big. But any other advice would be much appreciated.
  • neilc
    neilc Member Posts: 3,096
    post a general picture, floor to ceiling, showing the controls side,
    post a closeup on the controls and site glass, and gage while it's firing,
    low water cutoff, pressuretrol, may need service,
    known to beat dead horses
    EdTheHeaterMan Member Posts: 11,494
    Does the flame light? YES = the ignition box, pilot and gas valve is working.
    When it goes off you need to determine what is causing it. There are several things that can cause the flame to go out so quickly after it starts up. Most of them are electrical. Are you handy with an electrical meter? I can talk you thru the diagnosis process.
    Jamie Hall Member Posts: 26,705
    Before you even start thinking about the gas valve and ignition… there are a number of other things that could be the problem. Poor main venting (or non-existent)? (suggested by the initial short run 1 to 2 minutes is way too short for a starting run!). Low water level and surging causing the LWCO to trigger. Poor of otherwise inadequate radiator venting. Even poor near boiler piping… and that's for starters.
    You need to begin by figuring out what is shutting it off.
    EBEBRATT-Ed Member Posts: 19,285
    Short cycling can have many causes. If it is ignition /flame proving issue some boilers will try to star 4-5 time before they lockout, so the flame can light…go out…light …go out.etc.
    Other than that short cycling can be caused by the low water cutoff not enough water in the boiler or a surging water level.
    Also could be the pressure control, it could be adjusted wrong or you could have a plugged pigtail.
    There are other causes but those are the most common.
    Dianapagu
    109A_5 Member Posts: 3,316
    If you post your video on a web site that hosts videos and then post the link to it here.
    Is the short cycling issue new to the system, that is it never did that before ?
  • Dianapagu
    edited November 4
    All things I have also thought of. I did notice the radiators closest to the boiler were not heating while the others furthest did. I dont think i have an electrical meter around but can definitely get one. The ignition box / pilot was replaced only 2 years ago unless thats how long they only last? Low water meter light isnt lite , smallest dim but i heard that was a "normalish" feature on Williamson. But the boiler is definitely full. Has it done this before? Not like this i want to say , only one winter we didn't get heat at all which is why I had an emergency service call done bc it was middle December and a weekend unfortunately but pilot wouldn't go off completely and company that serviced changed the ignition box n pilot for that reason.
    Short video link here to view.
    What looks like the main burner drops out and intermittently the pilot stays lit and/or goes out then it restarts again. I'd verify that the 24 VAC to the Spark Ignition Control module is consistent and stable when the burner drops out. If the 24 VAC is good the Spark Ignition Control module is probably bad again. However before changing the module I would verify the flame sense rod is clean and there is 24 VAC from MV/PV to PV only when the pilot is lit.
    Dianapagu
  • neilc
    loose wire, bad ground, somewhere there,
    all spades snug? all screw type wire terminals tight?
    somebody's loose,
  • Dianapagu
    edited November 1
    @109A_5 today we tried to clean the pigtail, it wasn't an easy one to take of so had to get a bit creative to get some slug out. Wiped burners off, not too dusty. This boiler doesn't have the traditional flame sensors I see when I search for an image. Its just the pilot like the diagram you added.
    @Jamie Hall one of raditor closest to the boiler (#4airvent) wasn't getting warm at times. So I took it off when no heat was on valve closed and its slowly heating up where as the others on my floor #5 (lr/dr) already full of steam. Im going to replace the #4s and retry just so all radiators have new valves.
    Uploaded another video from start of thermostat calling for heat to view. More of less the same as the first video. https://youtu.be/4rQdbYQ2OZU?si=XZoSdcA-4M3gTOtx
    Sometimes the ignition rod at the pilot is also the flame sensor. All depends on the ignition module and the boiler setup. Boiler model ? The high voltage will jump through contamination but the much more sensitive flame detection may not work correctly.
    It seems the pilot is staying lit when the main burner is going out, which seems to me as odd behavior from the ignition module. The due diligence with a multimeter with a logical process that actually verifies the ignition module is actual defective should be done.
    Also verifying all the electrical connections are physically secure should also be done.
    It now seems like a similar failure to when the old ignition module was changed, which makes me wonder if something else is going on that was missed back then.
  • Dianapagu
    edited November 1
    @109A_5 some pictures to view. If its definitely the ignition module then ill have to start calling around for quotes/diagnostic but I think most things to troubleshoot have been exhausted. We're also going away next week and although it heats in the home may not be able to risk it giving out while we're away with tenants around.
    " If its definitely the ignition module then ill have to start calling around for quotes/diagnostic but I think most things to troubleshoot have been exhausted. We're also going away next week and although it heats in the home may not be able to risk it giving out while we're away with tenants around. "
    Well without doing the troubleshooting due diligence it is just a guess. The ignition module is easy to change. Shut the power off, looks like a Philips screwdriver and maybe pliers for the electrical connections.
    edited November 1
    This failure in the first video and around time stamp 6:23 on the second video remind me of a flame proving signal being lost. More than likely there is a ground path failure in the Flame Rectification path from the UTEC ignition control thru the flame back the the UTEC control That is common when a burner is connected to the rest of the boiler the way your burners are fitted. To be sure the ground path from the burner to the UTEC control is not corroded or compromised I run a physical ground wire from the pilot burner to the GND (BURNER) terminal of the UTEC Control.
    Here is an illustration of the wire in place
    This wire will eliminate any fault with the ground connection present from the burner to the control
    EBEBRATT-Ed
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,313
    Another common cause of short cycling is the thermostat. Occasionally the stat is bad, but often its not properly set up for steam or the electronic programming simply doesn't know what to do at light loads. I just changed out my Digital stat (lots of short cycling in 40F + outdoor temps on a high mass boiler and system) for a simple mechanical stat and the short cycling is now gone. Long burn cycles and I still have stable air temperatures. Old fashioned heat anticipators in mechanical stats often are much better than expensive digital stats.
    I would think if it was a thermostat issue or a poor ground issue the pilot would always go out also, which it does not if you look closely in both videos. Maybe the dropout and recovery is too fast for the pilot to go out every time. Troubleshooting due diligent testing would prove what the actual issue is.
  • Dianapagu
    A few updates. With what we could and had available for troubleshooting. Cleaned pigtail somewhat, only bc ours was on pretty tight and didnt want risk any force. Got creative and used a spray bottle head and straw to siphon some out. Not terrible , but yes somewhat dirty of course. Tried to use our battery powered air duster around little crevices that couldve be covered in dust,touch and push in wires incase anything seemed loose.Called for heat did a little better than last video but still did the same thing just lasted longer in between beeps. Instead of short 30sec to 1 it , run up to 5 mins start then 1 to 2 every in between. Still hadnt added the #4 vents to those front raidtors that didnt heat up firag.So no go but better?
    Got hands on two #4 vents for those front radiators. This time found this video , which was great knowledge. Got us thinking, for sure. We dont the multimeter but still was worth the shot to try. Only thing we weren't confident on was how to remove the pilot to try to give it a better clean to the rod like Ed mentioned. But found another video and will try today. But before this. I checked the nut , like mentioned at min 6:19. It had a little give so wasn't as tight. I used our air duster on the orffice of the pilot, from the angle that I could. With new #4 vents installed, called for heat again. It did way better! At Start lasted 10 mins until it started beeping again but again in between beeps were 2 mins long. Then I realized I didnt leave one of raidtors valves open from the recently changed #4 air vents. But overall did much better , now it was very late at night so thermostat was satisfied quickly bc I only called it for heat at a few degrees more than what it was. So for over night I opend the valve to that radiator that I forgot and left it for next day, to try again and try to clean the pilot rod better. I wasn't able to watch it this morning when it calls the schedule since i have it set for 4am to 10am. And we didn't get up on time , its the weekend after all. So going to aim again and get try to clean the rod before the next schedule at 4pm today. Found another video on how to change the piolt out and try to follow the cleaning of the piolt orffice and clean the rod a bit with some sandpaper closest to steel wool and use our air duster to blow anything out. Also my father in-law may have a multimeter so ill be asking him about that today. So hopefully something comes from all this and hoping its not like the ending of this video about cracked heat exchangers .
    AC Service tech has excellent videos
    Dianapagu
    More and more I'm thinking that while you may some electrical probems, your main problem is that you either have no main venting at all or it's woefully inadequate. Or just not working.
    I'm not concerned abort radiator vents — I mean main venting.
  • Dianapagu
    @Jamie Hall appreciate the feedback. Everyone's given good look outs. Unfortunately father in law didnt have a multimeter. But we tried to clean the pilot rod a bit more , emery cloth was not an easy find unless ordered so tried with some fine sandpaper. This morning it called for heat ran the full 10 mins again before it started beeping for a 1-2 min, it did it twice then ran again for 10 mins and so forth. We're in Queens ,NY so thankfully the weather isnt freezing yet, so calling for heat will be minimal for now or atleast until we leave for vacation and its too late to cancel those plans. Hope we can get someone in time to consider coming in quickly. For the 5 years that we've lived in the area and the home the plumbing companies we've dealt with have been just ok, but always ready to just replace every part rather than minimal diagnostics. More and more im realizing how the art of steam boilers is becoming a lost form with folks. I guess eventually we'll consider getting an updated boiler since this one was installed in 2017 it looks like from some signatures left on the side of the boiler , hahaha.
    There are several really good steam folks who service your area. Try @JohnNY . Unfortunately, they're really busy and not cheap…
    Dianapagu