New NYC steam radiator inspection law - what does it mean?
bipbap
bipbap Member Posts: 233
I just saw this new law pass in NYC requiring steam radiators to be inspected after there has been some horrible accidents in the past:
https://www.cbsnews.com/newyork/news/ben-zs-law-nyc-radiator-inspections/#
  My understanding was besides the vent and the valve, there isn’t much that can go wrong about the radiator itself, assuming the boiler is operating properly.
Isn’t the radiator really just a transporter of the heat and any issue that could be dangerous is really a boiler problem not a radiator problem?
What does a radiator safety inspection look like? Aside from making sure the vent is attached properly.
  • Pumpguy
    Pumpguy Member Posts: 794
    I wonder if the inspector would even know the difference between a one pipe and 2 pipe system, where on one a radiator vent would be needed and the other it would not?
    And what would the inspector think if he saw radiators on a Paul air line system, or all the various vapor systems?
  • bipbap
    it doesn’t even seem to outline what the inspection consists of or what exactly should be inspected or even if it has to be done by a licensed plumber or just a homeowner.
    EBEBRATT-Ed Member Posts: 19,908
    This is the "green energy" people trying to get rid of steam and fossil fuel
    Long Beach Ed
    The ispection will be:
    walk in the room. yup that's a radiator and then walk out.
  • bipbap
    Yeah it feels like what safety measure will this satisfy?
    Based on the accidents which happened, is it ever the radiator at fault rather than the boiler?
    109A_5 Member Posts: 3,692
    " His room steamed up to almost 300 degrees "
    How is this even possible.
  • ratio
    ratio Member Posts: 4,203
    Sounds like the common justification: "Something must be done! This is something, therefore it must be done!!1!"
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,690
    edited October 2025
    Part of this is educating the tenants. I’ve seen many times in NYC where tenant will turn the air vent upside down to stop the overheating. Many times it’s hanging by a thread. High steam pressure (typical) can knock the vent off. Steam fills the room, which most of the time will have a closed door so the kids can sleep. I’m very glad they’re finally doing the inspections.
    Retired and loving it.
    CLamb
  • bipbap
    edited October 2025
    Thanks so much for chiming in, Dan.
    So as a homeowner, what exactly should I look for or what do you believe this inspection should consist of?
    Making sure vents are properly secured? No steam escaping out of vents? Anything else?
    And would you say that if the system is being run at the appropriate low pressure, then there should really be no danger to worry about on the radiator end of things?
    The language I’ve seen about this law doesn’t seem to say lay out exactly what to inspect or be looking for or even if it needs to be done by a homeowner or a licensed plumber.
  • DanHolohan
    Thanks. Yes to the vent and the supply valve. Also be sure a child’s bed is not too close to an uncovered radiator. In NYC, little kids have fallen out of bed and gotten trapped between the side of the bed and the steaming radiator. It’s horrible.
  • ARobertson13
    ARobertson13 Member Posts: 128
    This is just a law requiring what would be called proper practice. I tell my Coop and clients of mine that there must be a check of radiators and a steam on test prior to the heating seasons start. No responsible building manager, owner or property manager should have to be told this. Several years ago, a steam vent on a radiator came off and filled a small bedroom with steam. Fortunately, the person who normally sleeps there was not present. This person is know to be under the influence. He could have died easily. The vent was not properly attached. The vent treads were not NPT 1/8 standard and someone 'Made it fit". I deep tapped the radiator vent hole and changed the vent. Legally, unless I could prove that there were inspections and tampering occurred just after, my Coop and I as an engineer, would be liable. All of the radiators supply valves and radiator vents and master vents are inspected in my Coop. You cannot trust the shareholders or tenants. Not only do residents tamper with radiators an associated equipment, but some "real men of genius" have installed their own radiators and TRVs.
    So what happens if the radiator is inspected and is passed as compliant and then the tenant adds a TRV or messes with the vent and causes a problem? How do you prove it or point the finger? Take a time stamped picture of every radiator?
    Steam has been around for 140 years
  • bipbap
    edited October 2025
    Dan, if a valve or pipe fully cracked or a vent did come fully off, but the system was running properly and was at the appropriate low pressure (like .5 or 1lb pressure?), would it still be very dangerous in that room?
    I’m just curious what would happen in this situation.
  • HydronicMike
    HydronicMike Member Posts: 295
    Funny you think they may actually go into the rooms.
  • DanHolohan
    @bipbap if the bedroom door is closed the steam will displace the air. Much depends on how long this goes on before anyone notices. Kids have died from this in NYC.
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,550
    I am 100% behind safety measures. Safety first, always. But let's just walk ourselves off the ledge a bit. Many more kids have died from tricycles, and cribs, and pillows, and dogs, and window shade chords, and .......…, then from steam radiator related issues. I'm not even sure if there are five documented cases of kids dying from Steam related Burns or asphyxiation. And steams been around for an awful long time
  • DanHolohan
    I’m thinking that if one kid doesn’t matter then none of us matters.
    Dave in QCAWaherMad Dog_2Big Ed_4
    Jamie Hall Member Posts: 27,014
    The whole question — of which this is a part — is one of balancing a known risk (with widely variable consequences and level of hazard) with variable capability of users to understand the risk and how to mitigate it with varying desirability of reducing the risk by government action and possibly restriction or regulation.
    And there is no easy answer. There isn't even any one answer! For those of us who have been around for a while and been observant it is really fascinating to see what risks were tolerated and how that perception has changed over the years.
  • ARobertson13
    As I stated, all of the radiators are inspected in my Coop and other buildings that are clients of mine. Also, I take pictures and note the type of vents and their condition. You as owners / Management should protect yourselves. I forgot to point out that the incident in my building where the vent came off, the pressure was above 3psi. There really is no excuse for this happening.
  • STEAM DOCTOR
    Of course every life matters. But as Jamie said, where do we draw the line? Should kids only be fed the bare minimum of food, because kids sometimes choke on food. Should cars be banned, because people die in car accidents? Should every car seat be inspected, by a government official, every time a kid is taken for a car ride? Should the government be checking the wheels on every kid's bike and tricycle? Should the government be checking everyone's medicine cabinet, to make sure the containers are closed properly? Should the government banning or restricting or inspecting the pets in every home that has a kid?
  • bipbap
    I've had just the opposite experience. As a rambunctious teenager the dining room vent was broken off the radiator. We (I) did not repair right away, may have went for weeks or longer until the boiler water consumption became annoying (manual fill). The steam coming out was no greater than a lazy tea kettle boiling, no one felt threatened.
    Come to find out decades later this house heats just fine at no more than 2 inches of water column (0.072 PSIG). Maybe the issue is not so much the radiators and vents but the Boiler / EDR sizing and the boiler pressure being too high. Which the residences usually have no control over.
  • STEAM DOCTOR
    And inspections don't guarantee safety. Dan references such a situation in one of his books, where a babysitter removed an air vent, because the room was not warm enough. The child died from lack of oxygen. Unless the inspector happened to be there at that moment, it's fairly unlikely that inspection would have made a difference. In all likelihood, that young teenage babysitter, had seen her parents and other adults, doing the same thing, without adverse results.
  • STEAM DOCTOR
    And just for the record, I am the safety nut of my family. Was going on an outing with extended family. One adult family member refused to buckle their seat belts. While I was the driver. I refuse to drive without that family member buckled in. He refused and got out of the the vehicle and did not talk to me for many months afterwards.
    HydronicMikeCLambGrallert
  • ARobertson13
    First of all, As a manager and owner, I do not want anyone to get injured or die because of a problem with equipment on my property. This applies to the side walks, fire escapes, roof access, gas and combustible air ect. I make it clear to all residents, they may not modify alter or disconnect anything attached to the radiator. It is in the lease. They are allowed to turn the supply valve off. The inspection that I perform is a steam on inspection. I will verify that there are no leaks from the supply valve or vent openings, or the radiator itself, there is proper tilt allowing condensate to flow back to the supply valve, the radiator is on a stable flooring, the vents open when air is forced up and close when they are heated by steam. I will then take a picture of the radiator. If there is a master vent, verify that it is operating. Each radiator has a ID: example: R451 R = radiator, 4 = floor, 5 = line, 1 = riser pipe left to right. This will take time but resolves other issues like balancing.
    PC7060
    pecmsg Member Posts: 6,894
    and how many steam radiators are we talking about just in Manhattan?
    The city does have that kind of manpower.
  • DanHolohan
    edited October 2025
    Each building has a superintendent. They can do what @ARobertson13 does.
    Waher
  • mattmich
    mattmich Member Posts: 221
    » The steam coming out was no greater than a lazy tea kettle boiling,
    Which is what usually happens in a single-family home.
    But an apartment building can easily build up pressure if the balance isn't right and then it gets dangerous. I wasn't even aware of this risk but it makes sense.
    Is it clear from the legislation that this only applies to single-pipe steam? I'm not sure what would be inspected on a two-pipe system.
    I also have to wonder if an education campaign wouldn't be more efficient. As has been pointed out, taking off or breaking off a vent takes seconds.
    On the other hand, the co-op or building owner has a vested interest in inspecting or informing the residents. Who the heck knows steam in 2025 — even if you live with it? I didn't know nuthin' until my system bought the farm…
    cheers -matt
  • CLamb
    CLamb Member Posts: 347
    That would require a steam pressure of over 50psi. I'd be very surprised if there was that much pressure in the radiator. Nevertheless, the law should've included a maximum steam pressure for the system.
  • CLamb
    edited October 2025
  • DanHolohan
    edited October 2025
    Thanks for sharing your thoughts with us, Ed. I think that if this law will protect one kid then it’s worth it. These little ones are innocents, and our country’s future. If they don’t matter then none of us matter. I say this because I am old and have had much time to think about such things. Kids need adults to care about their safety. They really do.
    Thanks for always taking the time to care enough to share your thoughts with us, Ed. Respectful dialogue is what this place is all about. Thanks. 👍
  • STEAM DOCTOR
    Why only English and Spanish? There are literally a few hundred languages spoken in New York City. If I remember correctly, the tenants involved in the most recent incident, were non Spanish speaking, foreign born residents.
  • STEAM DOCTOR
    Bit of correction. About 800+ languages spoken in NYC
    The way I see it, it may push tenants with children to rent in a much worse environment for their children. The end result may be a greater loss. Time will tell.
    Long Beach Ed
  • ARobertson13
    To All,
    This law which is ID as 27-2056.21 in the NYC administrative code passed by the City council by a super majority for the mayors approval does not say:
    1 Inspections are to be done annually 2 Inspectors must be master plumbers
    The law which is very likely to go into effect if the mayor decides to veto it or not does say:
    1 Inspections are to be done semi annually 2 Inspectors can be: a licensed master plumber, high-pressure boiler operating engineer or stationary engineer, oil burning equipment installer, mechanical contractor, building superintendent, engineer or stationary engineer, oil burning equipment installer, mechanical contractor, building superintendent, heating plant technician employed by the New York city housing authority, heating maintenance worker employed by the New York city housing authority, an individual working under the direct and continuing supervision of a licensed master plumber, an individual working under the direct and continuing supervision of a licensed high-pressure boiler operating engineer or stationary engineer, an individual working under the direct and continuing supervision of a licensed oil burning equipment installer, or an individual working under the direct and continuing supervision of a mechanical contractor that conducts inspections of steam radiators pursuant to this article.
    There is a difference between proposed legislation INT 925 and what the council voted on.
    Grallert
  • CLamb
    Sorry about that. I posted a link to the bill as initially proposed instead of the one finally passed. The bill finally passed can be found here
    While I agree with you in principle, @DanHolohan , I have one other — and it's major — concern. If this regulation is necessary — and it may be — it points to two underlying problems. The first is that the people who own and maintain buildings are assumed to be incompetent to perform proper maintenance. This may be true… but the assumption is unfortunate. The second, however, is a deeper problem: it was one assumed that the parents had an absolute and unbreakable responsibility to care for their children, to teach them well (in many different ways!) and to protect them from harm..
    This relatively minor regulation is just another one saying that the parents can outsource that responsibility to "society" without consequence — indeed that it is preferable that they should do so.
    Not sure I like that.
    ChrisJpecmsgGrallertLong Beach Ed
  • DanHolohan
    Good point, well made. Thanks, @Jamie Hall
    Grallert