Type K copper pipe
Comments
-
Hi, Maybe a dumb question, but do you have a water quality report for your water? I ask because if the water is agressive enough to damage solder, I'd be concerned about what it will do to copper. Some sort of plastic piping might last longer, even if it means putting it in conduit to prevent damage and to make it far easier to replace if ever needed.
Yours, Larry
3 -
-
I looked on the Harris web site at their brazing rods. I couldn't find any information on whether it is allowed to use on drinking water. It contains copper, silver and phosphorus.
I couldn't find that it is NSF approved.
You could Google Harris and call them
0 -
-
Harras Stay Brite #8 is NSF Approved. It is a low temp solder not brazing a rod.
0 -
Code does not allow you to bury a soldered line regardless, so it would need to be brazed.
That said, I'd use either hammer flares or pack joints or similar. That's what's typically done on water service lines.
https://www.supplyhouse.com/Legend-Valve-313-214NL-3-4-Pack-Joint-CTS-Union-T-4301NL-No-Lead-Bronze
I even used one in my basement rather than soldering it because it seemed like a really good connection and could easily be worked on. It's a compression joint with a very thick heavy rubber gasket and a metal clamp that secures the pipe. I believe they're called pack joints because they used to use lead packing.
These aren't cheap cheesy compression fittings, they're literally what water companies use for this work.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
How much copper -K- type tubing will you need for your hose? If you need to make a joint, consider using a compression joint suited for a buried water supply, or better yet, a full length of tubing with no joint at all.
0 -
You can get them in 100' rolls.
0 -
Thanks for the help.
0 -
Unfortunately i live on a hill. the pipe goes straight out but has to go down somewhere to meet the shutoff at the curb
0 -
Would type k soft be ok for underground?
0 -
and can type k hard be hammer flared?
0 -
if it is in a roll it is soft copper. you can anneal it with a torch if you need to.
0 -
-
Yes it can me flared
0 -
what size tube? Above 1” it can be gnarly to handle, roll out kink free
Sweat fitting don’t work great as coiled soft copper is not perfectly round
Get the correct flare tool, they drive with a small dingle jack easily. You do not need a flare bar
Ream the burr after you cut the tube.
Put the nut on first😮
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks. Is plastic a option for under ground?
0 -
plastic is probably the best option for underground. unless you're an electrician.
0 -
-
Far superior to copper, as I said a few posts earlier. There really is no excuse for installing copper pipe for underground water service, at least in my opinion, and hasn't been for decades (I started specifying it and using it for well lines somewhere around 1960…)(and some of those lines are still in service; haven't had one actually fail yet that I know of)).
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
the vast majority of underground water service pipe I sell is the blue SDR9 water service poly pipe. it's sold in either a copper tube size, or iron pipe size variant, need to know which you get so you know the proper fittings to buy (cts or ips) you can use the brass water service fittings, (commonly called Ford fittings, though Ford is a brand many make them!) and if you are using those compression style ford fittings you need to use a stainless steel stiffener insert. If it were mine I would only want a connection made underground at the water source, and the next connection in the house, I would do what I could to get a roll long enough to make the whole run with no couplings, not that there is a pattern of leaks I just don't like buried couplings if they can be avoided.
1 -
Starting to sound like plastic might be the best bet for my situation. Didn't want to go that way for health concerns. I heard chemicals can leach into the water. Can you give me more information on the fittings? I should have no problem getting a straight run with no connections between my basement and the street.
Thanks
0 -
Probably more copper leaches out of the copper than anything from the plastic though it is sub parts per billion amounts in both cases.
0 -
That main thing with plastic is that it be NSF approved. If it is — it's pretty free of anything leaching out of it. Polyethylene — which is what you'd be using — hasn't much of anything to leach anyway.
Copper. depending on the pH of the water, will leach varying amounts of copper into your water. Is this a problem? Not that I know of from a health standpoiint.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
Thanks. Great info. I got it about the CTS or IPS. Just a little more info on fittings and I should be good.
0 -
-
I think in most jurisdictions it is only required for gas but it is still a good idea.
0 -
Polly Ethilean (PE) is a great choice—no need to use type-K- copper. Maybe use 160# or greater rather than the standard 100# PE
0
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.6K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 48 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements