Neg subcooling

I was doing a p.m. on my year and a half old unit. it's a Grand Air 3 and 1/2 ton. I have a normal suction pressure slightly high superheat and a negative subcooling. Head pressure is also low.
The system is cooling perfectly.
123.3 psig
17.2 SH
42.1 VSAT
59.3 SLT
74 ambient inside
227.0 PSIG
-13.3 SC
77.3 LSAT
90.6 LLT
87.7 Ambient outdoor
I did a pump down on the compressor. it would only go to 4 PSI. At 40 psi the compressor started to become noisy and rattled.
I am leaning towards a week compressor or a bad TXV. Your thoughts would be appreciated
Mike
Comments
-
Impossable!
4 PSIG is unrealistic for an A/C compressor
0 -
So isn't that how you store refrigerant in the condenser. I have pumped down a lot of units and always reached 0 psi with the liquid line service port closed.
I am not understanding what you mean
0 -
The bulb for the TXV is in the correct position and insulated? Any static pressure readings? Fan on low speed, or a high MERV filter?
0 -
The bulb is insulated and in the right position. I haven't taken a static reading at this point. The fan is on high speed. I opened all returns and removed filters.
I am running a 18.5 degree split
0 -
Your not supposed to pump scroll compressors down that low and according to some they shouldn't be pumped down at all which I don't agree with.
0 -
are you using the right chart or scale on the gauges?
0 -
A/C compressors especially scroll's will only pump down to a determined deferential pressure at which point a safety opens.
0 -
Im using sman 482 guages
0 -
Not sure how the readings you say you have are possible.
0 -
-
You cannot have Negative superheat or subcooling.
How do you cool the liquid line Below the ambient temp? The pressure will respond accordingly.
0 -
Exactly the problem. I have never seen this before.
0 -
Yet, you are saying it is cooling fine, so all is good.🤷♂️
0 -
look for a restriction!
Where are you taking the measurements? Pictures
0 -
-
If a scroll goes negative in the can—not necessarily at the suction port—the winding may start to arc over. You can hear it popping inside.
I've seen negative subcooling and superheat on digitals before. Most of the time, it's because the unit isn't charged properly (especially on microchannel coils), or the digital was set to the wrong refrigerant.
0 -
The gauge is saying the saturation temperature is 10* below ambient, then it warms up to a few degrees above the ambient as it goes thru coil! ? ! ? Guess I am missing something…
0 -
Is that condensation on the high side of gauge set or just the way the surface looks on pic?
0 -
-
-
It's straight cool. Guages are a month old.
Never pumped the compressor into vacuum.
It's not condensation just a glare from the picture.
I just hooked up my old sman 380 to verify that there's not an issue with the new guages. I'll let you know.
At this point I'm leaning towards an internal issue with the compressor or a restriction at the txv. Checked the drier is not restricted
0 -
Okay update. hooked up my old s-man 380s got normal subcooling 9. Which told me my new 482s had a problem. So so I did a factory reset on my new gauges and got correct readings.
I would not haveI would not have guessed that a brand new set of gauges would be doing that. That explains why I never seen settings like that before.
My thanks to everyone that contributed.
1 -
-
I totally agree. I have been doing this for a while and have never seen it. I wouldn't think that a set of gauges out of the box would do that. My old s-man 380s were completely reliable never failed me. Only replaced them because the display is wonky. Thank you for your help
0
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.6K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 47 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements