Neg subcooling
5earlys
5earlys Posts: 8
I was doing a p.m. on my year and a half old unit. it's a Grand Air 3 and 1/2 ton. I have a normal suction pressure slightly high superheat and a negative subcooling. Head pressure is also low.
The system is cooling perfectly.
123.3 psig
17.2 SH
42.1 VSAT
59.3 SLT
74 ambient inside
227.0 PSIG
-13.3 SC
77.3 LSAT
90.6 LLT
87.7 Ambient outdoor
I did a pump down on the compressor. it would only go to 4 PSI. At 40 psi the compressor started to become noisy and rattled.
I am leaning towards a week compressor or a bad TXV. Your thoughts would be appreciated
Mike
    pecmsg Posts: 7,634
    edited September 2025
    Impossable!
    4 PSIG is unrealistic for an A/C compressor
  • So isn't that how you store refrigerant in the condenser. I have pumped down a lot of units and always reached 0 psi with the liquid line service port closed.
    I am not understanding what you mean
    HVACNUT Posts: 7,785
    The bulb for the TXV is in the correct position and insulated? Any static pressure readings? Fan on low speed, or a high MERV filter?
  • The bulb is insulated and in the right position. I haven't taken a static reading at this point. The fan is on high speed. I opened all returns and removed filters.
    I am running a 18.5 degree split
    Your not supposed to pump scroll compressors down that low and according to some they shouldn't be pumped down at all which I don't agree with.
    are you using the right chart or scale on the gauges?
    pecmsg Posts: 7,634
    A/C compressors especially scroll's will only pump down to a determined deferential pressure at which point a safety opens.
  • Im using sman 482 guages
  • JMWHVAC
    JMWHVAC Posts: 134
    Not sure how the readings you say you have are possible.
  • JMWHVAC
    JMWHVAC Posts: 134
    Did your gauge kick the bucket? Is this AC or HP?
    5earlys
    pecmsg Posts: 7,634
    You cannot have Negative superheat or subcooling.
    How do you cool the liquid line Below the ambient temp? The pressure will respond accordingly.
  • Exactly the problem. I have never seen this before.
  • JMWHVAC
    JMWHVAC Posts: 134
    Yet, you are saying it is cooling fine, so all is good.🤷‍♂️
    pecmsg Posts: 7,634
    look for a restriction!
    Where are you taking the measurements? Pictures
  • JMWHVAC
    JMWHVAC Posts: 134
    Somehow the gauge has to be wrong. How can the evap side be good when the condensing side is so low?
    5earlys
  • ratio
    ratio Posts: 4,344
    If a scroll goes negative in the can—not necessarily at the suction port—the winding may start to arc over. You can hear it popping inside.
    I've seen negative subcooling and superheat on digitals before. Most of the time, it's because the unit isn't charged properly (especially on microchannel coils), or the digital was set to the wrong refrigerant.
  • JMWHVAC
    JMWHVAC Posts: 134
    The gauge is saying the saturation temperature is 10* below ambient, then it warms up to a few degrees above the ambient as it goes thru coil! ? ! ? Guess I am missing something…
  • JMWHVAC
    JMWHVAC Posts: 134
    Is that condensation on the high side of gauge set or just the way the surface looks on pic?
    pecmsg Posts: 7,634
    or the placement
  • It's straight cool. Guages are a month old.
    Never pumped the compressor into vacuum.
    It's not condensation just a glare from the picture.
    I just hooked up my old sman 380 to verify that there's not an issue with the new guages. I'll let you know.
    At this point I'm leaning towards an internal issue with the compressor or a restriction at the txv. Checked the drier is not restricted
  • Okay update. hooked up my old s-man 380s got normal subcooling 9. Which told me my new 482s had a problem. So so I did a factory reset on my new gauges and got correct readings.
    I would not haveI would not have guessed that a brand new set of gauges would be doing that. That explains why I never seen settings like that before.
    My thanks to everyone that contributed.
    JMWHVAC
    pecmsg Posts: 7,634
    Thanks for getting back with that
    the first red flag was - sub cooling
    5earlysPC7060
  • I totally agree. I have been doing this for a while and have never seen it. I wouldn't think that a set of gauges out of the box would do that. My old s-man 380s were completely reliable never failed me. Only replaced them because the display is wonky. Thank you for your help
    Glad you found the issues.
    Sometimes old tools are better than new shiny tools. It like having a multimeter that doesn't work. If you can't trust it it leads you down the wrong path
    Not even looking at the sub cooling if the OA is 87 your liquid saturation can't be below that temp but its 10 degrees less. LL temp of 90 seems low with an 87 OA so the whole high side seems wrong. But you already found the issue
    5earlysPC7060