I get all the weird ones...
Tom_133
Tom_133 Member Posts: 969
So I have a local steel scrap yard that is putting up a 100x50 steel building. They will be spray foaming the outside walls which will be great, and the roof is done in with an R50 insulation. 3.5" high density foam under the slab, with thermal breaks along the slab. They want to maintain about 65 degrees and it cant go below 60 because the hydraulic fluid in the big conveyor needs to stay above 60 degrees. . So it'll be 12 loops of 5/8" tube, and we will be on our way to success!
All that would have been great.
Where it gets weird is today when I stopped in to discuss radiant loop layout, they mentioned they wanted hydronic fan units probably two 100k each. So i asked why and they said that in the winter they will probably be leaving the 22x18 door open most of the day to allow the loader to come in and out. So now, my design has been chewed up and spit out.
My question is how would you design for that? Treat it like a snowmelt design? its going to have 8 hours of open door time and 16 hours to come back up to temp?
I asked if they planned on doing that even when its -20 outdoors, and they were hoping to!
any thoughts?
Tom
Montpelier Vt
  • Illinoisfarmer
    Illinoisfarmer Member Posts: 62
    So does the building have to be above 60 at all times? My experience would be that the hydraulic fluid might need to be above 60 to 'start', but once the conveyer (or whatever) is operating, the fluid temp will be fine. If that's the case, the temperature only needs to be maintained when the conveyer is idle. Maybe that's what you're saying - with the 16 hours to come back up to temp. There is a buttload of equipment out there that operates below 60 degrees ambient. Most modern tractors will limit cold weather operation until hydraulic temperature reaches 50 degrees, but after that it's game on - regardless of the ambient.
    If not, prevailing wind direction is also going to mess with you a bit. Can't imagine the energy (and equipment) necessary to maintain 60 degrees with that door open, bitter cold temperature and a windy day.
    Another option might be Low Viscosity hydraulic fluid. Performs better at low temperatures. All depends on the manufacturer's specs though.
    Interesting situation for sure!
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,491
    Can they use those clear, hanging thick plastic "drapes" that you see in factories? Trucks drive right through and they part like the Red Sea, then fall back in place...Conserves most of the heat and definitely better than keeping the door open (foolhardy).
    I've also seen motion activated clear, superlight, plastic bay doors that open superfast and shut just as fast. Mad Dog
    rick in Alaska
  • Tom_133
    I can ask about the plastic drapes, thats pretty smart!
    I dont know about the hydraulic equipment as much as I need to, but will be digging in a bit.
    Tom
    Montpelier Vt
    hot_rod Member Posts: 27,203
    my Local Toyota dealer has those large super fast overhead door openers
    It seems a months worth of fuel cost would pay for that setup
    I’ll bet the company that manufacturers those has some fuel saving data
    GGrossdean_s
    mattmia2 Member Posts: 16,284
    An air curtain on the door will help keep the heat in but not as well as physical barrier options.
    Jamie Hall Member Posts: 27,167
    As noted, @Tom_133 — air curtain or the heavy plastic drapes. There's a supplier for the drapes in Windsor, CT — custom fit, not outrageously expensive. But it's likely you may have an ag. supply outfit closer.
  • Tom_133
    so I ran it by the customer, and he doesnt think when he rolls in with a grapple full of razor sharp aluminum scrap they will hold up very well. I also sent the quick door as hot rod mentioned and he may look into that, but they dont go as big as his door is spec'd for, I did ask if we could shrink it up a bit.
    So lets play the idea he wants to keep that door open, and wants to maintain 55 degrees, any ideas how to design for that?
    Tom
    Montpelier Vt
  • Pumpguy
    Pumpguy Member Posts: 795
    When we built our repair shop, we had a makeup air heater installed. This was primarily for use when the paint spray booth was in operation to heat makeup air that was exhausted by the paint booth.
    We also turned it on whenever we had one of the overhead drive in doors open for any length of time.
    Sorry i don't remember the details.
    EBEBRATT-Ed Member Posts: 20,018
    I think they are nuts to think they can keep the doors open and still maintain temp, what a fuel hog. So much for energy savings and going green.
    They better have a lot of good scrap to sell to pay the fuel bill.
    Air curtains are a good idea.
    At my old shop which was 100,000 square feet we had RT units for heat and Ac in the shop. When the units were 20 years old and the HXs were failing (the AC was ok) we installed gas fired radiant overhead.
    The difference was amazing. We had 10 x 10 garage doors and they got opened in the morning and all the trucks were moved out and the door was closed. This may have taken 1/2 hour to move the trucks and the place would be freezing by then
    With the RTUs it would take an hour to recover on a cold day. With the gas radiant as soon as the door shut the space was back to temp because the slab was a giant radiator.
    Open all day doesn't seem feasible to me.
    I don't know how long fast opening doors will hold up in a scrap yard environment, probably get smashed in a week.
    A good idea though.
    MU air heaters may help to pressurize the building to keep cold air out. have it discharge right at the door.
    no matter what they do it will be an energy pig.
    kcopp
    109A_5 Member Posts: 3,819
    edited August 2025
    " discuss radiant loop layout " In the slab I assume ?
    " the conveyor " is secured to what ? An if they decide to move it ?
    Air Curtain ?
    Sounds like they want to put themselves out of business with heating fuel costs.
    kcopp
    edited August 2025
    do you have a heat load software program? Run it through the loadcalc.
    I use Siggys Heat Load Pro
    There is a free demo on his site, Windows based
    Although it may “error” when it sees no wall 😲
    https://www.hydronicpros.com
    air curtain. They are power hogs for the blowers, but they are oddly effective.
    In_New_England
  • Tom_133
    thanks for all the input. I agree this is going to be difficult and possibly not possible.
    The conveyor is a big boy that is already in place and built into the floor about 8' down. then the conveyor track rises from the floor 15' into the air and dumps into the end unit that has a piston for squishing the material into a square for banding and shipping.
    They need the door open for several reasons, they bring the material in with a loader, and then it gets placed with a 308 CAT excavator onto the conveyor. So they want the door open for the fresh air (i already told them bad idea) but also they run that loader in and out about a 100 times a day.
    Im not sure how to make this all work, but there has to be a solution. They are using a waste oil boiler to heat primarily, and an LP backup when that fails. perhaps radiant isn't the best solution due to its long recovery times. It's also a 9" slab tubing will be in the lower 3rd of the slab.
    Tom
    Montpelier Vt
    HVACNUT Member Posts: 7,365
    Since we're just throwing things out there. How about a 50 ft long entrance tunnel with doors at both ends. Only one door open at a time. Overhead IR heaters in the tunnel.
    Paulvar1ttekushan_3
  • kcopp
    kcopp Member Posts: 4,659
    I second Harvey suggestion. Walk away. This sounds like a no win situation.
    HydronicMikettekushan_3
  • ratio
    ratio Member Posts: 4,215
    At least you heard about it early enough to place enough disclaimers to cover their dissatisfaction with either the temperature or the operational cost. Or both.
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,289
    "They need the door open for several reasons, they bring the material in with a loader, and then it gets placed with a 308 CAT excavator onto the conveyor. So they want the door open for the fresh air (i already told them bad idea) but also they run that loader in and out about a 100 times a day"
    What a god awfull idea. Running a diesel engine inside a building.
    Why don't they do things the normal way. An overhead trolley crane with a grapple. Staging area outside for unprocessed material. Crane moves material from outside in through a small opening right to the conveyor. Forklift inside for handling the bales.
    GGrossIronmanIn_New_Englandttekushan_3
    Seems to me that maybe there's another way altogether, @Tom_133 ? As I read through your comments, one of the reasons they want to maintain temperature in the building — and possibly the only one which really is important (though working a freezing cold building isn't much fun…) is the hydraulic system. Which is not unreasonable.
    So… completely different approach. First, include in the hydraulic system a heat exchanger to maintain the temperature of the hydraulic fluid. Now this may require some thought and additional piping, as the fluid in the hydraulic cylinders doesn't recirculate, and for installations with long piping to the cylinder it might be necessary to have recirculation lines to keep the fluid warm enough. But that's a detail. (An alternative would be a cold compatible fluid, such as is used on aircraft — but that's not cheap).
    Then to keep the workers warm enough to work (never mind keeping OSHA happy) the various work stations would be provided with infrared local radiant heaters (gas or electric) and, possibly, heated floor mats.
    The concept isn't totally out of the blue — that's how we handle dairy milking parlours.
    Intplm.CLambttekushan_3
  • Tom_133
    I appreciate most of the comments guys. I did have a conversation with them verbal and through email, that discussed their expectations. I told them that no matter what we do that building wont maintain a satisfactory temp if any of the 3 overhead doors remain open for prolonged periods.
    The best I can offer is at startup in the morning, the space will be 70 degrees, but within mins of the door opening, all bets are off. They understood and think they can manage as long as the conveyor and hydraulic oil get warmed up and rolling. I said keep it on through lunch then!
    I dont think I will walk away from this job but I will have enough disclaimers and exceptions it'll make a lawyer wanna high five me!
    Tom
    Montpelier Vt
    ratiogarretjhIn_New_England
    It doesn't sound like a radiant slab is the best answer to what they expect ?
    The scrap yard and transfer stations near me all have over-head radiant. Much faster response to opening and closing doors as you have a much higher temperature you are dealing with. They tend to glow red hot.
    If you go to the CoRayVac website they show examples of tall buildings with radiant tubes.
    Since they heat what the "see" one right over the hydraulics would warn regardless of the doors being open or closed.
    I've sat outdoors under radiant heaters at Chicago restaurants on a windy 0°f day, AHR events in January. It felt like my head was on fire!
    Intplm.
  • neilc
    neilc Member Posts: 3,152
    redesign the whole job,
    keep the conveyor warm inside,
    put the feed hopper outside, maybe under a shed roof if snow or rain matters, have a small opening for the feed conveyor, air curtain that,
    known to beat dead horses
    109A_5
  • Tom_133
    I think you guys maybe right. I may put the tube in for future, in case they repurpose the space to be a mechanical shop in the future. But we may need to re think the heating.
    They make ALOT of waste oil from old cars, and equipment and so the heating with waste oil is kind of a necessity. Maybe I will do more research.
    Thanks all
    Tom
    Montpelier Vt
  • psb75
    psb75 Member Posts: 1,113
    The radiant tubing in the BOTTOM 1/3 of a 9" slab is NOT going to favor a quick recovery.
  • Intplm.
    Intplm. Member Posts: 2,969
    I see much use of glycol in your future. Hopefully, this customer is maintenance-aware and will maintain this system.
    I worked along with the Clean Burn waste oil guy in Missouri. I did a few of the CB boilers on radiant systems.
    The Clean Burn waste oil unit heaters were very common in truck and tractor repair shops.
    This graph gives you an idea of the effect of the tube depth in a slab. At the bottom of a 9" slab would be a huge hit in performance and output, a lot of downward loss also.
    edited August 2025
    Putting stuff in slabs that is hard to repair when compromised always seems like a bad idea to me. I've seen electrical conduits and the wires damaged (even with the 'As-Built' drawings). Shops where equipment should be secured to the slab is just inviting problems down the road.
    A war slab will help the building hold heat with the doors open better tan anything else. Maybe slab heat with a gas fired MU air unit or overhead gas radiant near the doors.
    Direct fired MU air is 100% efficient no flue and with open doors combustion byproducts will not be an issue.
  • Dan_32
    Dan_32 Member Posts: 21
    I would tend to agree with Hot Rod. I don't know what your budget is, but I would still go with your original radiant floor design and supplement it with overhead low intensity radiant tube or high intensity radiant heaters. I'm not sure if you have flamable or combustionables in the space. If there are concerns with the combustionables, design with the sealed combustion, low intensity heaters.
    Since radiant heat works on line of site and heats the objects, placing some the units over the hydraulics would warm them regardless of the doors being open or closed.
  • CTETeach
    CTETeach Member Posts: 33
    I have done some work in granite in Northern Mass southern VT. Same situation but add a dirt floor. Two huge garage doors with one or the other being open most of the day. Some days both open. The issue there was to keep water for the saws from freezing. We used Space-Ray Tube heaters 250,000 btu units in several locations. The employees still had to wear their long johns and layer up but the water didn't freeze.
    The company was very helpful with design https://spaceray.com/commercial-industrial-heaters/
  • Lance
    Lance Member Posts: 334
    There are only three ways to heat this situation. Radiant floor, or infra red. The third way is use a High velocity spot hvac air duct system if only the work station needs to be satisfied. Target air flow to the right to the spot. Could even put a handle on a hanging duct so the user can point it where they want it. With proper air balancing, "its required", doors can be left open and cost will not be too steep. Just draw return air from opposite area of any open doors. Consider their door openings as a fresh air makeup system and size accordingly. Also air curtain fans at doorways do work. Many of my clients are happy with them. I worked in subzero weather with kerosene space heaters blasting away. It works.
    My job has taken me in -10F freezers in front of evap fans to work. In August I was wearing a down feather coat, and as much thermal clothing I could tolerate. Wool cap etc. Need more advice talk to the Alaskans.
  • Bill_Kitsch69
    Bill_Kitsch69 Member Posts: 51
    edited September 2025
    without knowing more about the actual usage of the building and how people fit in, I would generally say this is a job for infrared.
    You put heat tracer on the oil lines that need to stay above 60. And spot heat everything with infrared high intensity.
    whether or not some of it will be tube style and some of it ceramic I don’t know it’s a design job. Contact me and I’ll fly out and design it for a nominal fee.
    get your Supply house to send you the manufacturers rep for your favorite brand of infrared heating and get them out on the job to get this laid out seriously
    do not go price shopping them after they design the whole job for you like some idiots do. Loyalty, baby.
    Does infrared work with the waste oil they are using ?
  • Tom_133
    Yeah thats the point. They are a scrapyard so not an unlimited amount of waste oil, but so much that they dont care if it runs ALOT. I basically explained to the customer the limitations of the heating, and suggested strongly a couple big waste oil ceiling mounted heaters that would be aimed at the open doors. The radiant will work all night to make it warm in the morning, but then the ceiling mounted heaters will take over. We have been round and round with the inefficiency of the whole thing. There will be no actual workers suffering in the building, just a guy in a heated excavator cab sorting, and then running more material in with the heated loader.
    Kind of a silly building that could have been done so much better, but thats neither here nor there I guess.
    Tom
    Montpelier Vt
