Cooling won't turn on. Need help identify Thermostat Wiring

First time trying to switch on the cooling in my house since we move in. The house contains 2 thermostats controlling two outdoor HVAC Units for different rooms. (Heating for the house is using boiler)
Thermostat A works fine to turn on the cooling (when cooling on is set, outdoor unit starts fine), but the Thermostat B doesn't seem to do anything (outdoor unit won't turn on).
I check the wiring found those two are using completely different wiring.
Thermostat A (working) is using 3 wires G Y R
Thermostat B (not working) is using 3 wires B Y R
Anyone know based on the wiring, is Thermostat B wired for cooling or not? Thank you
Comments
-
Thermostat B serves a heat pump. It does air conditioning, and heat (AC in reverse). Indoor blower motor (fan) is on but the outdoor unit isn't? It could be any number of things. Low refrigerant pressure. High refrigerant pressure. Contactor. Capacitor. Relay. Defrost board. Compressor. Where are you located? It needs an HVAC tech who knows heat pumps.
0 -
Both indoor fan and outdoor unit are not on.
0 -
-
Switch off. Circuit breaker off or tripped for the air handler. Fuse in the air handler.
If the breaker is tripped or the fuse is blown in the air handler, it happened for a reason.
A heat pump air handler might have breakers in the air handler door if there's electric resistance heaters.
0 -
Just measure the voltage on Thermostat B wires, there is no AC voltage between any of the two wires.
Checked electric panel all the switches are on.
0 -
Blown fuse or transformer. But why?
0 -
You probably won't read any voltage at the stat that will make sense. The stat is a switch so you only have HOT 24 volts to it on the red R wire . You don't have the other leg of the 24 volts there.
If you jump R & Y with the stat off the wall the indoor fan in the AHU should start and the outdoor unit should start.
If it doesn't go to the Air handler and find the control circuit transformer. it should have 120 or 240 feeding the transformer (see Ahu name plate) and then 24 volts coming out of the transformer.
Make sure the breaker to the trans is on and any 24 volt fuse in the ahu is good.
0 -
-
-
~24vac
0 -
First time trying to switch on the cooling in my house since we move in. The house contains 2 thermostats controlling two outdoor HVAC Units for different rooms. (Heating for the house is using boiler)
That being said I would think that the unit is straight A.C. If that is the case, someone hooked the blue wire up to the B terminal thinking that was a common? Remove the blue wire from the subbase and jump R and Y Indoor fan should start as well as the outdoor fan and compressor. Don't be impatient there could be a built in delay in the out door unit.
0
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 426 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 991 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements