Steam pressure; always amazed folks set it high
Love to hear some takes on this pressure setting. I like 1.5-2psi with 1psi diff.
The house is probably 1500 square feet. 5 year old Burn PIN done completely with propress copper. Owner says they got it done for a “great price”.
    Jamie Hall Posts: 27,738
    Pressure setting is way too high. That particular pressuretrol can be set all the way down to a bit below 2 psig, with a 1 psig differential — which is the best they'll be able to do.
    Long Beach Ed
  • Ironman
    Ironman Posts: 7,942
    If it’s a one pipe system, 2 psi ; if it’s a two pipe system, then it may be less than 1 psi.
    Bob Boan
    ethicalpaul Posts: 8,993
    It's not really a setting, it's a limit. How high is the actual pressure while the system is running?
    mattmia2 Posts: 17,997
    people with bad vents set it high, the pressure compresses the air that can't get out and some steam gets in and the parts without venting sort of heat some.
  • Long Beach Ed
    Long Beach Ed Posts: 1,846
    edited June 2025
    Simply poor practice, like piping a steam header with copper Pro-press.
    They didn't know better, couldn't be bothered finding out the proper setting, or as Mattmia suggested, it was the only way they could heat some radiators without taking tools outside the boiler room.
  • jumper
    jumper Posts: 2,605
    People who ought to know better think that steam "blows" condensate through trap.