Steam pressure question
So I definitely got lucky……..I was able to drill out the center of the broken stub, and kept drilling until there was just a little bit of material left of the brass stub pipe. Took my handy pointed chisel, sharpened the end, and started peening over one end of the remnants. I was able to break it out in little pieces. Nicked a few threads of the insert, so I have to run out and get a thread chaser of the proper size.
Would have been easier if I didn’t have to work between the boiler and the basemenwall to the right, only 15 inches of space to work in.
I plan to put about a 2 inch copper stub pipe into the insert, then put in a 90 degree brass fitting, the put a new 30 psi gauge with a bottom mount fitting.
So the next question…….heres the gauge I pulled out. I noticed it is only about 3 inches above the water line. Is there any special 0-30 gauge I need to get, as it would appear this one is subjected to direct steam as it was not fitted on a pigtail.
it needs to be "internal syphon", that protects it from steam. Or you can just plug it and use a tee or cross and put it with your other gauge.
Or better yet plug it with a short nipple and a cap, that will be easier to get out if you ever want to use that tapping for something else.
They all fail fast and you don't need them except apparently for code purposes. The Right Way™ is to leave that factory one in there broken and forgotten and use your low-psi one that you added.
So don’t bother putting any 0-30 gauge back? Saves me the cost of purchasing one.
Failure usually has to do with it getting tweaked, if you bend the case while levering on something or drop it you are very likely to throw it far out of calibration or just plain get it stuck at some reading.
You still need a 0 to 30 psi gauge for code and insurance purposes. The gauge must have at least twice the range of the setting of the pressure relief (safety) valve, which for a low pressure steam boiler is 15 psig by code.
Bburd0 -
I believe a 0-30# gauge is required by code!
Yes, I'll quote myself:
Nope, they die all on their own very fast
I put in a copper stub pipe with a 90 degree elbow and plug for now. My local plumbing supply store only had a back mount, but it did not say it was an internal siphon style. Once I find the correct type I will install one just so I’m up to code.
A few years ago I looked into the design of pressure gauges with low pressure ones in mind. Manufacturers stated different pressure capabilities, but it was somewhat common that gauges are designed to withstand 130% of the full scale (6.5 psig for a 0-5 psig gauge).
In the discussion about low pressure range gauges one option is to have both gauges installed, but to be able to isolate the low pressure gauge so that if for some reason the pressure does exceed the 130%, the gauge would not be damaged or rupture. Keep it isolated as mentioned previously and only have it in service when you are present and need to know the reading.
Chris J has lots of comments over the years of using a Magnehelic low pressure gauge that can withstand the 30 psig pressure.
If there is no 30 psig and something goes wrong, your insurance company and/or lawyers might have an issue with covering damage (if they even know the code).
Type of valve used may be important as well. I noticed my valve when shutoff tends to trap vacuum in the gage. Left for long periods like that I have to rezero my gage. Now I just leave the valve open all the time because I know I never exceed the 3psi pressure but I'm not sure why my valve does that.
No one has ever said remove the 30psi gauge and replace it with a low pressure gauge
you're trapping steam or water vapor on the gauge side of the valve. it isn't hot enough for live steam but it is hot enough that the air can hold more moisture than at room temp. it cools and that moisture condenses and you get a negative psig.
Interesting. If the pigtail actually holds enough water to create a seal, then the void space between the seal and gauge would probably contain moisture (i.e., humidity) at the saturation level at the temperature and pressure at the time it was filled. If the overall temperature changes enough and goes below the temperature at which the pigtail was filled, it could go to vacuum.
If anyone has nothing to do, they could try a test, using water, then use a liquid that won't evaporate and run the test again to see if there is any measurable difference. Or install an oil filled manometer in parallel with the small gauge at the boiler pigtail.
A bench test might be easier than an in-place test.
@dabrakeman Any idea how much of a vacuum you get?
fill a pop bottle part way with hot water from the faucet, put the cap on and see what happens when it cools off. it collapses some.
Just shut the isolation valve to the LP gauge when the boiler is off.
Or if you really want to be nerdy put a tee between the gauge and its isolation valve put a 1/4 ips x 1/4 flare fitting with a shrader port in the flare. Close the isolation and bleed the shrader.
I was able to fit a 30 psi gauge in the original port, using a copper stub pipe and ball valve just below the gauge.
I can rest a little easier knowing now that I’m barely getting a reading on the 0-5 psi gauge with the boiler running, whereas before my original 0-30 gauge was jumping up to 6 psi with the boiler running. The new 0-30, as expected, reads 0. Wondering if it’s worth getting a 0-3 psi gauge in place of the 0-5 so I can get a more accurate low pressure reading.
Appears I have to skim my water again, as I accumulated some additional brown oily residue above my water line in the sight glass.Going to start looking into making sure my main vent lines are functioning properly. Making some progress……….
That's a fascinating thought about the water vapour in the space between the gauge and the pigtail condensing and causing a vacuum. It's also wrong, unless the pigtail is closed off from the boiler. If any vacuum were to be created momentarily, it would just raise the level of the water seal on the gauge side relative to the boiler side with no change in pressure once the levels had adjusted.
they have a valve between the pigtail and the gauge. the partial vacuum forms between the valve and the gauge.
As others mentioned, if you really want to see a better view of the normal operating pressure and your boiler is not the typical oversized for the attached EDR, put on a low pressure Dwyer Magnahelic Gage. Many new old stock on eBay. You will have to determine which range is best for your system there are many pressure ranges and center zero versions to choose from. The downside is the scale is usually in Inches of Water Column not PSIG. My system never goes over 2 Inches of Water Column.
Since the Gage can tolerate up to 15 PSIG I don't bother with a shut off valve. As an example in the picture below the Gage goes to 30 Inches of Water, which is just over 1 PSIG. 27.68 Inches of Water Column equals 1 PSIG (Red arrow on Gage scale).
This valve may be a code violation. For just the reason shown, the valve appears closed in the picture rendering the gauge that is there for safety purposes useless. You may know to open the valve, but others may not.
One Pipe System0 -
The 0-30 PSIG Gauge should have a Internal Syphon. The Internal Syphon acts like a miniature internal version of an external pigtail or water trap. Another method that may work to protect the Gauge is have a tall vertical nipple (probably greater than 12") to trap a buffer of air between the steam and the Gauge.
Does this Gauge have an Internal Syphon ?
One Pipe System0 -
It does not have an internal siphon………I’ll look into getting an internal siphon style and remove the ball valve.
@Jamie Hall If the space between the gauge contained 212F steam and cooled to 70F, what would happen to the water level, given steady state on the boiler side of the pigtail? As we all have discussed many times, steam vs. water specific volumes are significantly different….saturated steam at 212F occupies 26.799 ft3/#, water at 212F occupies 0.016719 ft3/#, and water at 70F (data for 68.939F) occupies 0.016048 ft3/#. A factor of ~1700 in round numbers.
The water level would rise, but since the volume of the piping and gauge are so relatively small, it nevertheless might not be detectable. But it does exist.
The dynamics on the boiler side have bearing as well.
Now this all gets wiped away to some extent, because it is unlikely the gauge side of the pigtail sees 212F steam. The initial conditions on that side makes all the difference. If there is no "steam", just air and a minimal amount of moisture in the water, all bets are off and the effect is less. Just for the heck of it, the specific volume of dry air at 212F is 16.93ft3/# and 70F dry air is 13.35 ft3/#. So as the air cools down it would occupy about 3/4 of the space. These numbers are based on 14.7psia atmospheric pressure.
Anybody got a headache?
Have a great holiday weekend and thank you for your service to all those who have served in the military.
You might consider using a 30 - 0 - 15 compound gauge. These are graduated to show a pressure range of 30" Hg. vacuum and 15 PSI positive pressure. I frequently see these on old installations.
I can't comment if they're are of the internal syphon type or not.
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
The water level would rise, as you say, @SteamingatMohawk — but only far enough so that the height difference was enough to counteract the pressure difference.
And that woul only be if there were steam in the space between the pigtail and the gauge. If it is just condensing water vapour from the air in there — which is all that there should be in there — the air volume change will be very small.
fill a pop bottle with about 120 degree tap water and put the cap on and tell me what happens when it cools.
The point is that depending on how much air, steam and water vapor is in the space determines the amount of "shrink", I think. Maybe the easiest way is to use a clear manometer instead with the gauge on the vent side and the boiler on the other.
@mattmia2 Even better use some boiling water. Then you get the shrinkage I mentioned.
@Pumpguy In the range we are talking about 1 inch of water is .07+ inches of mercury. On a 30 inc scale that's pretty small. But it would be interesting to actually see the real vacuum level.
I'm not so sure the issue I am seeing is as localized as being theorized. If I start the boiler cold with the valve closed to the 3psi gage and gage reading zero the needle stays on zero throughout the cycle. When the boiler shuts off at end of a longer cycle the needle is pulled negative and then it just stays there. It occurs instantly and is not a matter of trapped air between the pigtail seal and gage slowly cooling and contracting. It corresponds entirely with the vacuum the entire system sees moments after the end of a cycle. I just think my valve is acting more like a check valve than a bidirectional shutoff.
Yes, that's a different situation you suggest. The check valve behavior of the isolation valve is mysterious. Assuming on the cooldown a vacuum is created as the steam condenses in the piping, etc. there would be some amount of vacuum, which would eventually go away as long as there is an open path to air via the vents.
I just find it interesting to noodle on what happens to the gauge side of the pigtail if the shut valve is actually tight.
that isn't much pressure for that valve to not be holding against but it isn't unusual for a seal to seal better in one direction rather than the other. in one direction the pressure differential pushes the sealing surfaces together, in the other direction it pushes them apart. with that information i'm betting your valve is bad.
- 87.1K THE MAIN WALL
- 58 Biomass
- 113 Chimneys & Flues
- 110 Geothermal
- 161 Indoor-Air Quality
- 998 Plumbing
- 391 Solar
- 55 Water Quality