Steam pressure question
Comments
-
So I definitely got lucky……..I was able to drill out the center of the broken stub, and kept drilling until there was just a little bit of material left of the brass stub pipe. Took my handy pointed chisel, sharpened the end, and started peening over one end of the remnants. I was able to break it out in little pieces. Nicked a few threads of the insert, so I have to run out and get a thread chaser of the proper size.
Would have been easier if I didn’t have to work between the boiler and the basemenwall to the right, only 15 inches of space to work in.
I plan to put about a 2 inch copper stub pipe into the insert, then put in a 90 degree brass fitting, the put a new 30 psi gauge with a bottom mount fitting.
So the next question…….heres the gauge I pulled out. I noticed it is only about 3 inches above the water line. Is there any special 0-30 gauge I need to get, as it would appear this one is subjected to direct steam as it was not fitted on a pigtail.
0 -
it needs to be "internal syphon", that protects it from steam. Or you can just plug it and use a tee or cross and put it with your other gauge.
Or better yet plug it with a short nipple and a cap, that will be easier to get out if you ever want to use that tapping for something else.
0 -
They all fail fast and you don't need them except apparently for code purposes. The Right Way™ is to leave that factory one in there broken and forgotten and use your low-psi one that you added.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
So don’t bother putting any 0-30 gauge back? Saves me the cost of purchasing one.
0 -
Failure usually has to do with it getting tweaked, if you bend the case while levering on something or drop it you are very likely to throw it far out of calibration or just plain get it stuck at some reading.
0 -
You still need a 0 to 30 psi gauge for code and insurance purposes. The gauge must have at least twice the range of the setting of the pressure relief (safety) valve, which for a low pressure steam boiler is 15 psig by code.
—
Bburd0 -
I believe a 0-30# gauge is required by code!
0 -
Yes, I'll quote myself:
They all fail fast and you don't need them except apparently for code purposes
Failure usually has to do with it getting tweaked, if you bend the case while levering on something or drop it you are very likely to throw it far out of calibration or just plain get it stuck at some reading.
Nope, they die all on their own very fast
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I put in a copper stub pipe with a 90 degree elbow and plug for now. My local plumbing supply store only had a back mount, but it did not say it was an internal siphon style. Once I find the correct type I will install one just so I’m up to code.
0
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 975 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements