Spanish power grid

Any insights from someone who's guesses are more informed than mine?
Comments
-
Insufficient rotating inertia. Similar to what happened in Australia a few years back. Fluctuations in input frequency from renewables not offset with rotating turbomachinery
Common cause- too many windmills, not enough turbines.
You'll see more of this , not less as the percentage of non dispatchable power sources climbs.
IMHO they should be banned over 20% of input just for grid stability.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.6 -
Usually it is just one component that fails at just the wrong time that causes a cascade. Like in Ohio or NY.
0 -
-
-
Saw that. Sounds like gas as it's hard to believe a 30 +/-degree delta T could cause such a difference in resistance. In any event, none of that would cause a frequency shift. Lack of inertia does. The article said Spain is about 80% non dispatchable/ asynchronous sources.
Tick, tick, tick.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
-
BIG turbines. That's why we haven't seen synchronization failures here. With this , that makes 2 strikes against loading the grid with asynchronous sources
https://www.aer.gov.au/publications/reports/compliance/investigation-report-south-australias-2016-state-wide-blackout
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
no, i'm talking about the issue with harmonics in the transmission line. if the frequency is varying in the transmission line more mass is going to make it harder for the generator to change with it
0 -
But how would weather vary the frequency? That's my point. Nothing in the lines can vary frequency -only sources.
That's why you need a lot of rotating mass. If you have a sudden load change, a low mass source will change frequency quickly and the grid goes down. High inertia can absorb the fast changes without significant frequency shifting. GE, Siemens et.al. don't sell synchronous condensers for grins.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
August 14, 2003, Ohio proved poor load management can cause destabilization of synchronization.
Since then they have shut down many coal fired plants along the Great Lakes. What's replacing that rotating resource ? Breath easy, it will get better, honest.
The good thing is when resources trip and go off line, they can be restarted and reconnected. If you burn them up (trying to maintain or quickly correct a bad situation) the restoration time is much greater.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
It will be interesting to see what the engineers come up with as a root cause. My money is going to be on a frequency droop or instability somewhere — why? Who knows at this point. At least that was what was found to be the root cause of the Texas grid blackout a few years back.
Thing is, if bits of the grid get out of phase — even slightly — with each other, huge currents can flow and things trip. Or if the frequency gets too far out of limits things trip. And then you have dominos…
The problem with a black start on a grid with a lot of asynchronous power is that you can't start any of that stuff without a power source which is synchronous running and feeding them, since all those gadgets are phase following.
Completely off grid systems, if they supply AC, will have a crystal controlled inverter. I wonder if the big battery energy storage systems could have that? Hmm… if they were big enough, they might be able to force stabilize things…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
I’m not sure why it happened but it was eerie. We were in an Uber going from Marbella to Ronda when it occurred. As we approached Ronda the car driver was really confused. No cell service, no power anywhere. He had no way to locate our hotel in a town he was not from. Of course we did not know at the time that all power down. Driver asked a local and finally got to our hotel. Hotel mgr said all of Europe was down he heard, he had no way to check our reservation but luckily my email saved the confirmation that I could show him. No cooking so only cold foods but that got us by. 6 hrs later power back on. Took appx 24 hrs to get comms and all else back to normal. Really a trip.
2nd time in our lives we’ve been out of country when a major event happened, other time we were in Akumal Mexico on 9/11. Crazy!1 -
-
Some of the grid is DC.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
DC is used for a number of the very high power interconnects — including the ones between France and Spain. Problem is, while they can contribute power if needed, they can't do anything to stabilise grid frequency and thus oscillations. Hence… lights out. The problem is being worked on… but nowhere near to practical engineering never mind installation yet.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
I'm confused Jamie…..
We have several DC transmission lines in the US, some of which are 40+ years old. So I'm confused by the "but nowhere near to practical engineering never mind installation yet." part.
They generate whatever frequency they need and lock it to the grid and since they're controlling it's frequency how is that any different than a typical generator turning at a set speed?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Three reasons for using DC power links: Reduce losses and line costs on long links (you don't need intermediate substations to compensate for cables), undersea links (cables have high capacitance), and linking systems together that are not synchronous or different frequencies (japan).
How the converter stations operate is another consideration. Most of the converter stations (certainly the older ones) are based on thyristors. These devices can be switched on electronically but rely on reversing current flow to switch off. So they will only work when connected to a working AC system. In many ways they are same as PV and wind turbine inverters that also require a working AC system.
Some of the newer converter stations are based on IGBTs and these can act as a voltage source just like a spinning generator.
The way PV and wind turbines are connected to power grids is becoming a problem with higher levels of penetration and a reducing amount of spinning metal. It does not have to be this way. With modern power electronics "inertia" can be created with the right control strategies.
In some ways the whole renewable strategy seems to be to make connecting thousands of small devices as cheap and simple as possible and let someone else solve the problems this creates.
John
2 -
Well, @JDHW pretty well covered the problem. The short answer is that virtually all DC to AC inverters — whether on your rooftop panels or a wind turbine or a solar panel farm — or a gigawatt interconnector — track the frequency and the phase of the AC network to which they are connected. There are various ways to do this, but so far they all have the same basic principle: they vary their voltage and current output to exactly follow the voltage of the lines to which they are connected.
They do not generate a stable 50 or 60 hz output wave by themselves, never mind one which is exactly in phase with the lines to which they connect.
Further, most of them cannot absorb power from the network to which they are connected — only deliver it.
Thus if there are instabilities in the network to which they connect, they will only follow (and often worsen) those instabilities.
Contrast this with a rotating alternator. In such a device, the output frequency is determined by the rotation of the alternator — which is, in effect, a huge flywheel. Even your little home generator is pretty good at this with varying loads — but consider at the other extreme "Big Allis" — New York's Ravenswood No. 3 with a power output at full song of just under 1 gigawatt. (During the northeast blackout of 1965, she alone was able to keep the lights on in Manhattan for almost 10 minutes — she eventually quit when her frequency dropped too far and the lube oil pumps dropped out and cooked her bearings). Such units can maintain a stable frequency for a considerable time — several seconds at least, which is an eternity in grid terms — by either delivering a huge leading overload current if the grid freqency droops or absorbing a similar current if it starts to lead, solely by the rotating inertia of the machinery.
Various opinions exist as to how much power in rotating inertia is needed to keep a grid stable; I've seen estimates ranging from about 20% to 40% of the load.
Now we get to what might be… on small systems, such as an AC/DC/AC ultra pure power supply for instance, the output can be controlled with a crystal controlled oscillator (which, by the way, doesn't have to be at the same frequency output as input). But that doesn't scale all that well, and it can't absorb power. On a grid scale I've seen suggestions of controlling the output frequency using satellites, such as GPS signals — but there are some interesting problems with that, as well as some vulnerabilities to be considered.
It's an interesting problem…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Pretty much all new inverters can do Volt-VAr, Volt-Watt, Frequency-Watt compensation. These are what you need what you need for grid support. Some utilities requires some functions enabled some dont. Anything with batteries behind it can do frequency regulation in both directions as they can absorb or source power.
Larger scale inverters have programmable synthetic inertia function that can simulate the effect of a rotating machine. This function is sometimes used in microgrid applications for similar stability control.
People also forget that wind turbines are giant spinning machines, so rotating inertia is not an issue. Again, a function that needs to be enabled.
As for high voltage DC, another issue with long distance AC is the line stops behaving like simple wires but as a transmission line (transmission line like in radio frequency). This means the generator at one end can no longer accurate control the voltage on the other end of the line. There will also be a phase angle between the two ends of the line, so the two grids can't be technically in sync.
As for the Texas fiasco. The power there failed because the utilities didn't winterize their gas supply lines and they simply froze up. For some reason, the Texas grid is also not interconnected to other grids, so when these generators went off-line there was nowhere to pull extra power from.
2 -
You guys know more about power distribution than I do. I am just a dumb electrician.
I thought the reason George Westinghouse (AC Power) won out over Edison (DC Power) was because DC suffered more line loss and it couldn't transmit long distances as easily as AC.
Am I wrong or did I skip school that day?
0 -
ac can be passively transformed to higher voltages and lower currents with a transformer, since the transmission line loss is proportional to the current, making the power high voltage and low current dramatically reduced transmission line losses. the parasitic capacitance and inductance of the transmission line causes losses in ac transmission that you don't have with dc. solid state electronics let you practically convert high voltage ac to high voltage dc, send it over a transmission line, then convert it back to high voltage ac so you get significantly less transmission line losses. 130 years ago you would have had to have used enormous rotary converters or motor generators to do that.
1 -
-
@Kaos 2 points. The inertia of a windmill armature is pretty small compared to a badeload turbine. If you had high inertia in a windmill you'd be shredding gearboxes even more frequently then they already are.
Second, each windmill is variable frequency and none of them are synchronized.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.1 -
This is a really interesting site. Lots of posters that love and know lots about heating systems - including steam. Then there is an advanced discussion about how power systems operate - wow. Here is a slightly different take on what inertia means in a power system.
Before the days of modern power electronics everything that rotates was connected to the grid synchronously and contributed to frequency stability and this includes motors as well as the generators in the power stations. Motors are considerable fraction of the load on most grids, industrial and domestic (fridges/freezers/aircon). There is no doubt than thousands of tons of spinning metal does contain lots of energy.
However, AC power systems are very sensitive to frequency. The transmission system has distributed inductance and capacitance in the form of cables and to maintain stable voltages discrete capacitors and inductors are dynamically switched in and out of circuits and transformer voltage ratios are changed. Because of this frequency sensitivity, AC systems are controlled to very tight frequency limits - 1% or better. In terms of keeping a grid stable you can only use 0.5% of the considerable stored energy.
What really keeps a traditional power grid stable is some generators operating at less than maximum output that can rapidly change power output in response frequency changes (the technical term is spinning reserve). Inertia provides the energy while this ramping up of power output takes place. This balancing must happen within seconds. Things like generators failing or transmission lines failing need to be take into account when deciding how much generation capacity is running as spinning reserve and where it is located in the system. This is what power system operators do all the time and it normally works. When it goes wrong it hits the news.
Power electronics come of age and there are new ways of connecting power sources - PV, wind, DC power links that don't contribute to spinning inertia. On the load side inverter motor drives are very common in the industrial and domestic equipment that don't contribute to spinning inertia. Electronic power supplies for LED lighting and computers take the same amount power regardless of voltage.
With high levels of renewable energy on power grids operators can end up with all their traditional generation acting as spinning reserve. Or worse, having to run generators on no load to maintain inertia and curtailing renewable sources.
The way out of this is to make all sources of power and loads frequency sensitive. You don't need much actual storage from spinning metal or batteries when everything is frequency sensitive. If there was a requirement for PV or wind turbines to operate at 95% output when the grid frequency is 50 or 60Hz there would be an automatic reserve of 5% if the frequency started falling.
Converting all sources and loads to frequency sensitive versions is easy to do technically but virtually impossible to do retrospectively. You could start with the bigger renewable installations.
Renewable sources are intermittent so will always require backup from some source of dispatchable power.
I wonder why the industrial revolution really got going when steam power came along and we no longer had to rely on windmills and waterwheels? There is a working textile mill that is maintained as a museum near Manchester airport (uk) which contains a time clock for workers to clock in and out. It is linked to the waterwheel driving the mill - so lower water levels = longer working hours!
John
1 -
Yeah..
The DC transmission lines I was reading about out in CA are 500k, negative and positive, so a million volts across the two lines.I'm pretty confident Edison never even imagined something like that. He'd need generators that could output it and then a load that could use it.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Old gen wind turbines were essentiall a big induction motor connected to the gear box running at fixed speed. Newer stuff is a doubly fed induction generator (think of them as a regular motor with an electric gearbox) which are pretty much the same thing but allows the motor speed to vary a bit from synchronous speed.
They are big motors spinning with the grid.
More info:
https://albertainnovates.ca/wp-content/uploads/2020/06/RAE-2429-N-ENERCON-Wind-Inertia-Value.pdf
0 -
How did they get the old ones to run at a fixed speed?
I understand once it's connected to the grid it'll run only so fast,but how do you keep it from turning into a motor?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Motors and generators are the same thing the difference is the mechanical input/output. A induction generator on a windmill will run at a slightly greater speed than the connected mains when there is enough wind. if the wind drops while the windmill is connected it will slow a little and take power from the grid acting as a motor. If you measure the power flowing on the connection between the windmill and the grid you can tell if it is acting as a generator or a motor. You can't make it run at different speed.
Modern wind turbines tend to be permanent magnet alternators connected to inverters. You can still run them as motors to store a bit of energy.
1 -
I understand that.
That's why I asked how you would stop them from acting as motors, because having a huge fan outside pulling power because the wind is a tad slow doesn't make any sense since it would happen often.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
@ChrisJ You can get reverse power relays that sense the current and phase relationship with the voltage ,so the answer is sense reverse power and then disconnect the wind turbine. This is the sort of protection is used on conventional generators.
I guess you sense the speed of the wind turbine and reconnect when the speed is high enough to generate power.
1 -
you'll have to sync the turbine up somehow before you reconnect it. i suspect no wind turbine has uses a synchronous alternator in about 50 years.
0 -
@JDHW "I wonder why the industrial revolution really got going when steam power came along and we no longer had to rely on windmills and waterwheels? "
Easy. For the first time we had dispatchable power. Worried about "net zero"? Install a bunch of small fission plants and call it a day. 👍
Trying to use non dispatchable, variable output sources is creating problems for which we already have solutions.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.1
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 975 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements