Repair or Replace Gas Boiler

Hi , my 30 year old teledayn lars
FHW natural gas
boiler blew up the t & p valve , copper tubing it was soldered on right off the boiler .
Prior to that , the second floor baseboard lost its heat.
First floor baseboard was still giving off heat. Boiler operating and heating.
Running like that for 4 weeks.
When one evening a loud explosion occurred in the basement.
Upon checking, I found the boiler not running and a little water around the boiler.
Looking further, I saw that the T & P valve had blown right off the boiler top.
Is the boiler repairable ?
By repiping a new T & P valve to the boiler and flushing and purging the air out of the first and second floors baseboards.
Then restart the boiler and do a boiler check.
( What causes the second floor baseboard to lose its heat ? )
Air in the system ?
Water filled evaporator tank ?
Clogged water feed valve ?
Thanks
John M.
Comments
-
Are you\ saying the threads where the TP relief screws into the boiler stripped and the entire valve shot out?
0 -
Sounds like either you don't have a low water cutoff or the LWCO did not work.
The boiler should be inspected for damage. If it looks like it may be ok it needs to be disconnected from the system and a hydro test done to check the heat exchanger.
Thats for starters
0 -
It may or may not be salvageable — I wouldn't say repairable. I wouldn't bother; too much more or less difficult to detect damage may have been done by the overpressure event.
In fact, I would scrap it, the expansion tank, and any trim, such as the defective pressure relief valve, the low water cutoff (if there even was one), aquastat controls — the lot. Again, not worth the time and effort to find out which redundant safeties failed.
Then start all over again.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
You got a long run out of that Tlyne-Laars...That's not even a company any longer, but Laars make a really nice replacement. Mad Dog
2 -
Could be the expansion tank was waterlogged and the relief valve was scaled shut. Could be system was low on water because the pressure reducing valve failed and it had a leak of some sort and the boiler got low enough on water that the boiler heated the joint on the relief valve to the point where it melted the solder because part of it was dry firing. In either case it would be best to replace the boiler after either event.
Did water pour out of the relief valve piping?
0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 941 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements