Repair or Replace Gas Boiler
Hi , my 30 year old teledayn lars
FHW natural gas
boiler blew up the t & p valve , copper tubing it was soldered on right off the boiler .
Prior to that , the second floor baseboard lost its heat.
First floor baseboard was still giving off heat. Boiler operating and heating.
Running like that for 4 weeks.
When one evening a loud explosion occurred in the basement.
Upon checking, I found the boiler not running and a little water around the boiler.
Looking further, I saw that the T & P valve had blown right off the boiler top.
Is the boiler repairable ?
By repiping a new T & P valve to the boiler and flushing and purging the air out of the first and second floors baseboards.
Then restart the boiler and do a boiler check.
( What causes the second floor baseboard to lose its heat ? )
Air in the system ?
Water filled evaporator tank ?
Clogged water feed valve ?
Thanks
John M.
    pecmsg Member Posts: 6,885
    Are you\ saying the threads where the TP relief screws into the boiler stripped and the entire valve shot out?
    bigjohnnymack
    EBEBRATT-Ed Member Posts: 19,891
    Sounds like either you don't have a low water cutoff or the LWCO did not work.
    The boiler should be inspected for damage. If it looks like it may be ok it needs to be disconnected from the system and a hydro test done to check the heat exchanger.
    Thats for starters
    Jamie Hall Member Posts: 27,008
    It may or may not be salvageable — I wouldn't say repairable. I wouldn't bother; too much more or less difficult to detect damage may have been done by the overpressure event.
    In fact, I would scrap it, the expansion tank, and any trim, such as the defective pressure relief valve, the low water cutoff (if there even was one), aquastat controls — the lot. Again, not worth the time and effort to find out which redundant safeties failed.
    Then start all over again.
    bigjohnnymack
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,469
    You got a long run out of that Tlyne-Laars...That's not even a company any longer, but Laars make a really nice replacement. Mad Dog
    Long Beach Edhot_rodbigjohnnymack
    mattmia2 Member Posts: 16,007
    Could be the expansion tank was waterlogged and the relief valve was scaled shut. Could be system was low on water because the pressure reducing valve failed and it had a leak of some sort and the boiler got low enough on water that the boiler heated the joint on the relief valve to the point where it melted the solder because part of it was dry firing. In either case it would be best to replace the boiler after either event.
    Did water pour out of the relief valve piping?
    bigjohnnymack
  • bigjohnnymack
    bigjohnnymack Member Posts: 9
    * Thank you
    Yeah The T & P valve and valve pipe it was affixed to shot right out of the top of the boiler . . Exploded boom.
  • bigjohnnymack
    * Thank you
    I tend to agree .
    Get a replacement gas boiler.
    Any suggestions on brand gas boiler.
    Thanks
  • bigjohnnymack
    * Thank you
    That Tele Larrs boiler was a good boiler. 30 + years old.
    It was used in heating swimming pools.
    Thanks
  • bigjohnnymack
    Thank you
    Sounds about right on.
    Probably scale clogged the
    Valves And T & P.
    Low Water - then hot steam -
    Boom - T & P Valves and valve pipe shot out - exploded.
    Looking For Replacement Gas boiler. Burnham , Weil McClain , Crown , Utica . .
    Thanks
    I assume it uses a HX to heat the pool water?
    You should probably stick with the same type boiler if it worked. Larrs or RayPac also make them
    Mad Dog_2bigjohnnymack
  • Mad Dog_2
    Laars makes a great product & fantastic tech support & warranties. Mad Dog
    bigjohnnymack
  • bigjohnnymack
    Yay Good News
    30 year age Teleydine Larrs 130k btu boiler repaired
    up and running - heating house.
    Plumber boiler tech
    new valves
    replaced the pressure reducing water feeder valve
    replaced pressure relief valve
    replaced expansion tank
    installed air vent on water supply feed ( never had air vent valve )
    replaced vent ( chimney pipe )
    valves replaced had clogged up over 30 years of use and no maintenance checks
    clogged up valves caused water blockage depriving boiler of water
    causing steam buildup
    resulting in clogged pressure relief valve malfunction - with pressure relief valve explosion shutting down boiler
    price of repairs $1,200 -
    * still no low water cut - off valve
    never had one - can a low water cut - off be installed
    happy repairs thanks all
  • bigjohnnymack
    Lesson learned . .
    do annual check up on boiler by
    HVAC plumber tech
    * if the FHW baseboards are
    sounding like you hear water gurgling thru the baseboards
    ( air in the pipes )
    and no heat to separate zone to the second floor of house
    when operating the boiler
    it's time to call the HVAC plumber tech
    to avoid boiler shut down
  • bigjohnnymack
    Question . . December 15, '25
    the city has contracted a utility contractor to take out from the street to the house the old water supply line and replace with a new water supply line , from street to house
    With the disconnecting of the main water supply feed to the house cause damage to the FHW gas boiler and gas hot water tank ? ? ?
    What precautions should be made . .
    Shut down the boiler and hot water tank ? ? ?
    While contractor disconnects old water line and installs new water line ? ? ?
    If shut down gas FHW boiler and hot water tank.
    What has to be done to put the gas FHW boiler and hot water tank up in running . . .
    any bleeding air out of the systems required ? ? ?
    I told the city why is the work being done at the beginning of the heating season , in middle of December - with temps in the teens o's . . when the house needs an up and running heating system.
    I told the city to do the work at the end of the heating season . .
    thanks for any advice
    hot_rod Member Posts: 27,075
    the boiler should have a fill valve with backflow preventer. As such the water and pressure in the boiler should not be affected by a water line shutdown. Unless the heating system has a leak?
    It’s possible the entire home has a backflow device or a PRV that acts as a check valve?
    The low water cutoff on the boiler would be the next layer of protection. That could be a probe into the boiler, or even a pressure switch which cuts power off to the system drains or drops below a pressure. It prevents dry firing, should the boiler drain completely, which is rare.
    Or just risk it, and do nothing.
    turn off the hot water heater but the boiler will be fine unless you have a huge leak in the system.
    edited December 2025
    test the pressure relief valve regularly. lift the handle and see if water comes out and if it stops when you release the handle. do it when you don' need heat so if it doesn't shut you have time to replace it. make sure the pressure reducing valve keeps the system pressure up after doing that. not a terrible idea to just replace the relief valve every 5-10 years either.