Packing Heat
    hot_rod Member Posts: 27,205
    edited February 2025
    I’d venture to guess even the brightest know it all gurus on this thread have tried and failed at energy projects along their careers😏 Pushing boundaries is one way to learn and expand.
    It’s your money, your property you get to try whatever you want.
    BTUserLarry Weingarten
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,057
    Hi, I'll add that I went a few rounds with Martin Holladay on this and ultimately, it depends on the assumptions you make going in. I have been able to greatly reduce the cost, complexity and labor involved to build solar thermal DHW. I'll add that there is no one-size-fits-all. My system works in a temperate climate. Martin had a hard time accepting the measured data I gave him, so continues to believe solar thermal is dead. I'm seeing it give a rate of return around 25%, with a life expectancy of at least twenty years. Blanket statements only keep some people warm.
    Yours, Larry
    BTUserhot_rod
  • BTUser
    BTUser Member Posts: 41
    58f is the average low during the hottest part of the summer. Indeed, we open the windows and run the whole house fan most summer nights. It definitely delivers a lot of cooling. But, not nearly enough to get us through the 98f average highs. By midmorning, the house is often roasting without AC.
  • BTUser
    From another arena, renowned quantitative trader & mathematician Ed Thorp on the subject of Technical Analysis:
    You can’t prove a negative. I can’t prove it doesn’t work. All I can say is that I did not see enough substance there to pursue it. I didn’t want to take time to try things unless I thought they were pretty good.
    Love that framing.
    LRCCBJ
    Solar thermal is not fact not dead, doubt it ever will be.
    I spoke with Sun Earth at AHR a few weeks ago, plenty of projects still be designed and installed. New technologies are being applied like the Viessmann ThermalProtect absorber coatings.
    True the residential boom once again came and went, like the two previous.
  • Kaos
    Kaos Member Posts: 854
    Larry,
    I can get a 4 of 400W PV panels and connect it directly* to a 48V heater and make hot water any time, without over heating, no freezing issues, no chance of leaks and no max temp drop in cold weather for less than the cost of the plumbing bits to hook up the solar thermal collectors.
    I really can't see how anything solar thermal would be cost competitive.
    That array of four panels would cover most peoples daily hot water needs a good part of the year on most days.
    *you do need an aquastat (can use the one built into the tank) and a pair of 48V rated dc contactors, if you want better efficiency also include MPPT. This is not the best use of PV, much better to put those 4 panels on microinverters connected to the house and use a regular resistance tank, comparing making hot water only.
  • jumper
    jumper Member Posts: 2,516
    The only solar thermal heating besides pool heaters that I've seen operating for years is direct air heating. I forget the name of the company. It blew solar heated air into industrial buildings where ~60° sufficed. When sun did not shine then good old NG kicked in. If your entire roof is covered with solar panels then you save something on your A/C use. Otherwise Contrarion & Kaos observations match mine.
    DCContrarian
  • Larry Weingarten
    Hi @Kaos , The assumptions we use really do matter. To start, here's a link to a Consumer Affairs report on the cost of PV. https://www.consumeraffairs.com/solar-energy/how-much-do-solar-panels-cost.html If I go with a lowish number of $2.50/watt, your system, without the tank is $4000. I don't know what percent of the total hot water needs it meets is, but let's say 90%. That's what the thermal system I play with delivers. The tank for my system was about $1000 and the balance of system, installed was $3000. If one wanted to make their own collector, they could save over $1000 with one or two days work. My system is freeze tolerant, but is suited for a temperate climate. As thermal captures roughly four times the energy per square foot of collector, it doesn't have to occupy all of the roof space that PV does. So, there are valid arguments for both systems, depending on climate and usage. In terms of up front cost, seems to me this thermal system wins. Maintenance over the last nearly ten years has been essentially zero as well. With what I've experienced, I feel it would be a dis-service to just nod and let it go.
    Yours, Larry
    4- 400W modules, 15-18% efficiency, produce maybe 6 kw over course of a day . Depend on the tank size, that will be a slow go to heat or recover a tank of water. PV modules degrade over time, thermal do not.
    I do agree with the simplicity of the Sun Bandit PV to thermal, both parts and installation.
  • Kaos
    edited March 2025
    I'm not sure if it is good to talk about installed costs as these are all over the place. Much simpler to do BOM costs. Labor for either option is close enough in the end.
    Solar Thermal:
    -indirect
    -drainback tank
    -twin pumps
    -diff controller
    -insulated csst tube
    -pile of fittings/valves
    PV
    -larger resistance tank
    -48v element
    -aquastat/relay/fuses
    -wire/conduit/roof junction box
    -small DC combiner
    Welcome to price it out, but I would guess the two are out by a factor of 2x to 3x.
    @hot_rod The goal for any of these is not fast recovery but to make enough average heat over say 2 or 3 days to cover your daily load. In both cases there would be a regular 240V element for high use/low sun days, so speed of solar recovery doesn't matter.
    In my area 4x400W makes on average 8kW/day. It won't cover DHW every day but will most days plus unlike solar thermal, if using micro inverters, the excess PV in the summer is not wasted but goes to the house.
    If you now change to a HPWH, the math gets even better as you need 3x less PV. Hard to argue with the math at point.
    No, I get your point on the math. The cost is in the eye of the beholder. Statements like solar thermal is dead really does little to help the industry. It will be dead when the sun no longer shines I suppose😮
    There are pros and cons to both methods of generating DHW from the suns energy.
    The selling feature of PV to DHW is that it didn't involve connecting into the grid, no interaction with the utilities, engineered permission, licensed electrician obtaining permits, etc. It is attractive as a stand alone system, somewhat installer friendly for the average handy homeowner.
    Unique to HH is most of the folks are capable of doing their own installs. Some with the tutoring of the experienced talent present here.
    I'm not sure discouraging someone from trying something different based on what the should spend or ROI, is true to the motto of HeatingHelp?
    Has everyone of you projects penciled out financially?
    Present out the concepts, the thermodynamics, the physics, the math, let digest the various opinions, then decide how to spend their $$.
    Larry Weingarten
  • Kaos
    edited March 2025
    Sometimes we have to stand back a bit and figure out what we are trying to accomplish. My point is that making heat from the sun with PV is cheaper now and simpler install. If not connected to the grid, you can DIY PV.
    @BTUser for example is designing a new house in a very mild climate. It might be worth it to look at what the building loads can be reduced to with minimal effort.
    Something that is code min up here in the Great White North (2x6+R5 exterior rigid with decent windows) will get you near passive house levels of energy intensity in that climate. With proper orientation and window location with engineered overhangs, the building load will be low enough that you can probably heat the whole place with a space heater.
    Better question to ask, if building in that mild climate, where one should spend their engineering effort and dollars. I don't think complicated mechanical system is the best place.
  • DCContrarian
    DCContrarian Member Posts: 1,449
    @Larry Weingarten : "As thermal captures roughly four times the energy per square foot of collector…"
    I've seen that claim thrown around. I went a long way down the road with evacuated tube collectors (which at the time were the most efficient available) about 15 years ago, even going to the point of calculating detailed month by month estimates of production. The output of solar thermal is highly dependent upon outdoor temperature.
    In my climate (Washington, DC) in July, when the average daytime high is 88.3F, the collectors have an efficiency of 62% with a water temperature of 120F. The PV panels that are available today typically have efficiencies in the low 20s, so that's maybe three times as efficient.
    However, in January, when the daily average high is 42.5F, the efficiency of solar thermal is only 46%, so about twice nominal PV.
    Conversely, the efficiency of PV is highest when the temperature is low, and drops as the temperature rises. PV panels typically have a temperature coefficient around -.4%/C, so with a 46F (25.6C) change between July and January you get about a 10% increase in efficiency. Nominal efficiency is measured at 25C /77F, so in January you could well be getting 30% or more efficiency from PV panels. Thermal is still more, but now it's only 50% more.
    Where I am there is 3.3 times as much sunshine in June as in December, but a thermal solar collector produces 4.1 times as much in July as it does in December because of the effect of temperature. (June has more sunshine than July, but July gives more heat because is warmer out). PV on the other hand produces about 2.2 times as much in June as in December, due to the temperature effect.
    As I wrote upthread, the biggest problem with solar thermal is trying to size the collectors to deal with the seasonal variation in output, and then dealing with either the shortfall or the excess. Even if you just use PV as a replacement for solar thermal, the temperature effects make that a smaller problem. But there's also a fundamental difference, in that the surplus that a PV panel produces is electricity, which is useful in all kinds of ways, as opposed to heat, which takes active effort to vent safely. And even if you don't have a use for the surplus electricity you can safely limit the production of a PV panel simply by not attaching loads to it.
    Jamie Hall Member Posts: 27,167
    The rumbling noise you hear in the background is William Shurcliff (an odd duck, but did know passive solar thermal heating for buildings) and my father-in-law (another odd duck, but he and I designed and built passive solar homes and buildings, about 50 years ago now).
    They worked. Simple as that. But… nobody believed it. Bill died, and so has my father-in-law, and I have other things to do.
    Larry Weingarten
  • Larry Weingarten
    Hi, "As I wrote upthread, the biggest problem with solar thermal is trying to size the collectors to deal with the seasonal variation in output, and then dealing with either the shortfall or the excess." … It required some backerwards thinking, but I got around these problems by using inefficient collectors. The inefficient part matters. Even at stagnation on a summer day, they don't exceed 170F, so no overheat protection is needed, just a tempering valve. Being NSF rated poly pipe, they can freeze without damage. So, I oversized the systems collector to storage, and this allows even a little sun in winter to quickly bring the tank up to a usable temperature. This isn't a system for New England. I've measured temps from 18 to 109 here and this solar works. It's far less complex and I think more durable than the PV plus heat pump approach. I've used Marathon tanks so they don't even require anode replacement. Anyway, hope that helps. This solar thermal is just different.
    Yours, Larry
    ps, By the way, I had some fun correspondence with Bill Shurcliff. He was a very clear thinker.
    edited March 2025
    Bill was indeed a very clear thinker. I didn't always agree with him, but he certainly challenged one to think things through! He also was just plain delightful to be around. I wouldn't say I knew him well, but the few family dinners we all had together are fondly remembered. He had a wicked sense of humour!
  • Kaos
    edited March 2025
    @Jamie Hall The reason passive solar disappeared is because of thermodynamics. To get heat into the structure, the temperature must go up. To get heat out the temperature must drop. No way to engineer your way out of that temperature swing without active means.
    Best case scenario passive solar houses ended up the hottest by the evening and cold by the morning. This is exactly the opposite of what most of the population would want. Well designed passive solar did save energy for those that were willing to live with that, the issue is most people would not. That is the reason that super insulation won out in the end, well insulated house created a place that had low energy use but would keep the occupants within the temperature range people like.
    For my own home I installed limited passive solar design ideas. Went so far as to optimize the coatings on the south facing windows which reduce yearly energy use by about 2% (which seemed like a steal as it was "free").
    The heat would not need to run during most days but it also meant that even on a cold sunny day the house would get up to 80F by the afternoon, many days I was walking around in shorts in the middle of winter. Luckily a manufacturing defect meant I got all the windows replaced, this time around I speced low solar gain and better U value glazing. Everything is better in terms of comfort. The house still get a boost from the sun but no more overheating and cooling loads are way down.
    A very light sprinkling of passive solar is a good thing. Too much and you are asking for trouble.
    As they say, can't fight thermodynamics.
  • DCContrarian
    @Kaos , your house sounds a lot like mine. On a sunny winter day my house will get up into the mid-70's, it's 32F right now, my heat hasn't run since 9:35 this morning. Lots of south-facing glass and deep overhangs.
    But I'm not kidding myself. By my calculations those windows break even compared to an insulated wall. Sure they absorb heat during the day, but they lose more heat at night than a wall. If what you want is a window, having one that breaks even is a great deal. But adding windows to get more solar gain doesn't get you anything.
    Passive solar was big in the 1970's. One thing that has changed a lot since the 1970's is what is considered well-insulated. A typical house from the 1970's would be considered barely insulated today. Joe Lstiburek summarized what has happened: “We were here in the late 1970s when ‘mass and glass’ took on ‘superinsulated.’ Superinsulated won.”
  • BTUser
    Well I appreciate that the solar thermal is dead people are trying to prevent me from wasting my time and money. But they have registered their concern many times over and the arguments they have been raising here are ones that I've already come across and pondered. And I landed at a different conclusion from them. To the extent that they're continuing to address me in this thread, I don't find their comments discouraging so much as off topic. My decision is already made as far as the general direction I'm pursuing. I'm not interested in going the PV route. I thought I've been clear about both from the beginning and reiterated it several times by now, but I guess I still haven't gotten the message across.
    No, it's an existing house that I'll be retrofitting. I said that at the beginning of the original post. Fact of the matter is I lost you at "solar thermal." This is why I've had so little to say to you guys: You are not interested in the project! And yes, building envelope upgrades are also already part of the plan. Anyway I am bored to tears by the pv vs thermal debate and so I'll take a stab at taking it out back and shooting it, at least for the purposes of this thread. So I propose you guys table the topic, let anyone who is interested in the project discuss and we'll see how it goes. And then 5 bucks says I can make some version of the above pencil out as a stronger option for my circumstances than PV and ASHP. Calling you out @Kaos! $5.00 USD.
  • DCContrarian
    @BTUser , it's a fair criticism that because better options exist doesn't make something else a good option.
    The traditional way of looking at energy improvements is to look at the payback period. When I say PV is superior to solar thermal, what I'm really saying is it's going to have a shorter payback period.
    You say you don't want to look at PV. That's fine, it's your house. But when you're assessing a design, what are you going to look at if not payback? Because how can we help you if we don't know what's important to you?
    I went back and read the whole thread after your last posting. There's very little about what you're trying to accomplish, almost all you've written is how you want to do it. In the first post you did write, "All I'm looking to do is be able to hang on to a little sunshine during winter storm systems that sometimes last a week or so." That's not a lot for us to go on.
    If you've already decided how you want to do it I'm not sure why you're posting here.
    edited March 2025
    "My mind is made up and this is what I'm going to do" is, frankly, a rather poor way to learn anything, @BTUser . As @DCContrarian said, why did you bother to come and ask questions at all, or was it just to affirm your ego? We all learn something from each other, and from discussions such as this thread, but if you're not interested, that's your puppy.
    DCContrarian
  • BTUser
    I'm basically optimizing for ROI or you could say total cost of ownership. That's all things included: capital costs, expected maintenance, reduction in costs that would otherwise be paid to the utility. The same overall objective I think most of us would optimize for, without splitting hairs I don't think we have any disagreements on that. Where we disagree is that you view it as a foregone conclusion that the approach I'm describing will not pencil out as the superior option, while I see potential worth exploring.
    I have decided on the general direction of trying to make a large array of solar thermal collectors cover the majority of my annual DHW and space heating load, and also to use the same array to cover the majority of my annual space cooling load by way of night sky radiative cooling. I've decided to implement radiant hydronic heating and cooling, by way of flooring on the slab on the first floor, and ceiling panels on the second floor. I'm exploring how best to gain some kind of thermal storage/flywheeling the slab in the process. And finally, this approach will be complemented by additional thermal storage which I'm still exploring. This may involve a water tank but I will continue to explore the possibility of the namesake of this thread: Packing heat from the solar array into the ground of the crawl space by way of something like pex tubing/hydronic paneling.
    That's the vision I remain optimistic I can make work. Now, the details of how to implement it I haven't got figured out at all. And in that department, I have already received a ton of help in this thread! It's just that the whole situation looks different from the point of view of people who still see potential in solar thermal. They have been chiming in and addressing all kinds of issues and questions that come into play with all of the above.
  • DCContrarian
    Fair enough. Have you calculated your current heating loads? Either through modeling or the process outlined in this article?
    https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler
    Do you know your heating and cooling design temperatures, and heating and cooling degree-days?
    Have you looked up average monthly insolation for your location?
    Without that information you can't even begin to look at a design.
    BTUser
  • BTUser
    Hi Jamie!
    ah man. I have enjoyed your posts which I’ve encountered over the years as a HH reader, sorry to hear it’s being taken that way. I think there’s more to the story, for instance in Kaos’s first post in this thread he asserts “we both know thermal solar is dead except for pool collectors.” Will you apply the same criteria there? Because that sure sounds to me like his starting point is that his mind is already made up. And I don’t judge him for it, I just respect the fact that he has made a judgment call that the bottom line is there’s nothing there.
    But can you blame me for lack of interest in engagement from that explicit starting point? Throughout the thread — because advocates of PV keep circling back to why they think PV is a superior option — I have periodically stated my rationale for not going the PV route, indicated that I’m not looking to convince them otherwise, and sought to respectfully bow out from spending my time on that subject. They don’t seem interested in taking no for an answer.
    Up to you what you make of where I’m coming from. But closed-mindedness is not the driver of every decision to not continue to spend one’s time on a topic — particularly polarizing ones!
  • Larry Weingarten
    Hi All, I'm probably about to sound silly, but please bear with me. My experience is the most cost effective things you can do to make any heating/cooling system perform is to have a superior shell, so the loads remain small. It's hard, but possible to reduce the loads by 80% with good design, air sealing and insulation. Yup, 80%! If you could get anywhere near that number, any flavor of solar works and is easier to accomplish.
    My climate is predominantly heating, but by reducing South and West facing glass, and thinking about low-E glass appropriate for each orientation, I've minimized the problem of overheating. A reason I like to use water as my thermal mass is it can be moved around, but importantly, I don't want to live inside of a solar collector with its temperature swings. I live in a low-mass house.
    I have played with a variation of solar cooling, but never completed it because the house works without. The cooling was to have unglazed solar collectors placed higher than a well-insulated storage tank, and filled with an antifreeze mixture. The tank is placed just above the living space and tied into finned tube baseboard elements. Both fluid flows are driven by convection. Thermostatic control for the finned elements is given by a wax filled piston operator, driving a ball valve. It's the same system I use for controlling a gravity driven heating system that I did build, and it works. During the day, the collectors get sorta hot, but do nothing. On a clear night, they radiate heat and convection moves the resulting coolth into the tank.
    I got ridiculed when I started to build my place 25 years ago because I used SIP panels, which people didn't seem to understand, and because I used 8" walls, 10" floors, and 12" roof. They told me I was nuts to be that well insulated. I was building for the life of the structure, not current energy prices. Anyway, it doesn't seem so crazy now, and my energy use per square foot is 10% of normal. Hope some of the above is useful.
    Yours, Larry
    LRCCBJBTUserPC7060
  • DCContrarian
    @Larry Weingarten : "Yup, 80%! If you could get anywhere near that number, any flavor of solar works and is easier to accomplish."
    I agree very much with the general sentiment. I'll add that a well-insulated house is just more pleasant: more comfortable, quieter and less dusty. I like to say that an ounce of insulation is worth a pound of hydronics when it comes to comfort.
    But I have to disagree with the statement that "any flavor of solar works." There are lots and lots of failed attempts at passive solar and heat storage out there, what Joe Lstiburek calls "mass and glass." Sometimes they work, a lot of times they don't, and when they do work it's mostly because of the conditions at the site, particularly the climate.
    Installing one of these systems isn't like putting a deck on a house, where you just have to follow some basic guidelines and it's going to work, and the design involves mostly deciding whether you like deep and narrow better than wide and shallow, or whether a square works best for how you see yourself using it. I'd say it's more like building a hydro-electric generator on your property. Before you even begin, you have to ask, do you have water flow? How much? And how much does it drop? And do you have the right to build on it? Because if you don't have those things, there's no way to make up for the lack.
    This is what's behind the questions I asked three posts ago. Without knowing specifics of the energy use in this house, in this climate, it's impossible to do any of the calculations that would tell if some sort of heat storage would make sense at all.
    BTUser
    I've heard stories of creative tinkers coming up with passive radiant system and controls. A good place to store some vodka also. Here's to them😎
    Hopefully the ROI passes the beancounters math :)
    Screenshot 2025-03-02 at 5.07.20 PM.png Screenshot 2025-03-02 at 5.07.31 PM.png Screenshot 2025-03-02 at 5.07.41 PM.png
  • jumper
    Regarding big south facing windows. You can cover them at night to reduce heat loss. How about big uncovered windows on north side? Put thermostat there and heat will be roaring in morning. Nice.
    President Carter had a sweet way to reduce heating cost. Lock thermostat at 55° and tell your pampered family to suck it up. I knew Canadians who survived in unheated homes except for kitchen.
    Let me say a word (again) about passive thermal solar or whatever.
    The most important word is that trying to retrofit passive solar is… I've never seen it to work well. The house — or other building — has to be designed for it from the ground up, and architected to fit the site and the conditions. No two will be quite alike. There are also some real "gotchas" in the game as well — the most obvious of which is controlling overheating, which can be a real problem in the "shoulder seasons" — mostly because from the solar standpoint the sun angles are the same in the fall — when in most cases you don't need much heat — and in the early spring when, at least in most climates, you most assuredly do. So what keeps you warm in say March is going to keep you really toasty in, say, October.
    Storage is not a problem — if it is designed in from the start.
    Second, most passive designs which work aren't, really: almost all of them, if not all, depend on some forced air movement if only for adequate air exchange for air quality considerations.
    Most are also designed, quite deliberately, to have some warmer spaces (e.g. studies, living areas) and some cooler spaces (e.g. bedrooms). They don't have to, but it makes life a lot easier.
    I have real problems with what might be called active solar thermal systems — not that they can't be made to work, but it's not really just a matter of some pipes on the roof. The biggest problem I see with them is heat storage, and transferring heat in and out of the storage in a controlled way.
    PV in my view is interesting. If — and only if — you have enough area for a big enough panel array, there is no reason why it can't work — but again, the hitch has to do with storage; only in this case it is obtaining adequate battery capacity and ensuring that that is safe. If you are using PV for heat, you need a LOT of battery storage, unless you are grid connected — and there you may run into some interesting arguments with the rules from the public utilities commission in your State (many of them get difficult if you are trying to generate more power, over the year, than you use, over the year, and there may be limits on the installed capacity).
    Oh and just one more thing — when the title referred to "packing heat" my thoughts went to the Anaconda or Python which sometimes ride on my hip, and I wondered what we all had gotten into…
  • Larry Weingarten
    Hi @DCContrarian , The concept of installing a solar system that doesn't work didn't even occur to me. The basic thought was that with solar, you expect to have less energy to work with, so not leaking it out in various ways is a good thing. And yes, every system needs to be matched to the place it lives… more-so for space heating. I've watched "solar" since the late 1970s, so have seen what was built and how it later got changed to help it work better. I prefer to learn from other people's mistakes, if possible. I both designed and built my place, so site conditions and weather data were taken into account. Designing a low mass house, some sort of storage was essential as I'm off grid, and needed something to even out the diurnal temperature swings. Also, I needed to know how many days of energy storage were needed. Lots of moving pieces. Doing heat loss calcs on a room by room basis allowed me to design the radiant system @hot_rod was so nice to pull up pictures of. Just as an aside, much of the math for it came out of books from the late 1800s and early1900s. I suppose I could have skipped all the work and just wear sweaters by the fireside 😏, but I didn't quite follow Carter's lead. For a while, I got to be my very own lab rat. But the ideas I wanted to test out seem to work, so my nose is less pointy now, and just possibly there are more strategies tested and available for others to use.
    Yours, Larry
    ps, I did get a bid on doing conventional forced air and my system, (with me doing most of the work) came in at 1/4 the cost.
  • BTUser
    Thanks for the link! Handy as a quick and dirty. I may start with that. Have not done load calcs, partly because I was planning on having a pro come in and doing the job right, and also because I plan on going after all the cost-effective upgrades to the thermal envelope before doing any of the rest. But maybe I will start modeling it out here and with the help of HH I can get a pretty good idea of current load calcs, which envelope upgrades will be worth doing, and what the loads will look like after they're in place. I know we've been averaging about 3.5 therms a day over the last couple months. 3000sqft house. I don't anticipate there will be reasonable ways to upgrade the thermal envelope sufficiently to make the rest of the project not worth doing? But that's nothing more than an uninformed guess, I could be totally wrong there. If cost-effective envelope improvements are able to bring this existing house's energy needs waaaaaay down, it's not going to make sense to go the route I'm talking about. I have envisioned it specifically as an alternative to something like an enerPHit or other deep energy retrofit. ie, for existing houses where it's simply too expensive to drop energy needs by anything approaching the 80% Larry mentioned above.
    From my solar PV report (again, I already do have a bunch of existing PV, 18x360 Sunpowers, 6.48kwh system), I know the monthly solar access on my south (20 degree) roof is 85% in Nov & Dec, 87% in Jan, 88% in Feb. For the other months, it's 93% +/- 1%. The Annual TOF for that roof is 97%; I don't have it worked out monthly but am less concerned, because the panels could be tilted a little to optimize around the (relatively narrow) elevation and azimuth that the sun traverses during winter days. Again, the winter months are key for this design, as it is all about capturing whatever heat is available during winter. I came up with 1155 BTU/sqft average daily solar insolation at winter solstice, that's after considering winter cloud cover patterns, but that is also only a quick and dirty napkin estimate. During the summer, the solar insolation numbers won't matter at all, as the system will be way oversized for summer DHW needs. During the summer, what will matter is the array's night cooling capabilities.
    One thing that has caught my interest is how little interest has been expressed here is how little interest has been expressed in the potential of solar arrays for providing cooling BTUs. Although I see Larry was going that route but ended up not needing it. This seems huge to me, again my numbers have an array optimized for winter heating and summer night cooling delivering 1000 BTUs/sqft/day of heating during peak winter, and equal amounts of cooling during peak summer. To me these challenge the problem of more conventional solar thermal arrangements that you and others have (correctly) pointed out: Sized correctly for winter, they are mostly useless at best during the summer. The numbers are far from certain but the modeling is probably more sophisticated than you think. Next step for me is to use one of the solar-oriented programs @hot_rod pointed me towards to find out if my wireframing is anywhere close.
    Anyway thanks for helping me with the nitty gritty on the hydronic+solar approach, even if you think that overall it's not going to be the way to go. I certainly recognize that you may be correct.
  • DCContrarian
    @BTUser : "One thing that has caught my interest is how little interest has been expressed here is how little interest has been expressed in the potential of solar arrays for providing cooling BTUs."
    I had never heard of anyone doing this, I did some googling and couldn't find any examples of it being done.
    My quick take is that you're going to be doing a lot of heat exchanging: fluid flows into the collector and exchanges heat with the night sky, then flows into some sort of storage medium and exchanges heat there. Then during the day some sort of fluid flows between the storage medium and the interior, exchanging heat at each end. So at least four exchanges. Temperature delta is the key to heat exchange, it's what makes heat flow, and the overall temperature delta is going to be pretty small, it's basically the difference between the inside temperature and the nighttime outdoor. And that delta has to be split over four exchanges.
    The amount of heat transferred is equal to delta times flow rate, so with the small deltas you might need quite substantial flow rates, which might mean sizing the system significantly larger than what is needed for heating. I would also think that a solar panel's ability to radiate heat would be substantially smaller than it's ability to absorb sunlight, because the temperature difference is so much smaller.
    Do any ratings exist for panels used for cooling?
  • BTUser
    edited March 2025
    Here is an article rating cooling capacities of various solar thermal collectors by Bristol Stickney, an engineer out of Santa Fe. Unfortunately the image with the cooling ratings and the names of the panels is blurry, but at least you can get the gist.
    http://www.solarlogicllc.com/Articles/pe01_2009%20extracted.pdf
    Stickney was producing content on this subject in the 2000s and 2010s, and had been incorporating nighttime cooling functionality into all his installs as a matter of course for many years. He was a proponent of what he called "solar hydronic combisystems" and installed many of them. They are basically validated implementations of what I've described here, less my (questionable) twist of trying to extend it by packing heat into my crawl space. I've tried to contact Stickney but contentwise he seemed to fall off the map in the late 2010s and I haven't been able to reach him. If anybody ( @Larry Weingarten or @hot_rod perhaps?) happens to have contact info, I'd be interested.
    Agreed. I spent some time studying this matter. If you google "dual-purpose solar thermal collector" or something like that you'll eventually come across various approaches being tried to increase cooling capacity without compromising heating capacity. I didn't love any of the approaches, because they would all be significantly less performant than an idea I proposed above: Flat Plate collectors with a seasonally removable enclosure. These would basically be something like the Gull 4000 linked to below, with a greenhouse like box that fits around it for heating season. During the winter, it appears to be and functions indistinguishably from ordinary glazed flat panel collectors: enclosed, insulated, and enhanced with IR rejecting film — all standard fare for glazed flat panel collectors. During the summer, it's sheet metal bonded to copper tubing: exposed to the night air and wind on both sides, uninsulated, and maximally emissive of IR heat. My numbercrunch puts that configuration into a different ballpark from other collectors. Simple harp-shaped pool collectors probably come close but I haven't come across any that specifically optimize around cooling. Metal like this Gull 4000 would improve their capacity to discharge heat at night despite the small temperature differentials.
    I think you're right about all the heat exchanges being a key challenge here, and now you're getting to the edge of where I've worked things out conceptually. Some thoughts: Radiant flooring in the bottom story of a slab on grade house offers a way to get a 2 for 1. First and foremost its job is to maintain thermal comfort on the first floor, but it also stores heat (or cold). With close to 1000 square feet of room on the slab of our house, that's a lot of heat transfer surface area. Compared to eg coils used as heat exchangers in water tanks, 1000 seems like it could move some BTUs even at fairly low temperature differentials. First approximation numbers looked promising. And for the downstairs interior, since the slab largely is the entire needed thermal energy store, that basically cuts it down from 4 to 2 exchanges.
    But for the upstairs, yes I'd be (summer example) moving heat from interior to TES all day, and then TES to solar collectors all night. 4 exchanges like you said, and no handy 2 for 1. Name of the game to make this work will be outside of the box thinking to see how little temperature differential I can make it work with, at all 4 exchanges. Above I mentioned the thermal collectors with seasonally removable enclosures to significantly enhance summer night cooling capacity, that is one example. Got some ideas for the exchange into the upstairs interior, too. No bright ideas yet for the two exchanges that take place at the TES.😁
  • BTUser
    Love it Larry! Gotta make myself go to bed now, but I took a look and am intrigued. Can't wait to return to these with rehydrated eyes in the morning.
  • BTUser
    @DCContrarian
    Your question got me thinking about whether it may be possible to hack the thermal efficiency equations on the SRCC listings to answer this question. Like this:
    Plug in 1 BTU for solar irradiance. For this panel, 68f inlet water and 59f ambient air produces an instantaneous efficiency of -7459%! Lol. That’s keyed to the supposed 1 BTU of irradiance, so -74.59 BTU/h/sqft. Unless the moon is shining really bright, we then would need to subtract out the fake 1 BTU of irradiance, leaving us with a cooling power of about -76 BTU/h/sqft.
    Unsure if the hack works, still puzzling about the (1-b_u*u) factor. But it seems like all the elements are there in their formula: radiative heat loss, convective heat loss, wind speed. So I bet there’s a way to use it, at least as a first approximation. Maybe some of the professional solar software Bob mentioned uses a similar approach to calculate cooling?
  • DCContrarian
    In the Bristol Stickney article he talks about how to calculate the heat loss of a solar panel at night.
    Because the universe is quite cold, a surface exposed to the night sky can cool below the air temperature. Stickney calls this the "white plate" or "T Plate" temperature.
    He writes:
    When measured at night, “T Plate” will almost always be found between the dew point temperature and the night air temperature. During the testing phase of this project, we measured these temperatures every five minutes with data loggers and produced nightly averages time, and time again. The goal was to find a long-term average correlation for our climate, shown as “C” in Figure 2. “C” is shown at the midpoint between the dew point and the air. This is not a bad assumption, since our test results show an average of 0.441 when all our bench test data is combined, and an average of 0.488 when all the field test data is included from the summer season of 2005. On very clear nights the value is lower and during unfavorable conditions, the value is higher. But is seems that on the average, a value of 1/2 will yield reasonable results when used as a rule of thumb.
    He found that the heat loss, in BTU/hr, of a surface with temperature T could be given by;
    (area)*(T-Tplate)*U
    Where U is the U-factor, a measure of ability of a surface to lose heat. He calculated the U-factors for 11 different kinds of radiators. Unfortunately the table of values is too fuzzy to read in the PDF, but he says that all of them are between 1.0 and 2.0 in the text.
    So let's say at night it's 60F, dew point is 50F so Tplate is 55F. Indoor temperature is 75F. With a U-factor of 1.5 you'd get 30 BTU/sf/hr.
    But that's not sustainable. You want to be reducing the temperature of the interior so that you've saved some "coolth" for the next day. So if at the start of the night your interior reservoir is at 75F, by daybreak you want it to be at 55F. So your average temperature over the course of the night is more like 65F. Which gives more like 15 BTU/sf/hr.
    BTUser
  • DCContrarian
    My guess is a 3,000 SF house would average about 30,000 BTU/hr cooling load on a hot day. Figure you'd have about 10 hours of cooling, 10 hours when the outside panels are cooling (that's what Stickney figures) and four hours of in-between. So you'd have to move about 300,000 BTU out at night and then absorb them during the day.
    A floor that is below the air temperature will absorb about 1 BTU/hr per degree of difference between air and floor. If we assume the same 75F interior temperature and 65F average temperature for the store, that's 10 BTU/hr, so you'd need about 3,000 SF of interior surface — 100% of the interior square footage.
    On the exterior, assuming the 15 BTU/sf/hr from my previous post, you'd need 2,000 SF of radiating surface. I seem to recall that the footprint of the house in question is only 1,000 SF so there would have to be some sort of outboard array.
    Note that ultimately it comes down to the difference between the interior temperature and the Tplate. You have to assume the same temperature for the heat store on both sides, because it's the same store. So if you make your heat store warmer, which makes the outside radiators more productive, that makes the inside delta smaller and your internal radiators need to be bigger.
    BTUser
    The night cooling effect is quite real — I've had a bucket of water get a skin of ice on it overnight, camping in the desert in New Mexico in July… but it does assume a very clear sky. Cloud cover, or even haze, will have a big effect.
    BTUser