I lost track of some of the old solar dogs.
Bristol, Boaz, and Joel had a company called Cedar Mt Solar, dod a lotn of unique solar thermal around New Mexico. I thinkmBoaz is still inn the PV side of the industry.
Bob Nape was another ST guy that did a lot of unique projects. He kept an online data logger comparing two systems on his roof. It would have some nightime data. Sadly I see he passed away a few years back.
This was a Cedar Mt Solar, I don't remember if it was a pool, or reject array.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Broadly agree, but I think we can push the numbers up a bit. Looking at the fuzzy picture it appears to me he clocked the best one at 2.15. That is presumably an exposed wetted plate collector. I'm uncertain whether that was an aluminum wetted plate, with maximally emissive coating. Point being I don't know that any manufacturers actually set out to optimize their panels for cooling, it's more that they incidentally happen to do somewhere between a poor and pretty good job. But it looks like at a dT of 20 we'd get 2.15 * 20=43 BTU/sqft/hr, and I think there's reason to think better is possible, though I don't know how much better. Still that's a ways off from my estimate that one could average 100 per hour; I suspect my estimates for wind speed explain most of the difference. In my area summer night winds average about 5 mph so that's what I plugged in to estimate convective heat transfer, but idk how that translates to average wind temps on the panels.
One thing to add is that it wouldn't be an average of 43 and 0 in the case of the slab. Maybe more like an average of 43 and 23. Planning for a very low R-value surface on the slab flooring, with pipes situated as shallowly as possible. We don't want to lower the floor temp below 66 (ashrae min for barefoot spaces), so Stickney's best panel would give us an average of about 33 BTU/sqft/hr.
My property slopes downward from the street. The bottom floor of my house is lodged into a hill on two sides; from the street, one enters onto the second story. As a result the bottom story should have lower design load needs than the top. Especially if we have used the spare production capacity from the array during mid to late spring for "Packing Coolth" into the ground below. I believe what will happen during summer daytimes goes something like this: The floor starts at 66f. As the interior heat accumulates, the top of the floor begins absorbing it and it starts climbing. But the more the temp at the top of the slab climbs, the more the bottom of the slab and then the earth to which it is coupled will conduct heat away. So it will climb some during the day but may still be manageable.
Note that this same effect changes the math from earlier in this post in a favorable way. The more one chills the slab during the summer night cooling cycle, the more the ground starts warming it back up. We are chilling the slab, but at the same time renewing the ground beneath the slab. This helps keep a little extra temp differential between the water flowing out of the array and the temp at the top of the slab as the night progresses.
I also plan to incorporate high efficiency ceiling fans into the design. These will boost max slab output beyond 1 BTU/sqft/hr of cooling, while also providing indoor wind chill and serving some other functions. In the context of this specific design, they become particularly handy for design conditions when the slab has climbed up a few degrees and we need to extract more cooling out of relatively high floor temperatures.
Again, that's for the 1000sqft or so of on the slab downstairs interior. It's less favorable for upstairs, but I think this can be used to our advantage. With little thermal mass upstairs, whatever TES we use to cool it will tend to reach higher temps by the end of the day compared to the downstairs slab. When the array starts pumping at night, it first cools the upstairs TES that has risen up to perhaps 78f, and then once the night gets cool enough it start circulating through both slab and TES, and then late morning once the slab gets down to 66 it focuses on bringing TES down as low as possible.
Thank you for giving me the benefit of the doubt by calling on me to walk you through my reasoning! Whether or not this thing can pan out, for me it is quite a fun idea and fun to talk about. And at this rate, if there are ultimately some fatal flaws in my plan, you will certainly track it down. I am being grateful for your time and engagement and not facetious when I say: You may yet end up saving me from a bad idea.
0 -
@BTUser : "In my area summer night winds average about 5 mph so that's what I plugged in to estimate convective heat transfer, but idk how that translates to average wind temps on the panels."
Wind will make the panels less effective.
The radiative cooling allows the panels to cool below the air temperature. Air blowing over them will tend to warm them to air temperature.
0 -
No I agree. It's a question of how much of the heating and cooling demand the solar-thermal array is well-suited to handling. With @DCContrarian closely eyeing the issue of temperature differentials as a possible achilles heel of the whole approach, consider the role of a water to water heat pump in the whole configuration. The heat pump could be used for backup and peak loads, but it could also be used strategically to increase temperature differentials in various ways. For instance, it could cover some of the interior cooling load and that process would raise the TES temperature a little higher, which in turn would increase the cooling output of the array at night.
0 -
»a water to water heat pump in the whole configuration«
Depends on climate each year. A pit or pond. In northern climate usually A/C heat rejection will not balance winter heat draw. Then you need to somehow augment with solar. Or gamble that next winter will be mild and summer will be vicious.
0 -
Depends on use case, doesn't it? If the system is engineered so that it can provide useful cooling needs with inlet water always a few degrees above air temperature, the wind helps. For this design, in the late hours of the night when the temps are down around 59, we still have a lot of thermal mass that still hasn't dropped that low.
0 -
If you're going to go with a heat pump anyway, we're back to the beginning of the thread and asking why you don't just have a conventional heat pump…
Putting that out of the way, if you want to go all mad scientist, a tank of water seems like the way to go. Or perhaps two tanks. During the day heat the water up to 100F* or so with the rejected heat from air conditioning, then at night pump it out to be radiated to the night sky.
Let's say it comes back at 55F, that's a 45F delta. If you need to move 300,000 BTU, that's 6,700 pounds of water or 800 gallons. With the water going out at 100F and a U-factor of 1.5 you get 67.5 BTU per square foot, which means you need 444 square feet of emitters. With a 45F delta you only need 1.3 GPM to move 30,000 BTU/hr.
The reason I say two tanks is that both the heat pump and the outside emitters will work better if the source water temperature is constant. If you have a hot tank that is always at 100F and a cold tank that is always at 55F, and have the heat pump go from cold to hot and the emitters go from hot to cold, they will work at maximum efficiency.
With a heat pump you can chill the water inside the house to 40F or so, which means you can use small pipes, pumps and emitters inside to get the cooling you need, no heroics required.
*(100F is just a guess, the actual number will depend on your choice of heat pump.)
0 -
In this case, the slab and TES would substitute in for the role that a pit or pond play in conventional geothermal arrangements.
0 -
In winter, you just reverse everything — the heat pump pumps from the hot tank to the cold tank and sends hot water around the house, the solar collectors take water from the cold tank and return it to the hot tank.
What I like about this scheme is that if it doesn't work you just replace the water-to-water heat pump with an air-to-water one. So there is a plan B if not everything works according to plan.
0 -
if you want to look at other ST/AC options.
There were some small absorption units that were powered by evac tubes. So you had winter heat, DHW and summer cooling. Solar Panels Plus in VA brought in a bunch of small absorption units. I don’t see them at their site anymore, just PV/AC units.
Bill down at Arctic Solar took the evac tube concept and wrapped it in a concentrated trough to get so very high temperatures for chiller power.
https://articsolar.com/applications/ac-refrigeration-dehumidification-2/
The only ST technology I have never played with was concentrated type.
Nevada 1 near Boulder City has been running since 2007, providing about 136GWh per year with a CSP plantBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Hi, A friend of mine designed efficient greenhouses. One of his tricks was to pull hot air from the highest point in the greenhouse and push it down through corrugated drain pipe buried in the soil under the plants. This cooled the greenhouse, warmed the soil, and condensed humidity from the hot air, putting it back into the soil. Again, perhaps something here could be of use.
Yours, Larry
1 -
If you're going to go with a heat pump anyway, we're back to the beginning of the thread and asking why you don't just have a conventional heat pump…
The issue is air. With air to air heat pumps, in the winter you may be pumping enough heat out of 30 degree air to raise the temperature of a coil to — idk the number, maybe 150 degrees? To then warm the air to maybe 120, and then it's down to 110 or something when it hits the registers. A heat pump lifting the temps 120 degrees seems totally the wrong way to go to me. COPs of 2 to 3 are not exciting when we'd have to get to an average operating COP of 5 just to match, on a dollar basis, what we currently spend on natural gas.
With an air to water heat pump you can at least load shift. Run it when rates are low and outdoor temperatures are high so your operating COP goes up. Out here we (for the time being) have relatively low rates until 3pm, peak rates start at 4p. Could run the heat pump from 10a til 4p and charge up your tank or whatever you're using as a TES. There's a significant improvement to be had there.
A water to water heat pump is the perfect complement to what I've been describing. Now instead of harvesting 55 degree winter highs like an A2WHP would, you're harvesting maybe 150 degree water from the solar panels. Using your scenario of two water tanks, at night when all the supply water for the hydronic delivery system to the house drops down to say 80, the heat pump kicks in to keep it at 80 by pumping heat from one tank to the next, but maybe the other tank only has to drop down to 65 to get you through the night, and once it drops to 70 you start letting the 80 degree tank dip to 75 (akin to scheduling the thermostat to drop 5 degrees overnight while sleeping). But now instead of having to pump heat 120 degrees uphill, you're talking about moving it single digits up the temperature gradient. Now we are in the territory of ultra low temperature lift heat pumps.
You know all those graphs we're always seeing showing outdoor temp vs COP for heat pumps? Usually ranging from maybe 1.5 to 3.5 with a slight arc. They always seem to cut off before the juicy part, but as the temperature lift required drops to very low numbers the COP ramps up exponentially. In theory, as the required temperature lift approaches zero, COP approaches infinity. Obviously there are some practical considerations that come into play such as the energy required to exchange the heat, which is one reason water on the delivery side also helps. Far less energy required to move the same BTUs hydronically than by forced air.
Anyway ultra low temperature lift heat pumps can't provide infinite energy for nothing, but when the pump is only pumping heat up single-digit temperature differentials, the COP will shoot up off the charts. We're talking less electricity by an order of magnitude, and significantly less wear and tear on the heat pump. And, this system is built around pumping heat up single-digit temperature differentials. You have highlighted the issue that the temperature differentials at various exchange points in my proposed system may be too narrow. Strategic incorporation of a W2WHP can widen those temperature differentials by a few degrees in specific situations where the increased differential is most useful. So we get heat on the cheap by operating at sky high COPs, and that heat is added tactically at points that garner the additional benefit of improving performance of other components at the exchanges. All this in addition to simply being available as a backup source during design conditions, and thus negating the need to size the array and thermal storage so gigantically that they could cover 100% of any possible heating and cooling needs.
The other thing the w2whp accomplishes is that it allows the TES to be useful even when it dips below the required supply temperature. In effect it increases the storage capacity of the TES. If I need 80f supply water for my house interior and my TES drops to 79f during the night, all is not lost. I turn on the heat pump to bridge the gap, and the electricity it consumes to do so ends up being a far cry from what an air to air heat pump would consume to provide the same amount of supplementary BTUs.
0 -
Yeah those absorption chillers are one tech that I haven't quite got my mind around. My understanding is they are fairly inefficient (20% or something?) but since your solar collectors are probably producing way too much heat during the summer, a 20% conversion rate is better than just wasting them. I suppose if the 20% number is in the ballpark and your collectors have a 75% solar capture efficiency, you can get maybe 15% efficiency out of the collectors when used for cooling purposes. Which isn't too far behind the 20% neighborhood for PV. There you go, still another way to make solar collectors productive during the summer.
0 -
-
You want fun?
How about, instead of two 800 gallon tanks of water, two
six120 [edited for math error] gallon tanks of calcium chloride phase change solution?See:
Let's say the hot side is at 120F, the cold side is at 55F. In the summer, the solar emitters pull from the 120F tank and dump into the 55F tank. The heat pump pulls from the 55F tank and dumps into the 120F tank, and provides 45F water to the house. In the winter, the solar collectors pull from the 55F tank and dump into the 120F tank, while the heat pump pulls from the 120F tank and dumps into the 55F tank and provides 140F water to the house.
Year-round the DHW pulls from the 120F tank.
0 -
Talk about a concept that doesn't pencil out for a small residential application :)
Although I think Richard @Derheatmeister just brought in a load of the Latento tanks. I'd like to see some of those get installed and observed.
Maybe he will donate one, or a dozen to your project 😏
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The SunAmp water heater uses a storage tank with phase change material:
0 -
I love these ideas but why don't we see more of them being applied? Even straight forward symbiosis like using indoor pool room dehumidifier for heating usually doesn't balance. You want wet bulb less than water temperature and dry bulb warmer. Go ahead and try.
0 -
Did a couple go rounds exploring PCMs. Definitely interested but there always seemed to be some drawback, discharge cycle limitations etc. Some youtube guy did periodic updates on his sunamp, was definitely excited about the tech and wanted to make it work, but iirc had to call the company back for leaks a few months later, and then again a few months after that. Looks like the function of the PCM in the Latento is to increase capacity and also buffer against vaporizing? Everything I've come across so far has circled back to water or slab being a better option than PCM for primary TES for buildings, but it makes sense to me that it could find a good niche as a supporting actor.
Sooooo… I noticed I have so far failed to sell anyone on my concept of using the ground under the house as thermal storage 🤣. But for anyone who has made it this far in the thread, I am trying to come up with why it wouldn't work. Now, I understand why it would almost always be a bad idea. In general it's a terrible idea, because it would be — by far — inferior to a water tank when it comes to volumetric heat capacity, heat exchange rates, and insulation. My hope is that my (rather specific) set of conditions may be enough to tip the scales at least as far as "maybe a chance in hell."
I mean specifically in the context of these particulars: Moderate climate with dry summers, will be installing the hydronic-solar combisystem including radiant cooling that I have described at length, and that system at every turn is designed around the aim of reducing required water temperature differentials. As I understand it, best predictor for undisturbed ground temps at 20' deep or so is average annual temp, which is 62 here. And the average temp below a building will be warmer than that; somewhere between the average surface temperature of the slab and 62. The footprint of the house including crawl space is about 2000 square feet, and so I suspect I have a good 40,000 cubic feet of dirt before I get down to 62f temps, on a temperature gradient that's probably around 70 at the dead center of the slab and (I know I'm oversimplifying here) then ranges towards 62 as you go downward and outward. My guess is that during the summer I have an almost limitless supply of the 66f floor temperatures to draw down from, just sitting there right at my feet. The limiting factor is how quickly heat from the interior/surface of the slab can migrate into those depths, which is why I think it will be necessary to renew it nightly with 10 hours of night cooling from the solar array. I think in the long term all that ground would be almost self-renewing on its own, but in the short term the surface of the ground needs nightly recharging.
The winter situation is less favorable because the base temperature scenario of all that ground is lower than we need it to be. But not by all that much. By the time cooling season ends, we will have already begun to lift the average water temperatures we're cooling the slab and crawl space to each night. As fall progresses, we will be running as much heat into each as thermal comfort in the interior allows. I'm making a starting guess that by the time peak winter arrives we can have a lot of cubic feet of dirt down there warmed up to perhaps somewhere in the 70-80 range? There's going to be a lot of downward and outward heat loss still to be sure, but remember the TES is built around the concept of heating a huge volume of slab and dirt near the surface only up to something like 85 degrees and being able to survive the night on that. Using volumetric heat capacity of dirt being equal to the slab, and both being 1/2 the capacity of water as a first approximation. Then, the first foot of depth (ie, something like 6" deep of slab and then 6" deep of ground), that top layer has a heat capacity equal to:
2000sqft x 1' depth x 7.48 gallons per cubic foot x 0.5 = 7480 gallons of water
which can hold:
8.33 x 7480 = 62,308 BTUs per degree Fahrenheit
which should be enough to carry us through a peak winter night even if the array only heated that top 1' of surface up to 85f. Yes, a significant amount of heat will bleed away any way you look at it, but we are looking at heat loss into a giant cube of earth that has been conditioned all fall so that it might range downwards with a temp gradient of something like 80 to 70 over the first 10 feet. At this point though I'm only making up numbers, need CFD modeling to answer these questions.
But maybe they're at least questions worth asking? When the temp we need to increase the ground to is so low, I think the heat loss may prove an acceptable tradeoff. The massive volume of the earth underneath the house — and the fact that it's free and already there — may outweigh the fact that it's a far worse choice than a water tank on a per cubic foot basis. If — and only if — the temp we need to heat it to is fairly low. No way this works at all back east, or other climates where the starting point of the earth temperatures are far less favorable.
0 -
You have my permission to try this. If that is what you're asking :)
For the ST component, for dumping heat the glazing and low E coatings will work against you. A simple EPDM or poly pool collector would maximize that exchange. So a good plate collector for loading, simple unglazed for dumping.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
"My guess is that during the summer I have an almost limitless supply of the 66f floor temperatures to draw down from, just sitting there right at my feet. The limiting factor is how quickly heat from the interior/surface of the slab can migrate into those depths, which is why I think it will be necessary to renew it nightly with 10 hours of night cooling from the solar array. I think in the long term all that ground would be almost self-renewing on its own, but in the short term the surface of the ground needs nightly recharging."
If you look at ground source heat pumps, this assumption is often where they fall apart. Often by the end of the summer the soil around the loops is warmer than the outside air, and in winter it's even worse because the soil freezes and frozen soil is a better insulator and all of a sudden the fluid is coming back very cold. Now, I get that you're trying to return as much heat as you extract, but if those aren't balanced the soil can change temperature and then the COP is no better than an air-source heat pump.
0 -
@hot_rod : "Talk about a concept that doesn't pencil out for a small residential application :)"
You'd need about 1,000 pounds of calcium chloride, it's about $150/ton. An IBC would work for the container, they're available used on Craigslist for about $125.
0 -
You have my permission to try this. If that is what you're asking :)
Well maybe not exactly. Although if you were to forbid me, I don't think even Apollo could make this thing pan out
0 -
Now, I get that you're trying to return as much heat as you extract, but if those aren't balanced the soil can change temperature and then the COP is no better than an air-source heat pump.
Yeah, you're right. Self-renewing is too strong of a way to put it. Partially self-renewing over the medium term. Insufficiently self-renewing over the short term. Not self-renewing over the long term, without balancing.
I'm going to have to review the GBA discussion more. Reading through your responses on the page of that article, I thought you had concluded that it didn't really pencil out. Although those are from a couple years ago. So, do you currently think calcium chloride should be on the shortlist for residential TES?
0 -
It didn't pencil out for seasonal storage — where you store a bunch of heat in the summer and release it in the winter. I don't think anything does.
You seem to live in that very rare place where every day can be balanced, and every day is shoulder season. The key to any sort of storage is the more you can use it, the more sense it makes. So if you have an energy store that you can use every day it's going to make a lot more sense. Note I say "more sense," it may or may not make sense overall.
There are two main advantages of a phase change material for storing heat: first, it maintains a constant temperature. What you're always fighting with constant-phase storage is that you have to have a temperature delta to get heat to flow, so you have to put it in hot and take it out cool, and heat at a lower temperature is less useful. Second, the calcium chloride solution has a heat of fusion about the same as ice, 144 BTU/lb. This allows you to store a lot more heat in a much smaller space. Calcium chloride is good for this because you can change the melting point just by changing the proportion of water.
The SunAmp is a commercial product that works on this principle. I don't know what they use for their storage medium. It always seemed to me like a solution in search of a problem though.
1 -
The issue with using the dirt under the house for storage is that it doesn't actually hold all that much energy (sand is 0.2btu/lb/degF, water is 1) and you will be loosing energy to the soil bellow all the time. You could build an insulated box around all the dirt and figure out how to heat it somewhat evenly. With the amount of dirt you will need to heat, you will have to do some serious digging under the house to build it.
You also have to be careful with peak shifting. I'm on TOU rates but once you take in the delivery costs, off peak is still better but not as cheap as it seems.
If you look at the cost delta, you have to make sure that whatever you are doing the peak shifting with doesn't create an efficiency drop that could wipe out your cost savings. For example and heat pump COP depends on SWT. As you store heat at night, the COP will drop as the store temp increases, so the effective COP will be lower than having that same heat pump supply the low supply temp you need during the day.
My solution to TOU was a set back the thermostat. In the morning the house is boosted by a bit before peak starts and coasts through the morning peak. Usually the sun kicks in by then anyways and the heat doesn't need to run. This saves me about $20/month but it was free, so pretty good ROI.
1 -
ah that makes sense. Yeah even Martin Holladay said something like storage doesn't pan out unless you're only looking to store for 4 days. When I saw that I thought 4 days would be great for my purposes! Although I am hopeful this concept lends itself to extending that a little further… just long enough to get a running start in the fall. Even if 80% of the heat we pack in during the late fall goes to waste, that would still be a win if all the heat were generated using the array's spare shoulder season capacity.
Calcium chloride is good for this because you can change the melting point just by changing the proportion of water.
and I see without water the melting point is 84. I'm using ASHRAE's barefoot floor temp limits of 66-84 as a constraint, so it sounds like it could be formulated to hit the sweet spot for both summer and winter. Mouthwatering!
0 -
"I'm using ASHRAE's barefoot floor temp limits of 66-84 as a constraint, so it sounds like it could be formulated to hit the sweet spot for both summer and winter."
I think two tanks would work better than trying to have one tank at a sweet spot — one with a melting point around 55F, one around 120F. I picked 55F because that's about where I think the nighttime radiative coolers will come in, at night in the summer you want to be able to pull heat out of the hot tank, send it to the roof and then send it to the cool tank, and freeze them both. I picked 120F for the hot tank because that's an achievable temperature for the solar collectors, and it's also the temperature you want year-round for your domestic hot water. In the winter you'd be pulling heat out of the cold tank, sending it up to the solar collectors and then to the warm tank, thawing them both.
It might be possible to heat the house just with the 120F water and cool it just with the 55F water, but that would require a lot of doing and only use half of the capacity of the tanks. If you had a water-source heat pump, it could pump between hot and cold and produce much hotter and much colder water. That would allow you to have smaller emitters inside the house which would make everything easier.
1 -
Roger that on the shifting. Need to take into account both rates and relevant supply temperatures.
On the dirt, volumetric heat capacity is the better metric here, yeah? I've been going by volume. Will depend on specific soil composition but I think by volume it's closer, at least for something like an "average" soil composition. For prototyping I'm using water has double the VHC of dirt, and dirt has double the thermal conductivity of water. And slab concrete works out to about the same VHC and thermal conductivity as dirt. Obviously these are simplifications but at this point I'm only looking to land in the neighborhood.
No digging would be involved, except — possibly — for some perimeter insulation around the exterior of the slab, going down maybe a couple of feet. My understanding is that retrofitting insulation under the slab of an existing building is feasible from an engineering standpoint, but disruptive and expensive and the numbers basically never pencil out. No digging for the piping either; the radiant flooring would act as a heat plate on the surface of the ground, but the pipes wouldn't go downwards into the ground like geothermal. This is significant because the arrangement will concentrate heat at the surface and the isotherms will presumably show a declining temperature gradient the lower down you go. Whereas an analogous geothermal arrangement would disperse the heat more evenly throughout an imagined "cube" of dirt under the house, with 5 sides of the cube exposed to something like 62f base subsurface temperatures. Pretending those sides are like walls around a tank for the thought experiment, even though it's all just dirt, because the ground underneath conditioned space is a different animal than the ground adjacent to it. Anyway, with the "heat plate on the surface of the ground" configuration, there is much less surface area where high temperature soil under the building is exposed to the low temperature boundary at the sides of the cube. The lower you go, the lower the temp and the less heat you're bleeding. dirt stratification i guess
Anyway, I get an R-Value for dirt of about 1.5 per foot. With a 50'x40' footprint, in some sense it is already well insulated, especially toward the middle. Different parts of that cube of dirt would variously function as storage medium, transfer medium, and insulation medium. Compared to alternative materials, dirt doesn't do a good job at any of those functions, or I would say even a fair job. But I suspect the perimeter heat losses near the top may prove acceptable given the sheer volume of thermal storage we're talking about, AND given the fact that the dirt thermal store in this arrangement becomes useful even at VERY low temperatures. Like, even if we're only lifting the surface temp of the ground to 70 degrees and relying on a W2W Heat Pump from there, we're still talking about significant improvements compared to an A2A heat pump drawing from outdoor air ranging from 35-55. The more the ground warms up, the more heat our cube will bleed, but keep in mind the concept here is Big Dirt, Small Temp Lifts. It would be a different animal than typical TES arrangements like water tanks designed to get up close to 200. The hottest part of the DIRT-TES, the surface, may never even top 90 degrees. Because if the top foot of dirt is at 90, the next foot is at 88, then 86, etc all the way down to 62… That's a lot of BTUs packed in there. With temp differences between the store and the surroundings an order of magnitude lower than conventional arrangements, it should be able to get away with an order of magnitude worse overall… U-Factor? Can't remember if that's the right term here.
And with a few feet deep of perimeter insulation to bolster this arrangement available as a doable retrofit if that's what's needed… man the more I talk it out the more it just seems like there's got to be something there. We'll see but as best as I can put it all together so far it seems like the question is not whether there's something there, but rather how well it would stack up in terms of performance and cost compared to alternatives.
0 -
ah yeah never mind, with PCM storage configuration your 120 & 55 would be much better. I guess even with my dirt fantasy there's no reason to stop at 84 & 66 specifically. But there would be a need to tighten the two numbers as much as possible, because the tighter we can live with the less heat it would bleed.
0 -
The 65F soil will always be sucking heat out of the heated slab, the soil as insulation doesn't work. This has been tried before with heated floors in cold climate and the only thing you end up with is big energy costs. The slab will also be heating the basement, so it doesn't work well as a buffer. 90deg slab will be putting 40btu/sqft into a 70f the basement, that is enough heat to heat the whole house.
In your mild climate an oversized air to air running on low modulation would get a COP of between 4 to 5, not sure how much better you want.
https://ashp.neep.org/#!/product/33992/7/25000/95/7500/0///0
0 -
"In your mild climate an oversized air to air running on low modulation would get a COP of between 4 to 5, not sure how much better you want."
Now @Kaos, @BTUser has been emphatic that practicality cannot be a consideration!
But you raise a fair point. I've been bruiting about a 300,000 BTU storage capacity. That's equal to 88 kWh, at a COP of 4.0 it would take 22kWh of electricity to provide the same amount of heat. At $0.25 per kWh that's $5.50 worth of electricity. That's daily storage, but you're not going to be doing that every day, most days will be less, let's say you do the equivalent of 100 fills a year, so you use $550 worth of electricity. That's the most you could save. Even if you doubled the COP you'd only be saving $275 per year. What I'm proposing is most similar to a ground source heat pump, and they have trouble breaking 6.0 COP so doubling is probably unrealistic.
The annual electricity usage would be 2200 kWh. Where I am, a 2200 W PV array would provide that, and would have a net installed cost of about $4400.
I can't find online pricing for the Fujitsu you linked to, but similar units from Mitsubishi are about $6k for the pieces. So for less than $11K you could install a system with a heat pump and the PV to power it. I know that's not what BTUser wants to do, but that puts an outer limit on practicality. Alternately you can skip the PV and set your limit at $6K for equipment and $550/year of electricity costs. Or pick a point in between.
0 -
Right well I can't see how it could work in a cold climate. Slab heating under interior room would be limited to what thermal comfort will allow. The basement/crawl space could be allowed to get a little warmer, and/or insulation could be applied on top of the slab in that area to reduce heat flow.
I will use the heat pump you linked to and build on the cost analysis that DC did below to build and come up with a TCO for going this route. That will become my target cost to beat.
@BTUser has been emphatic that practicality cannot be a consideration!
😁😂🤣 This entire thread in a nutshell right there.
My objective is to bring our natural gas consumption to zero and our electricity consumption down by an order of magnitude, to the point that we can get a second electric car and still have our 6.48 kwh PV system wipe out all electricty spending including home car charging. Currently despite the PV system we've average $3250 per year energy spending over the last 2 years, excluding nonbypassable charges. A second electric car charging only off-peak would add about $3000 to that. So I'm looking at about $6K per year on the table to wipe out. Will build out the numbercrunch for the PV+A2AHP+envelope improvements route once I get proper load calcs and post here. That should be relatively straightforward and I'm guessing piece of cake for you guys to glance at and see if it's reasonable.
Modeling for the approach I've described will be much tougher, more debatable, larger error margin. The conventional approach will be a useful firmer reference point to compare against.
0 -
It would help to know how the current $3250 breaks down between gas and electric, and what your gas and electric rates are.
0 -
Here’s all the numbers I could think of to gather so far. I was off on my estimates for the second car. Looks like we’d be at $4000/year to PG&E if we were to swap out my wife’s car for a second electric, but otherwise make no changes. New car may not happen until a bit further down the road, she’ll want to keep what she’s got until it dies.
0 -
-
I would do the couple of tutorials required to run your place though this:
With a reasonbly accurate model, it is a great tool for answering what if questions like how much would more insulation save or a heating system with higher COP.
For most existing homes, at least in colder climate, usually the best ROI is better air sealing.
4 -
At $2.78 per therm, with an average COP of 4.0 your break-even price of electricity is $0.38/kWh. From the data I can't tell what your actual average price of electricity is, but for simplicity let's assume it's around there. So I get that you use 4562 kWh per year. On top of that is 526 therm of gas, which is equivalent to 3854 kWh at COP 4.0. So 8416 kWh of additional electricity production would serve your needs. I get about 1000 hours of direct sunlight equivalent, you probably get more, but let's say that's what you get, so 8416 W of nominal capacity. You'd have to check local pricing, around me solar panels cost about $3.40 per installed Watt but there's a federal tax credit of 35% that gets the cost down to $2.21 or about $18,600 for the array you'd need.
Figure about 200 W per square meter, so 42 square meters or about 420 square feet. This would be in addition to the 6480 you already have installed.
At an average cost of $.38/kWh and $2.21 per installed watt, the payback period would be 5.8 years.
These are all rough numbers but they help put a fence around what is practical.
0 -
Note that the more expensive your electricity is, the more sense solar makes.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 135 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 52 Job Opportunities
- 18 Recall Announcements