New boiler on gravity system

Hello my old boiler from the 30s I think finally died. I now have a crown boiler with a circulator pump and aqua stat with high and low settings. The way everything is set up now is overheating my house. The low setting on the aqua stat is set at 125 so every time the water reaches that temperature the boiler fires for about 5 minutes. The circulating pump is always on. My thermostat is set at 60 right now and the house temperature by the end of the day reaches 70-72. I have to turn off the boiler switch every night so we are not roasting in bed. I have cast iron radiators that hold heat very well. I have 2 questions 1 should the pump always be on or is it only supposed to be on when the thermostat calls for heat. The other is should I just turn off the low setting on the aquastat so the water is only heating when the thermostat calls for heat. The aqua stat is a hydrostat 3250 plus. Thanks for any info
Comments
-
Where does your hot water for kitchen sink and bathroom come from? It sounds like you have a domestic hot water coil installed in the boiler, which would explain the 125 minimum aquastat setting.
But your circulator shouldn't be running all the time. It should only be running when the thermostat calls for heat.
0 -
separate hot water heater
0 -
-
Are you sure the "separate" water heater has its own heat source (like gas or electric) and isn't an "indirect" tank that gets heated water from the boiler?
0 -
Whatever the hot water source — the thermostat should turn the circulator on and off. It shouldn't be on all the time. And the aquastat will turn the boiler on and off as needed.
Something isn't wired up properly.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
ok the plumber temporarily wired it so I would have heat. Electrician should be coming tomorrow to install a new wire from the shut off switch and I will have him check all wiring
0 -
Yes it’s a gas hot water heater. My boiler is oil fired
0 -
-
-
Did you call the person that installed it? They might have missed a few things while they were trying to get the heat back on like setting it as cold start. Note that on a converted gravity system, unless it has a flow check at the boiler, if it is set up warm start it is very likely to heat the system through gravity flow even if the circulator isn't running. Set the low setting to not fire the boiler.
1 -
0
-
yes it does have this feature thanks
0 -
I will call him tomorrow morning thanks. I was thinking the same thing. Between the pump going and the boiler firing so often I’m burning a ton of fuel
0 -
That not the way I would have gone about piping that system.
Typically you try to mimic the flow rate. That looks like a 0010 on the piping.
Im not even sure there is any boiler protection there.
0 -
i think i see a bypass in the back left. nice to have balancing valves between the mains, can't see if those are there or not. piping is probably bigger than it needs to be.
0 -
I don’t see any air purger? Also have him support the expansion tank a bit more.
When it fires from a cold start, time how long it takes to get the return to the boiler to 130F. You want that to happen within 10 minutes, ideally
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
yes he put valves on the returns and risers
0 -
where would the purger be located? It doesn’t fire from a cold start the low setting on aqua stat is 130.
0 -
an air purger would be best right at the boiler on the supply piping. For best heat transfer in the boiler, and in the radiators you want a completely air free system, micro bubbles and big bubbles.
Most often the boiler fires only when a thermostat call for heat. It would drop to room temperature if it is off for periods of time.
If it is running all the time, maintaining 130f, you may be wasting some fuel dollars up the flue.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
what would be ideal to prevent condensing?
0 -
are either of these air purgers?
0 -
the brass on the left is your backflow prevention and reduced pressure fill valve,
the brass on the right is an auto air vent, let us see how it's piped to that riser, where it should be piped on the top where that cap is, the boiler itself has a baffle under there and sends air up that riser,
let's see a wider view floor to ceiling showing circs, another air sep might be hiding
known to beat dead horses0 -
You don't need anything else. You already have a bypass plumbed in, which is a pipe path that takes hot water from the supply pipe exiting the boiler and returns it to the boiler. The bypass is the copper pipe that tees out to the left just above the top of the boiler. That increases the water temperature returning to the boiler, to help prevent condensation and also to prevent thermal shock to the cast iron heat exchanger.
Apparently your plumber set the boiler up initially with the aquastat having a low limit temperature because as you said, he was just trying to give you temporary heat until the elctrician could come and redo all the wiring correctly. It wasn't for condensation protection. The bypass does that.
1 -
-
Thank you for this explanation learning a lot about heating on this website very helpful
0 -
Overheat? No flow valve with Low limit on. I do not see any bypass piping. Is that a #30 Extrol on a gravity pipe system?
0 -
I do not see any bypass/boiler protection valve in this system
No air separator, which I guess just means that he would be bleeding the air at the highest points at the radiators.
Also looks like there's at least 2 sets of thermostat wires in the top left of the pictures (old striped cloth wrapped wire) but you only one set of thermostat wires into the control box. Its hard to see how they are all spliced together.
The 120v circuits all hanging in free air doesn't look too safe either.
0 -
-
@jakamini I stand corrected, there is no bypass plumbed in as I erroneously said. One of your photos has two pipes lined up one behind the other, and my eyes fooled me. The horizontal branch of the copper pipe coming vertically out of the top of the boiler is going to another supply main, not the return pipe behind it.
The boiler installation instructions probably do call for a bypass. However, I have two Weil-McLain WGO-5 cast iron boilers that also were plumbed with no bypass, and they have run for 30+ years with no sign of condensation, even with low return water temps, most of the time sub-130 degrees.
So if I were you, I wouldn't sweat it too much. On a call for heat, your boiler should run from a cold start at least 30 minutes at a time, during which time the flue gas will get plenty hot to burn off any initial condensation from startup, regardless of low return water temperatures.
0 -
why didn’t you just put pumps of the circuits?
0 -
The installation instructions show a bypass and explain why it is needed. However..
That boiler could run hours in condensing mode if the distribution piping and the cast radiators are more emitter than the boiler can keep up with. Thermal equilibrium is at that low RWT.
For example the return water may be 68° when a call for heat A properly sized boiler could maybe "lift" that temperature 5° or so. That indicates the boiler block is running around 70.
Assume 10 gpm is being circulated. There is no way a bypass, even full open can raise to boiler to 130° if the boiler can only make 70° water.
That is why the bypass needs to have a thermostatic function. Could be the aquastat as @kcopp mentioned, or a thermostatic valve.
Two ways to confirm this. Calculate the radiators output, EDR. Or watch the boiler when it fires up, time the cycle, measure the return.
Just because @jesmed1 boilers lasted, doesn't guarantee yours will😉
Observe it and see for yourself
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
0
-
This happens a lot. For some reason they just ignored some of the things that the manual specifically indicated should be installed. Maybe it was a heat emergency job for you and they didn't have everything but they had enough to get you up and running. Discuss the findings of this thread and tell them the things they are missing and should be installed and see what they say, if they tell you its a bunch of BS hen you should find someone else. If they tell you they are aware and that they can/will come back to make the final adjustments/corrections then they are an OK shop.
2 -
Unfortunately it seems common for installers to ignore the typical bypass requirement for cast iron boilers. I suspect they count on the ignorance of the homeowner (myself included, since I didn't know what a bypass was until I came here). They know the boiler will work whether or not they install a bypass, and if the boiler doesn't last as long as it should due to condensing, they'll be long gone, and the homeowner is none the wiser.
As I've mentioned, our two cast iron boilers were installed in the 1990's without bypasses, and fortunately it seems they haven't suffered from the omission, but now that I know, I will make sure our next boilers do get bypasses.
2 -
@hot_rod didn't say it but I will.
Have a Caleffi 280 mixing valve installed with a 115F element. It is the simplest way to protect a cast iron boiler installed in a converted gravity situation.
Are there other techniques? Yes. But have you heard of Occam's razor?
Occam's razor is a problem-solving principle that suggests the simplest explanation is usually the best.—Eric
0 -
@EricPeterson why 115F ? Don't the boiler mfr's typically say return temp must be above 130F ?
I'm not saying 130F is right, because as I've said before, our boilers run 90% of the time below 130F return. I'm just trying to understand the logic of 115F.
We can also use those Caleffi 280's when we replace our old boilers. Am just curious about the correct temp.
0 -
@jesmed1 - you are correct, I should have said use the appropriate element.
In my case 115F was the best option since my boiler is rated for 110F return temperatures. But yes for others a different value should be used (130, 140, 160).
I also went with 115F so that water starts flowing to the system sooner, and to play nice with the ODR that I installed.
—Eric
2
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 101 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements