How to calculate EDR for dummies

RTW
RTW Member Posts: 192

A lot has been posted on knowing EDR to match boiler size and thought this Link would give residential homeowners a better understanding on how to measure EDR on their own

radiatorest.pdf

I read in a post the other day the EDR # should correspond to the Steam Sq. # on the boiler label plate

Im an amateur with steam heat, so don't hold me to this info. and follow professional advice

All the best,

RTW

Ironman

Comments

  • delcrossv
    delcrossv Member Posts: 1,918
    edited February 13

    The book Every Darn Radiator is more accurate. But this will "ballpark" you.

    Not sure about the x1.25 to get boiler size as SqFt of steam on the boiler plate already includes a 33% pickup factor. Adding another 25% would get you well oversized.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Dave in QCA
    Dave in QCA Member Posts: 1,801

    One of the problems with the guide at

    radiatorest.pdf

    is that it only mentions one type of tubular radiator. In fact their are two and they are greatly different. The first version of tubular radiators had thicker section, mearsuring 2.5" on center, the same as most column radiators. Then, the slenderized version came on to the market with a section dimension of 1.75" thick.

    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
    bburd
  • Dave in QCA
    Dave in QCA Member Posts: 1,801

    Another good EDR guide comes from an old ASHRAE guide book. I have been using this guide since 1982. More exact EDR ratings from the manufacturers is even more accurate and Dan has a ton of those in his publication, EDR - Every Darned Radiator.

    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
    random12345
  • Pumpguy
    Pumpguy Member Posts: 726

    The EDR is equally needed when sizing vacuum and condensate pumps for 2 pipe systems.

    Whenever I'm asked about replacement pumps or system problems, and ask what is the system's EDR, no-one yet, ever, has given me this information based on an actual survey of the radiation.

    So that leaves me with having to rely on the steaming capacity of the boiler plant, or the pumping capacity of the old equipment.

    And then they wonder why the new equipment doesn't work any better than the old stuff did. Doing the same thing and expecting a different result is………………

    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
    delcrossvDave in QCA
  • RTW
    RTW Member Posts: 192

    Could use a YOUTUBE video showing how one measures a radiator to get an accurate number to establish EDR in steam heating system

    All the best,

    RTW

    jringel
  • dabrakeman
    dabrakeman Member Posts: 723

    For a simple sheet I liked this one. Includes the thin tube variety.

    random12345
  • Jells
    Jells Member Posts: 618

    Thanks, I was sure I'd seen one with 'depths' dimensions but could not turn it up!

    Stupid question: do all the mains and risers not go into the EDR calc in any way? There's a lot of surface area there!

  • delcrossv
    delcrossv Member Posts: 1,918

    That's the 33% pickup factor included in the boiler rating.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    bburd
  • Jells
    Jells Member Posts: 618

    Ah, I kept seeing that phrase used but had no idea what it actually meant!

    delcrossv