High system pressure cause mixing valve failure?
I've had 3 mixing valve failures in less than 2 years which come off my tankless coil from my boiler.
The coil is only 2 years old and I am on city water, but the pressure is over 100 psi. I'm looking into a pressure reducing valve to install since my house probably could only improve by having one.
I hope to take off the current mixing valve and do an analysis as to what is wrong, previously I had o rings ripped that I replaced and it fixed the problem, then I had a failure again in a few months so I stuck on a spare mixing valve I had (AM-1 I believe) and that lasted me several months but now is doing the same things as before (hot water at spigot drops as boiler temp drops), like the valve is just doing a direct proportional mix. (pressure is fine)
Do the internals have temperature component limitations that are concerning for temps getting up to 190-195? Sometimes my boiler can coast that high.
My suspicion is that the high pressure is causing undo issues for the mixing valve? It doesn't seem that a partially blocked coil is likely since it's age and being on city water, however I am getting the water quality checked and plan on installing some kind of filter to protect myself against such nonsense, what would I look for in my water that would cause scaling in my coil?
Please advise! I'm open to learning!
If I find my coil is blocked I think I'll be looking into an indirect for the future, anyone care to post some research links?
    pecmsg Member Posts: 7,024
    100 PSI is extreme. Install a reducing valve.
    GGross
    Jamie Hall Member Posts: 27,237
    Actually it is possible that the very high pressure could cause problems with the mixing valves — though I think it is unlikely. It is also quite possible that the mixing valve is operating outside it's comfort zone — if your hot water input is getting up as high as you say, and you are mixing down to 120 or so (I presume this is for domestic hot water), the hot side will be almost closed, and that can lead to problems.
    The only thing that will cause scaling in the coil is excessive hardness, but the water have to be really hard to do much in only two years. A filter won't help that.
    Do get a pressure reducing valve installed. However, also be aware that with a pressure reducing valve you will also need a small expansion tank on the domestic hot water. I you are using the coil, it needn't be large — but it is needed.
    Ironman
    hot_rod Member Posts: 27,329
    how high is your pressure, do you have a PRV?
    A thermal expansion tank?
    Most valves are rated to 195F, 150 static pressure , 75 psi dynamic operating pressure.
    High pressure, hard water, high operating temperature, excessive chlorine or chloramines, add stress to the valves.
    Unequal pressure between hot and cold will cause them to shut down. That can happen if the coil is badly scaled, the hot pressure drops, as you start flowing.
    Most valves have a 2:1 pressure ratio, if you have 60 psi incoming and the hot drops to 30, that will be an issue
    So check incoming pressure over a week with a lazy hand gauge. 60 psi is plenty, 80 is too high
    Thermostatic valves can be high maintenance in hard, high temperature water. You may need to clean or descale every 6 months
  • RascalOrnery
    RascalOrnery Member Posts: 137
    Thanks for the quick response guys! I do have a small expansion tank that I put in on the cold side for the domestic hot water to help relieve water hammer. With a system PRV is that sufficient or should it be after the mixing valve on the side where the hot water goes to the fixtures?
    I borrowed a gauge from a friend and I can't remember if the system pressure was 120 or 130 or something…but it was high. FYI while this may seem crazy, the area I live in a think is rife with this sort of thing, two other friends who bought houses did not have low water cutoffs on their boilers or PRV's in there homes. The house I grew up in did not even have a mixing/tempering valve, it was just "don't get burnt" and several people I know who have a boiler didn't know what I was talking about when I said about a mixing valve. :D so I am ahead of it! This house is 100 years old and probably has had water for most of that time, and there is pretty much just straight piping with barely any shut off valves, so me just getting to it as the recent owner…is rather embarrasing!
    Is it likely for my city water to be hard? I though hard/soft and such was usually a well water discussion?
    What items fail on these type of mixing valves in high pressure high temperature situations? Seals mainly or do you think the check valves get slammed around or o-rings get shredded from the stress?
    45-60 psi is plenty for residential systems. Above that all the plumbing valves and fixtures are stressed. Excessive pressure is more prone to water hammer also.
    Mainline pressure above 150 psi should use a two stage PRV. First stage to 100 psi, second to 45-50.
    Water hardness test kits are cheap. The color changing strips are close enough. Few places in the U.S. have soft water.
    Excessive pressure hammers seals, seats, o rings etc. A PRV is not an expensive protection device.
  • Ironman
    Ironman Member Posts: 7,902
    Caleffi’s angle mixing valve is a much better product than the Honeywell. We quit using those some years back because of the high failure rate.
    Bob Boan
  • RascalOrnery
    This is the one I was looking at:
    https://www.supplyhouse.com/Caleffi-535351HA-3-4-NPTF-Pressure-Reducing-Valve-w-Gauge-Low-Lead-Pre-adjustable
    Thanks guys! My brother in law told me our water authority posts the water properties so I should be able to look at that for starters, looks like I'm on the fringe of slightly and moderately hard area
    excellent PRV, easy to service, high flow rate
    Also when next you replace the mixer we still offer a solar version, higher temperature rating rating. It has different polymers inside for extreme temperature use. Although limit the hot temperature as much as you can.
    Intplm.
    EBEBRATT-Ed Member Posts: 20,085
    PRV and expansion tank as others mentioned above.
    the 520 anglemix is a valve designed specifically for tankless water heaters. It responds very quickly
    Notice two important numbers, on the two valves maximum temperature, and the minimum flow required
    If you use a lot of low flow faucets, or shower heads, the 520 is a better valve. But your high temperatures 195 plus are concerning
    The solar valve handles the temperature better, but needs more flow to be stable. With a small sink draw less than 1 gpm, the temperature will vary as the valve “hunts”
  • RascalOrnery
    Thanks you all so much, especially @hot_rod for the helpful links and info!
  • Intplm.
    Intplm. Member Posts: 2,994
    And if you're still concerned about the quality of your water, your water utility will send you a water quality report at your request. Some may even post them on line.
  • RascalOrnery
    Yes, I did find it, thank you!
  • RascalOrnery
    Today I shut the water off, installed the PRV, disassembled the mixing valve and replaced the o ring that appeared to be pretty well shot. It is running fine now, but the second I have problems with it I will be replacing it with the Caleffi. I've gotta say, the Caleffi PRV I got is really nice quality, excellent instructions included and the price was very good as well!
  • RascalOrnery
    I'm reviving this thread to try to get some further help. I finally installed a Caleffi Solar mixing valve on the tankless coil (very nice quality!) but I'm now getting some pretty serious water hammer on the HOT only if I close a spigot at any speed, or when the dishwasher or washing machine cycles. The cold is fine, the cold also has a small expansion tank, but my understanding is that the hot side of the mixing valve should still have access to this expansion tank "dampening" effect, but maybe not due to the way check valves work?
    Should I install a expansion tank or water hammer arrestor on the hot side of the coil now? My psi is about 70 coming into the house - this is before the filter - which was dumb on my part!
    Yes. You need a small expansion tank or water hammer arrestor on the hot side.
    If you installed a pressure reducing valve on the main water, that is acting as a backflow device also. So you do need a thermal expansion tank expansion tank. Actually plumbing codes require a thermal expansion device.
    When you install it like this it will act as a hammer arrester for H&C. Sizing info also.
    Thanks for the Caleffi support!
  • RascalOrnery
    Yah, that makes sense about the PRV acting as backflow prevention, so should I MOVE my expansion tank from the cold side to the hot side, or add an ADDITIONAL arrestor or expansion tank to the hot side?
    if you don’t have a recirculating pump, I would remove the checks. H&C will be the same pressure and the exp tank can see the entire system
    bjohnhy
  • RascalOrnery
    I removed the check valves and no more banging! Thanks!