New boiler - low end rumble
we had a new steam boiler installed, which has a drop header where our previous one did not. The boiler room is beneath our living room and at times there is a low end rumble/vibration/resonance particularly at the beginning of a cycle. The boiler is almost half the size.
the mains coming off the boiler are only supported by brackets about 10’ from the boiler, so no brackets at the boiler. I did notice one of the main has a little jiggle to it when running. Should I add support near the boiler? Should they be just straps or should they be firm mounted to studs using the threaded rod types?
I don’t hear any of the rumble when in the boiler room.
Pictures would help.
Was this boiler skimmed at start up?
What has the installing contractor said about the issue?
As has been said — so nice to see a good install for a change!
If you don't hear the rumble when you are near the boiler in the basement, it's going to be a bit difficult to find the cause. It probably wouldn't hurt, though, to add some extra straps to the mains. I'm not at all sure I'd use a rigid support, though — if the sound is coming from the boiler or the piping, that might make it worse!
Was combustion and gas pressure checked by the installer?
That chimney looks like it’s on an outside wall. Has it been lined?
Bob Boan
Chimney runs outside of the house, correct. No liner, cap on top. Combustion was checked, not sure about gas pressure.
If I am not mistaken in most cases especially in a cold climate all outside chimneys need a liner. Stainless steel is better than aluminum
An unlined outside chimney can cause improper draft. Flue gas condensation will also happen which will rot the mortar joints in the chimney eventually causing it to cave in.
IDK how you can properly check combustion without checking gas pressure.
Bob Boan
well since the only thing you can adjust on this boiler is the gas pressure, if the combustion gases look good, you’re all set, right?
Code mandated in MA?
Yes it is.
99% sure it's original clay on the inside. Does code require stainless for a steam boiler?
Not that I'm aware of but codes change all the time. You can use aluminum but don't expect it to last that long. Outside chimney combined with boiler efficiency's low flue gas temp leads to condensation in the liner which doesn't hold up as well as stainless. I've seen lots of failures with mid efficiency fan assisted category 1 appliances vented in aluminum. I don't think you can go wrong with stainless except a little lighter in the wallet.
By the way, that is how you pipe a steam boiler. I'm not a drop header guy because its overkill but he did a great piping job with everything but the black malleable. if he used cast iron fittings he would have gotten two thumbs up instead of one. lol
Thanks, got 55 years out of the last boiler, figure I could splurge for the drop header and do it once. Will insulate the near piping after inspections are all done.
Don't those burners have air shutters which are also adjustable?
Bburd0
- 117 Geothermal