LG Heat Pump frustration
135
  • LRCCBJ
    LRCCBJ Member Posts: 1,013
    His response:
    "The supply temp coming out will be about 110 yes.
    Your response:
    Then I suggest you fix the system so that we can both measure 110° at the supply registers. I will not accept the system until you do.
  • KarlW
    KarlW Member Posts: 183
    I feel for you - it's time to get another installer as it seems like the diagnosis here regarding too small ductwork does appear to be the case - perhaps you have a 5-year warranty and can go after them? (although good luck with that)
    My recommendation is to hire a company that does commercial and residential - they'll have someone who can do the calculations you need to determine what if any duct improvements can be done. Many residential guys (in theory all) can do this, but some can't and you don't want to roll the dice again.
  • KarlW
    edited December 2024
    @LRCCBJ unfortunately, it appears he had it installed 4 years ago so that argument isn't so simple…
    LRCCBJ
  • jesmed1
    jesmed1 Member Posts: 1,243
    I feel your pain. In the case of our church furnace, it took months of my own data collection to convince the installer that the furnace was overheating because the return plenum he installed was too small, choking the airflow.
    There was no easy fix, because space constraints made it impossible to install a larger return plenum. We ended up locking the furnace in "low fire" mode to permanently reduce the heat output and prevent overheating.
    I agree with @KarlW that you may need to give up on this guy and pay someone else to fix his mistakes, whether it turns out to be insufficient refrigerant or a duct problem or both.
    pecmsg Member Posts: 5,939
    heat pumps are actually fairly simple to troubleshoot. Measure air in air out. Each manufacturer has charts. If not in range pull and weigh the charge. If short there’s issues, if not this is where it gets difficult.
    the tech on site MUST contact tech support. That can be a long frustrating process!
    Jamie Hall Member Posts: 25,916
    If the system was designed for a 67 degree delta T, and you accepted the design (which, since it looks like you may have been dealing with some sort of State mandate, you had to), and it managed that delta T in the space, you got what you paid for.
    Note what I said above about unrealistic expectations.
    If you can find another company and engineer to go over the operation of the equipment, and the design, and find where something isn't right or wasn't designed correctly, you may be able to get somewhere.
  • bburd
    bburd Member Posts: 1,153
    @josephny this comment about your HVAC tech's visit got my attention:
    "We then opened the unit and (shockingly) there is no electric coil installed."
    Heat pump installations in cold climates have always required a backup heat source. Maybe this industry practice has changed now that we have hyperheat units, but these are relatively new to the market; if I had one, I would want backup heat. If nothing else, without it the house will be uncomfortable during defrost cycles.
    It may not be installed at the air handler, but there should be some other way of heating the house when the heat pump isn't working or cannot keep up in extreme weather.
    If your system has no back up, you will probably want to add something. Electric resistance heat strips are the typical default; as others observed you already have a propane boiler for domestic hot water that can probably supply a couple of hot water coils in the ductwork.
    Also as others have said, the heat pump performance should be checked against the factory specs. Your delta T between supply air and return seems awfully low. You might need to get a manufacturer's representative involved, or pay someone qualified to assess the system.
    Bburd
  • Kaos
    Kaos Member Posts: 587
    Folks, lets not confuse the issue here.
    The OP does not have a design or ducting issue. He has a simple equipment not putting out hot enough air. This is easy to deal with except you need to work with the installer.
    @bburd There is nowhere in code that requires a heat pump to have backup heat. This is one of those myths that is very hard to squash. The equipment needs to be sized to supply 99% design temp, as long as it does that, you don't need anything else.
    Some insurance companies do require backup heat in areas with intermittent electric supply. The backup is required no matter your heat source, a boiler would need one the same as a furnace or a heat pump. In that case, it can't be powered anyways, so both heat strip and hydro coil are out.
    LRCCBJDCContrarianHot_water_fan
  • GW
    GW Member Posts: 4,943
    ok yes probably better if you don't tell the hvac guy you "set it to 82 and it never got there". 99% of the hvac people will give you a polite yet head-tilting look "of course it won't get to 82".
    Did he check the superheat and sub-cooling? (did he hook up gauges)? I wouldn't blame the dude if he didn't, because it was 70, after all
    If your home is staying at 70 when it's that cold, you're doing pretty good.
    I re read your initial post, what temps are you hoping for?
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    ethicalpaulDan Foley
    A good example of why Back up heat is need!
    SuperTechDan Foley
  • lkstdl
    lkstdl Member Posts: 47
    I think I agree with Kaos here.
    If it was the problem was undersized ducts, wouldn't we see supply air temperatures that were too high rather than too low?
    Unless the units were automatically modulating down due to insufficient airflow — but based on the reported 11 kW power usage, they are running fairly close to their rated capacity. @josephny, can you get modulation data with the API?
    A competent tech should be able to determine if the refrigerant charge is correct. (NYSERDA may be able to recommend one, and may even be willing to send one out on their dime.)
    It is also possible that the system is working as designed, and the house just isn't comfortable for you at 73 degrees when its 5 or 10 degrees outside.
    Our thermal comfort isn't determined by air temperature alone — it is also affected by the humidity, air movement (air leakage, or intentional air movement from fans), and the "mean radiant temperature" (think about walking in front of a large window).
    If this is the case, you can work to reduce the leakage, turn off extra fans, increase humidity, or raise the mean radiant temperature.
    If your whole basement is as accessible as what's shown in the photograph, a radiant floor might not be too difficult to retrofit. You could run it off your existing IBC boiler.
    Luke Stodola
    LRCCBJDCContrarian
  • neilc
    neilc Member Posts: 3,020
    @josephny
    did you say above that the units are determining room temp at the units, and not at the wall controllers?
    Can that be changed to read at the wall ?
    known to beat dead horses
  • DCContrarian
    DCContrarian Member Posts: 1,115
    "BTW, keeping the tstat well above the temp setting that the system can provide uses about 11kw/h (which costs me about $2.20/hr or $53/day). This is maddening."
    11 kW is 37,000 BTU/hr. At 5F the unit has a rated capacity of 40,000 BTU/hr and at -4 it's 35,970 BTU/hr. So it looks like we're seeing COP of under 1.0.
    Looking at the NEEP page (I think the right one is:) https://ashp.neep.org/#!/product/33645/7/25000/95/7500/0///0
    At 5F and max output it should have a COP of 1.8.
    The unit is not performing properly.
    GGross
  • DCContrarian
    "If the system was designed for a 67 degree delta T, and you accepted the design (which, since it looks like you may have been dealing with some sort of State mandate, you had to), and it managed that delta T in the space, you got what you paid for."
    I took the tech's comment to mean that the design temp was 3F and the equipment was sized according to Manual J.
  • DCContrarian
    It depends on the noise! If it's air whistling and rushing in the ducts, sure. If it's the compressor outside rattling and moaning that has nothing to do with the ductwork.
  • DCContrarian
    "I've been fighting with this failed, $50k heat pump for going on 4 years now."
    So has it been like this for the entire four years? Or did it suddenly (or gradually) get worse?
  • DCContrarian
    On second thought, 11kW would mean a draw of 46 Amps. According to the spec sheet the maximum overcurrent protection is 40A so if that were happening it should be blowing the circuit breaker. On the other hand, if it were really drawing only 6kW or so it would be achieving the rated COP of 1.8 and the only thing that wouldn't be working as expected would be that the thermostat is way off. That would be about 25A draw.
    Where is the 11kW number coming from?
  • jesmed1
    The OP has three different heat pumps, so his 11kW number may be for all three systems combined.
    11 kW would be 37,400 BTU/hr, and assuming a combined COP of around 2, that would be a combined heat output of 74,800 BTU/hr, which is quite close to the OP's combined capacity of 78,000 BTU/hr.
    So if the 11 kW number is for all three heat pumps combined, then the numbers make sense.
    And if it makes the OP feel any better, if he were burning heating oil at $3.50/gallon, those 78,000 BTU/hr would be costing him about $2.70/hr (assuming a cast iron boiler at 75% overall efficiency).
    Yes, $2.20/hr heating costs hurt, but we're in the part of winter where heat pumps are least efficient, so the seasonal average isn't going to be as painful.
    But 11 kW total for all three systems appears to be reasonable at current temperatures.
    DCContrarianlkstdl
  • ratio
    ratio Member Posts: 3,958
    The heat strip for the air handler is likely to be field-installable, so you should be able to get one installed.
    GGrossSuperTech
  • DCContrarian
    OK, I missed that this was one of three. I agree with everything you wrote.
    OP said his house is 1500 SF on each of three floors, so that heat loss number doesn't square with his statement that the house is "super well insulated."
    jesmed1
  • jesmed1
    Yes, so 78,000 BTU/hr, which is apparently what the contractor calculated in his manual J, and for 4500 sq ft that's 17 BTU/hr/sq ft, which isn't much better than my 100-year-old rather leaky house in the Boston area with a heat loss of 20 BTU/hr/sq ft at a design temp of zero degrees.
  • LRCCBJ
    In truth, that is an exceptionally low value for a building of that type. 20 BTU/hr/sq ft. is "typical"………..most old houses are higher due to the infiltration.
    If he is at 17………..at 0° F………..I'd consider that quite good.
    You must be careful of the 'stat settings. Most don't hold a DT of 70 throughout a 24 hour period for the entire house. This can easily skew the result and the claimed 20 BTU/hr/sq ft would not be valid. It's difficult to get data at 0°F for 24 hours. Without it, you really cannot confirm the result.
  • DCContrarian
    Let's say this is a code-minimum house built to the current code — R38 in the roof, R21 in the walls, R10 under the basement and R5 for the doors and windows. Air infiltration is code maximum, no more than 3 ACH50. Let's also assume each floor is 30x50 and 9 feet tall. Design temp is 3F, indoor temp is 70F, soil temp is 50F.
    Heat loss through the roof is 1500 square feet at R38 at 67F delta equals 2,645 BTU/hr.
    The perimeter of the house is 160 feet, at 27 feet tall the wall area is 4,320 square feet. Insulated walls at R21 make up 85% of that, which is 3,672 square feet. At a 67F delta that gives a heat loss of 11,715 BTU/hr.
    The windows and doors are 15% of the wall area, or 648 square feet. At R5, that's 8,683 BTU/hr.
    The basement floor is R10, the interior temperature is 20F above ground temperature. That's 3,000 BTU/hr.
    Volume of the house is 27*1500= 40,500 cubic feet. ACH50 is 3 air changes per hour, or 121,400 cubic feet per hour or 2025 CFM. Natural infiltration will be 5% of that or 101 CFM. With a temperature delta of 67F, 101 CFM gives 7,055 BTU/hr.
    Add that all up and you get 33,098 BTU/hr, or 7.4 BTU/hr per square foot. That's for code minimum new construction.
    jesmed1
    Second to last paragraph there, @DCContrarian . More for my own education. if the code minimum air changes per houris 2025 cfm, on what basis is it correct to estimate the heat loss for 5% of that? I would think it would be necessary to size it for the entire volume, unless you are assuming that there is a 100% efficient energy recovery ventilator in there? Makes a bit of a difference…
  • jesmed1
    @josephny mentioned that he has a Lifebreath ERV installed, but didn't mention the size. I don't know how efficient those are.
  • LRCCBJ
    The 3 air changes per hour is based upon -50 Pa (during the test) relative to the ambient. At 0 Pa, the estimate for actual infiltration is 5% of that.
    For the record, I've yet to see a true R5 window or a true R21 wall (from 2x 6). Those numbers are magical!
    Hot_water_fanCanucker
    Maybe a handful of new construction out here actually meet the new #’s.
    Pencil whipping is as strong as ever.
    LRCCBJ
  • jesmed1
    So I think you're making my point, which is that perhaps the OP's "super well insulated" house maybe isn't quite as good as he thinks.
    We don't have enough data to make an informed decision. Only t-stat temperatures and run times data.
    LRCCBJ
  • DCContrarian
    Here (Washington, DC) they take it pretty seriously. In particular they require continuous exterior insulation and blower door testing on new construction.
  • DCContrarian
    We also know the square footage, design temperature and a reported 11kW electric load.
  • jesmed1
    I agree those are needed in order to assess how well the heat pumps are performing.
    My only observation was that the contractor calculated a Manual J heat loss of 78,000 BTU/hr, which for the OP's square footage I don't think qualifies as "super well insulated."
    Of course, it's possible the contractor was conservative with his Manual J.
    Thats a small % of the information needed.
    Air temperature in and out at the air handler?
    Has the charge been pulled and weighed?
    Just like the blower door tests the data entered needs to be checked. Pencil whipping manual "J" is done all the time. Do you think the building department actually checks any of those #'s?
    Steamhead Member Posts: 17,734
    If this were my house, at this point I would be installing either radiant floor or cast-iron baseboard, or some sort of panel radiators.
    Why? Because the heat pumps just aren't doing the job. And there doesn't seem to be any "smoking gun" that would explain the problem.
    The OP, @josephny , just wants a comfortable house. He clearly does not have one, even after spending all that money. If the heat pumps can't give him this, it's time to take a different route.
    Consulting
    jesmed1Hot_water_fanDan FoleySuperTech
  • LRCCBJ
    I'd really like to see how they get to R5 glass and R21 walls on 2x6 construction. I know of no materials that will provide that. Furthermore, as you know, the R value of a 2x6 is 7………….so the insulation must be MORE than R21 to achieve a true R21 for the wall. Good luck with that.
  • DCContrarian
    They require at least an inch of continuous foam insulation over a 2x6 wall.
    Chortle chortle… and here I sit, in Cedric's 1780 to 1893 home, not a fancy modern triple pane window in sight, and precious little insulation… with a known and measured gross heat loss rate (including infiltration) of 30 BTUh per square foot usable area at a delta T indoor-outdoor of 70 F on an average sort of day (a good bit more on a very windy day!)
    Not sure how far we've come in the last century or two…
    SuperTech
  • LRCCBJ
    ………and, apparently TRIPLE pane windows……………….$$$$$………………..!!
  • LRCCBJ
    ………..well, going from 30 😲 to well below 15………….I'd say we've come a long way…………..but, that's just me.