Thanks for that! Another good reason to only add distilled water. I wonder if there's a negative.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Cost and time. I'd have to add a gallon a week from flushing the LWCO on one system. (Mcdonnell Miller)
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
I didn't see anyone mention baking soda as a steam boiler additive. Is this not a good way to control the acidity?
Robert W.
Energy Kinetics
0 -
It can be used. It forms the buffer pair with sodium bicarbonate/sodium carbonate with a stable pH in the range of 9.5 to 10.0. You may have to use sodium hydroxide (fun stuff) to drive it to the stable range. As I mentioned earlier, you will need to titrate using your actual boiler water to determine the correct amounts.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I think Bicarbonate of Soda is a base, but the sodium part is undesirable IIRC. There are much better ways to raise PH
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I bet you could get to the point where you could return the flushed water into your boiler it would be so clean
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
☺️ Hasn't happened yet, but here's hoping. There's 60 years of scale in that bad boy.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
And that is why you titrate it: you want to use the least amount possible to reach the stable range, if that is your objective. This is one of those situations — among many! — where too much is WAY too much.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
What about borax? I'm only asking because it's really nice in a swimming pool. Might be a really bad day in a boiler?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Borax is a fascinating stuff. Useful for all kinds of things. There are several buffer pairs using borax as the basic side of the pair — none of them are either cheap or easily available, and they all buffer between pH7 and pH8. Borax alone, without a buffer pair, can go quite basic depending entirely on concentration, which is undesirable for pH control as the resulting pH is concentration dependent and unstable.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I have not had time to go through all comments. First, I wrote in the acidic direction. This means that it was reducing. I would like to point out to the members, that the advice that I gave on water treatment is not my own. It came from various boiler manufactures cast iron, fire tube, commercial and residential. Also, water treatment specialist. I am new to the steam heating industry and one of the first thing I noticed is a lot of water treatment practices that are contrary to what the manufacturers instruct. My rule is simple, If you cannot explain what your treatment is doing chemically, then you should think twice before you do it or advice others. I took chemistry in engineering school and I had learn from the water treatment people why certain things should or should not be done. I thought best practices is one of the things that this site is all about.
1 -
Please see an older thread I created which about half way down shows what I found Steamaster does. I asked what the individual chemicals listed in the MSDS would do for water in a boiler on a chemistry forum. I feel it's quite accurate.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I do not know what else I can say. My point is totally missed by some of you. I tried
0 -
I'm sorry.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I honestly don't think anyone here has disagreed with you. I pointed out that several boiler manufacturers recommend PH of 7.5 - 11.
I assume Rectorseal (the maker of several very similar treatments including Steammaster tablets, 8-way, Surge-X) has some chemists working for them since they manufacture and sell probably millions of dollars worth of chemicals every year. It's not in their interest to hurt anyone's boiler.
What is your recommended way for me to follow my boiler manufacturer's instructions to raise the PH other than to use one of the products that is advertised and proven to do so?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I'm one of the "some of you" I'm afraid. What was your point again, @ARobertson13 ?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I can totally understand how homeowners who mean well can be sucked into meaningless (or harmful) "voodoo practices" for stuff like water treatment of their steam boilers that go against what their manufacturers' recommend. And, yeah, I can see how that can be frustrating to someone such as yourself who has knowledge about this stuff.
However, it's not like the manufacturers give abundant information about proper maintenance and troubleshooting. Earlier, I provided the one paragraph from my boiler manual about water treatment. It basically says "do nothing" to the water if your system is water tight and that treatment might be necessary if the system has leaks or the water supply is hard and in that case consult a local water treatment specialist. This sounds like they're passing the buck. Probably they feel that if they give any advice other than "consult a specialist" that that they can be put on the hook if the end-user misunderstands their advice and destroys their heating system (or worse).
The problem is that water treatment specialists (I assume that means plumbers who are skilled with steam?) are not easily available. Moreover, a licensed professional can "say" they know what to do quite convincingly but then mess up horribly because they know their customer doesn't know any better. This is what happened to me, multiple times. With cranky old houses like mine, if you want something done right, you've really got to hustle to find someone or do it yourself. Good contractors these days can get plenty of work without having to take on complex jobs. I totally understand that and I don't blame them. The one super-skilled steam guy I ever got to come to my house (he had done recently done amazing steam system work on a large school that was repurposed into an office building), ended up ghosting me.
So far, @ethicalpaul has provided the most tangible advice, based on his observations and results— basically keep the pH at around 10. And perhaps use de-oxygenated water (distilled, pre-boiled, or de-humidifier condensate waste).
My situation is somewhat bad: I've got sludge in my boiler. I would like to get that situation under control. The reason I got sludge, I think, is because of some years of lazy maintenance as well as a badly leaking pipe at one time. Does controlling pH halt corrosion when it's already started? ¯\_(ツ)_/¯
1 -
My situation is somewhat bad: I've got sludge in my boiler. I would like to get that situation under control. The reason I got sludge, I think, is because of some years of lazy maintenance as well as a badly leaking pipe at one time. Does controlling pH halt corrosion when it's already started?
Because of this thread, and because of the time of the year here in the States, I made a trip to my friend's house just last night. Her situation is similar to yours, and also perhaps to that of @SlamDunk so maybe what I found can help you both.
She has a reasonably-sized boiler for her house, it's 4 sections and three burners, a Lennox branded Dunkirk design (that is prone to carryover due to its side-supply design) installed in 2007.
The boiler behaves quite well but she tends to listen to her plumber who advised her to drain the boiler monthly (BAD ADVICE). She certainly hasn't done it every month, but she has done it periodically. Her water is generally brown when I look at it, but I've never tried to get the corrosion there under control before. But with her permission I am now.
After last night, and also remembering my very-unmaintained boiler that I used to have, I think it can be a rather long road, but not a hopeless one. I'll tell what I did and what my plan is going forward. See if it matches what you are seeing.
- Her boiler has run a few times this season, and about a month ago she drained probably 4 gallons. The water was clearish-looking in the gauge glass. First, I released about 1/2 gallon from the boiler drain which started out medium brown but then ran mostly clear and indicated, as expected, about 7ph. Then I flushed the bottom gauge glass port. Then I cleaned the pigtail for good measure. It was dirty but not blocked.
- I added some water to the cold boiler to get it to nominal level again.
- I added only about 3 ounces of 8-Way the easiest way I could which was the main vent fitting, believe it or not. (Her main returns to the boiler resulting in a 4" wet return right next to the Hartford Loop.)
- I steamed the boiler for awhile to let the condensate carry the 8-way into the boiler
- Very quickly the water started to turn brown in the gauge glass. There was a little water coming into the glass from the top port which indicates foaming. Her boiler doesn't have a sight glass on the header (pity) so it's really hard to tell if it was carrying over, but it may have been slightly (the water level was down about 2-3" in the gauge glass).
- I stopped the boiler after about 10 minutes of steaming and drained about a gallon of what was surprisingly dark brown water which indicated about 10ph (higher than I expected). Some of that color was no doubt from the 8-way purple indicator, but a majority must have been from sedimented "mud" and/or scale that the 8-way freed up. I was reminded at that moment of my own experience in 2017 with my original boiler at my house which was another unmaintained and filthy (inside) Dunkirk-design Utica. In one of my very first boiler videos, you can see me being clueless about it but I already had a sight glass installed at the end of my main which indicated quite clearly that I for sure was carrying over (this was immediately after I started trying to clean my boiler with 8-way). See the 2 minute video here, it's quite shocking to see carryover for the first time!
- I ran the boiler again, and again it seemed it might be carrying over some (but not catastrophically—steam was getting to her radiators). I stopped it again after 10 minutes and drained another brown gallon that measured about 8-9ph, then slowly added more fresh water. I repeated this step once more.
- Finally it was getting late. I didn't want to leave her with carryover condition, so I drained to the bottom of the gauge glass and again slowly refilled. The water I drained this last time was still brown, I believe still from the freed-up mud/scale. When I dumped the bucket there were in fact some scale pieces.
So between my experience years ago, and last night, and what @SlamDunk saw, it seems pretty obvious we do have to be careful of carryover when adding 8-way (and I'm sure any of the other treatments) to boilers with scale and/or mud buildup (a new clean boiler has been shown to be able to handle even an extreme overdose without carryover. Not to say that's advisable, just stating the fact). This is interesting and ironic given that all these treatments claim to reduce surging. My own thinking has been flawed regarding this because I missed the idea that even though my clean boiler can take seemingly any amount of treatment, mud/scale in an older boiler can present a completely different behavior.
My recommendation is start SLOW and be ready to drain off the freed up stuff to avoid carryover. As much as it pains me to add fresh water during these steps, I think it's necessary. I feel that the amount of corrosion caused by this fresh water should be much less than the overall benefit of getting the water chemistry to a place where corrosion is greatly reduced over the long haul.
My plan going forward is to revisit this boiler in a week or so and try another couple ounces of 8-way. I believe that eventually the vast majority of mud/scale that is going to break free will do so, then her boiler can be almost as clean as a new one and won't require any cycle of drain, add fresh water, corrosion. Of course I'll report back, thanks!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el2 -
@ethicalpaul, well, that time has come. I put it off for as long as possible and am now powering up the steam boiler to avoid divorce :-).
When I shut it down last spring, I flushed/drained it and refilled it with water and added an entire bottle of 8-way Rectorseal. It had sludge when I drained it last spring. As I drain it now there is hardly any sludge, it just has a purple tint to it. Not surprising, of course, because of the rectorseal had been sitting in it during the warm months. By the way, the pH is solidly at 11.
This time, I'll try a half bottle (1/2 quart) of the 8-way and monitor the pH periodically, and only add more if it drops below 10.
Hopefully, I can get another season or 2 with this boiler. There is some concerning corrosion on the wet return. Not sure how big of a problem that is, but keeping my fingers crossed.
1 -
What do you mean this time? You aren't going to drain the nice 11 pH water with 8-way in it that's not rusty, are you?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
The majority of it was clear, but after it drained, I partially refilled and drained. This seems to stir up loose stuff at the bottom which does make the water muddy, I just want to try to get that stuff out as much as is practical. It’s still way better than last year, so some progress has been made.
I realize that fresh water has more O2, but won’t that boil out as soon as I start the heat? In other words, it’s the continuous exposure to O2 that causes corrosion, right? The hour or so of flushing with fresh won’t eat through much, I hope!
0 -
No, it just seems a shame to throw out nice boiler water 😅
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I wonder if I should have just just let it boil for a while before flushing it. It seems that the sediment had settled over the summer and didn't really come out until the water was more agitated.
Anyway, after adding the 8-way (1/2 quart) through the sight glass port, I let it sit for a couple hours and then poured some water out of cold return to measure ph, it was 8. After the first day heating, I measured it again and ph was 11. It probably had not fully mixed in until there was boiling.
This winter, I am going to try flushing half a bucket and replenishing with still water once a week in the hope of getting more sediment out over time— I had neglected flushing for a few years, maybe this will help?
0 -
If you're adding boiler water treatment without actually testing the water, then you might as well be using a Ouija board to determine the answer to chemistry questions. And yes, I'm old enough to to have actually played with a Ouija board - the "Magic 8-Ball" of the before times…
0 -
What do you guys think of NYC tap water and steam boilers? According to the DEP it has a PH of 7.2 which is close to neutral. NYC water is considered to be the some of the best water in the US.
I dont believe they add anything to it, its all natural from the upstate reservoirs. Do nyc boilers have an advantage even if they are being filled to frequently with fresh water?
0 -
The type and chemistry of the MU water varies all over the country. What works in one part of the country may not work elsewhere. Also the type and quality of the CI is variable.
In my area (Western, MA) many have given up on Burnham and from what I have herd Eastern, MA and Rhode Island are worse. Why? I don't know because I know nothing about water chemistry. Chlorides in the water is what I have herd.
But I know this much in my 46 years of being in the business.
Boiler failures pre 1980 was almost nonexistent. If you had a failure back, then it was usually from excessive MU water or a failed LWCO. HB Smith was the big player around here because their foundry was in Western, Ma years ago. Now all brands of CI boiler are sold around here
Now all CI boiler seem to not last as long as they used to for several reasons:
Increased firing rates/lb of CI pushes the boiler harder
The thickness of the sections is claimed to be less
Changes in mU water quality
We all know of CI boiler 100 years old (or more) that lasted and I am sure there are many still running that never had a drop of water treatment. Why? More iron and less firing rate/lb of CI is probably the biggest reason.
In the 80s 90s and 2000s Burnham made a big push in this area. The failures were many. And not just on steam their HW boilers failed as well and they didn't get serviced any differently than any other brand. Most of them you would be lucky to have them last 10-15 years. Water or steam.
When the efficiency of the boilers needed to be pushed up due to government regulations the life expectancy of the boiler dropped.
The harder a boiler is pushed and the more condensate a system loses (more MU water….like process boilers) the more important water treatment is.
I have personally cut up and removed steel steam boilers that were 90 years old that were in good condition. But that was HP steam with I guess good water treatment. But the old boilers were not fired as hard…….they were by today's standards oversized.
Less boiler mass/BTU input is probably why Mod Cons fail in a shorter time frame and are required to have better water quality.
All in the name of Progress😊😊
0 -
The things I've noticed about my tap water….
It always starts with a pH of around 7 but after it's been in my boiler for awhile that appears to drop some.
Yet, in my swimming pool I absolutely hate adding water to it because the pH always climbs above 8. Which of course is followed by me having to add muriatic acid to bring it back down to something reasonable like 7.6. And it takes quite a bit of acid over time to bring it back down to a nice stable number.
The water's total alkalinity tends to be high so I'm going to assume whatever is giving it a high TA is removed in the boiler. Does calcium count as a buffer?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I hate to beat a dead horse, but in my WM SGO-5 (about 5-6 years old), it has some type of elastomeric or rubber seals between sections. I had added some 8 way. pH was around 11. Then someone had posted about having a seal leak on their WM boiler and it was blamed on their pH of 9. I drained completely a couple times and refilled. I now have a pH of 9.5. Water is very clear. I know about the buffering capacity of the 8 way from this board. WM recommends pH 7-8.5. Should I continue to chase the pH or just leave as is? My main concern are he seals. My system is very tight. I think it added one gallon all last season. Thanks.
0 -
In my experience, the 8-way will free up sediment or scale and put it into the water. So I would continue doing what you're doing and let a little water out a little while after boiling when it has a chance to settle a bit, as you described.
The new corrosion/mud creation will be very low and eventually you'll just have a clean boiler that only needs a little drained off annually.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
The case we heard about from the homeowner said that WM claimed that his 9.0 pH led to the failure of his gaskets. To me that is insane that WM would say that 8.5 was OK but 9.0 was death to their boilers.
I suspect his pH had nothing to do with the failure and WM was just looking for a reason.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
I think the differences between a pool and a boiler are many and it's difficult to know exactly what in each case might be leading to a particular observed change in pH.
I don't know anything about pools, but I think they, just like the human body, have a pH buffering solution that works to keep the pH in a "good" range. It's difficult to change the pH in the presence of a buffer.
I just don't have enough basic chemistry to understand exactly which ingredients are the buffer part of a given pool or boiler additive, but you can get an idea from google. I don't have a lot to add here, but I wanted to reply so your post wasn't ignored.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I don't use any "pool additives"
Literally the only thing I put in my pool is bleach, occasionally cyanuric acid and on a rare occasion muriatic acid to bring the pH down.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
i
I believe the pH buffer in a pool is the alkalinity, which is controlled with baking soda. The pH is controlled by adding soda ash or muriatic acid. But the "alkalinity" is supposedly what buffers the pH, at least that's what our pool guy told me.
0 -
So, I guess I should just leave well enough alone at 9.5? As I mentioned, water is very clear after about 5 seconds of draining.
0 -
I'm using a WM EG-40 from 2011 and I've been using Steamaster since 2012.
I haven't decided to change anything I'm doing. If the gaskets leak, it'll suck but I'll deal with it if it happens and then make a decision.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
2 -
Many pools experience PH rise which is primarily caused by the release of carbon dioxide to the atmosphere. I believe it forms carbonic acid when in solution. I wonder if the boiler system doesn’t allow this as it doesn’t have the same exposure to the atmosphere (though its not exactly a closed system). Alkalinity speeds this process as the alkalinity ions compete for the hydrogen in the water, changing the equilibrium and letting more CO2 leave quickly
Thats probably an overly simple explanation but its what my tiny brain has been able to absorb from troublefreepool, another blog site which competes for my limited attention span.
@ethicalpaul - I hate to bust your theory about new vs old boilers and 8-way, but too much 8 way (ph got above 10) caused surging on my new install. The surging happened immediately after adding it and happened right after a good skim so I think the water was otherwise clean and the surging can be attributed to the too much 8-way.
I drained and added just enough to the refill to put the ph around 9.0 and its been good since. Before treatment the ph was down around 7.0 which was the minimum level in the manual so I wanted to add some to bring it above minimum ph.0 -
-
You're not breaking my bubble. I have published the video evidence showing me adding way way too much 8-way with no ill results. Your water may very well have had some oil or other contaminant in it or something (shrug).
I have also boosted my pH with a pH booster product for pools with the same result.
I do NOT state that 8-way or other pH booster can't be involved in surging, just that it's not the direct cause.
But pH alone does not cause surging.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
This is what happened when I tried 3 tablets instead of 2. 2 tablets runs about 1" WC under the same conditions.
https://youtu.be/NAtcDLePJis?si=B5Zyd4J3HtO02oP-
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
1.3 inches of water column instead of about 1inch of water column? Hardly conclusive or persuasive 😅
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements