Residential Chiller
Customer of mine has a chilled water system in his home. Home is about 12,000 sq ft. They have a small cooling tower outside and a packaged refrigeration system inside mechanical room with refrigerant to water heat exchanger. They have 11 3ton chilled water fan coils. What manufactures are there for system replacement. I was thinking of a air cooled packaged chiller outdoor unit? Or maybe standard condensers with a refrigerant to water heat exchanger inside mechanical room. Any help is appreciated. Thank you
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
I have seen systems where they use a brazed plate head exchanger as an evaporator but that was a relatively small system. If you change it to an air cooled condenser you need a condenser that can modulate to the load. Maybe some number of staged condenser.
I would use an air cooled chiller and scrap the water tower.
One important thing is buy the chiller with a REMOTE chiller barrel (heat exchanger). If you do that you will pipe refrigeration from the new chiller outside to the new HX inside. Don't try and rig up standard condensing units with your own HX it will become a controls nightmare
By doing this you will avoid having any issues with having to drain the chiller system water in the winter or using glycol and have no issues with freezing problems.
Carrier, Trane, York and there are others can supply this
Mitsubishi/Trane has several air to water models in the City Multi line of VRF units.
Thanks for all the insight. I was looking into the multi aqua air cooled chillers. Using a 10 ton & 5 ton or (3) 5 tons. Refrigeration would be self contained outside. I would then have to run properly size chilled water piping to mechanical room and install a pump. The installation manuals show a storage tank/buffer tank. Is the tank absolutely necessary? Maybe to eliminate short cycling on mild days
ASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
15-Tons of cooling in a residence?
Yep, a compressor is going to have a minimum output and a minimum recommended run time, the buffer tank is sized to absorb at least that amount.
Beyond that, the buffer tank is not your friend. You want the water as cold as you can get it, anything that mixes the water is robbing performance and efficiency.
There are residences, and then there are residences
Maybe I missed something but isn't the installed equipment capacity 33 tons? 11each 3 ton fan coils? so 10-15 tons is well below equipment capacity? With a bunch of internal loads, and glass I wouldn't be surprised to have peak loads close to that 15 ton point, but you definitely want to size condensing units that have lower minimum outputs because the average load likely won't even be half of that. The more I type the more it just makes sense to run the manual J, surely someone has prints and historic data for a 12,000 square foot home? The owner knows whether they plan to pack people in there or not. In my area the owners always want to size for the absolute worst case scenario and then they never actually see those conditions.
even out here in the Hamptons I can’t think of maybe a hand full of 15-Ton homes.
If you buy an air-cooled chiller and pipe the chilled water indoors you going to be faced with filling and draining it every spring and fall and maybe blowing the HX in the chiller out with air to prevent freezing. Or use glycol.
Both are a PITA and there is always the risk of a freeze up. JMHO. I would put the chiller barrell indoors.
There was a thread recently on GBA where a guy said he moved the heat exchanger from his Arctic indoors. It involved pumping down the refrigerant, cutting and lengthening the refrigerant lines and then recharging and adding a bit for the longer lines. But there are a lot of advantages to keeping all of the water in the house. For someone who works with HVAC that's all in a day's work.
See: post #44.Arctic goes up to five tons.
Why go through the effort of taking the charge out and relocating the HX?
All your doing is voiding the warranty
They make and sell chillers with remote barrels. I have installed many that way. @pecmsg is correct. Why fill and drain in the shoulder seasons?
It was 70 deg in my area today. We usually draing everything outdoors no later than 11/15 because usually by that time it's getting down around 18-20 at night. 32 may be freezing but you need some TD to make it freeze.
@EBEBRATT-Ed what manufactureshave remote barrels. My suppliers are providing packaged outdoor chillers. These are not common in my area.(North east). I would do a load calc once we find equipment
347-692-4777
ASMHVACNYC.COM
Ideally I'd go other way. Chiller in heated space and remote air cooled condenser outside. No glycol nor winter draining.
Artic heat pump is one
Almost every chiller MFG can provide the option of a remote barrel
- 15.8K Strictly Steam