Remorse w/ My Decision: Single Pipe Steam Radiators Kept and Home Renovated
I recently closed on a 2 family home with a steam boiler for the top unit (bottom unit has new baseboard heating). I’m living in the top unit.
Now all of the work is done and I have an immense sense of dread. I wished I had just removed the single pipe steam radiators to modernize the house, but didn’t. I paid for all of the work for ducts and an air handler, and could have leveraged this to move to a single system with less maintenance.
Well... the steam will provide more comfortable heat, and enough of it -- if the new boiler (did you really need one?) was installed correctly, and the piping is insulated, and the venting is balanced. The AC will do the job nicely -- as AD. It would NOT have done the job well for heating, unless the ducts were arranged for heating, and it would have cost more to install the heat pumps required.
I'd say you did fine. You would not have saved money on the forced air, and you would have been less comfortable.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England3 -
Six of one, half a dozen of another.
As you said, the way you went, your ducts and vents are optimized for cooling. Having warm humid forced air coming through cold attic ducts can have condensation problems. Steam heat gives the best radiant heat. Future idiot tenants on the second floor can't freeze your steam radiators.
Try it our for a winter and summer, you might decide you like it. If you don't, you might be able to sell or rent to a steam lover here on HeatingHelp.
Thank you both for making me feel better about my decision. I spent a lot of time originally deciding. I wanted cooling that did the job well and a dedicated heat source. I would have ideally wanted baseboard heating but the installation was too intrusive for the unit so I decided to keep the steam boiler, while replacing it because the old one was oversized and 30 years old barely hanging on.1
I'm just a homeowner, but based on what you said, I think you made a good decision. Why did you replace the boiler at all? The more important question is how the new boiler was installed...If you're concerned, post some pics of the boiler and the piping all around it as well as the main vents, if any. Did you calculate the EDR beforehand to size it correctly? Although this doesn't really matter much now because it's a done deal, it can help to know if your boiler is over or undersized and by how much.1
I would have done the same thing given the choice. As mentioned above...since half of the original steam system was removed the new boiler should be sized according to the existing EDR, not sized to the old boiler.
An atmospheric boiler and steam system is about as good as it gets in an existing house aside from maybe a condensing boiler and baseboard heating... but those have drawbacks as well.
Steam is very low maintenance. I am curious though to see if your boiler is piped correctly and sized correctly to the existing EDR.2 -
We'd love to see some pics of the boiler, the piping around it, and heck I'd like to see pics of your mini splits. Steam is a very simple heating method, and as said above, it's very good. If your installer knew what he was doing, it's silent, and it doesn't blow dust around or make drafts.
And don't worry about the mini splits, for some reason a lot of people here hate them. I installed 3 head units in my house and they are so nice. Way better than the window shakers that came with this house.NJ Steam Homeowner.
To add to the above, the AMA recommends against forced air heating in general due to respiratory health issues and in a fire situation, you wouldn't want it either.ethicalpaul said:We'd love to see some pics of the boiler, the piping around it, and heck I'd like to see pics of your mini splits. Steam is a very simple heating method, and as said above, it's very good. If your installer knew what he was doing, it's silent, and it doesn't blow dust around or make drafts.
You probably made the good choice. I only hope the ductwork in not in the attic... it would likely create large leaks and have very large losses since typical 42 Degree north latitudes are recommended to have r-38 in the ceiling and typical ductwork insulation is about r-3 to r-4To learn more about this professional, click here to visit their ad in Find A Contractor.1 -
Don't beat yourself up. You made the best decision at the time with the information you had. It will get the job done mad dog 🐕0
The Steam Whisperer said:To add to the above, the AMA recommends against forced air heating in general due to respiratory health issues and in a fire situation, you wouldn't want it either. You probably made the good choice. I only hope the ductwork in not in the attic... it would likely create large leaks and have very large losses since typical 42 Degree north latitudes are recommended to have r-38 in the ceiling and typical ductwork insulation is about r-3 to r-40
As promised here’s a picture of the system in my 1920’s basement.0
I’m trying to find something the installer did right, and I can’t find it.
There is a picture in the manual of how it’s to be done and that’s not it. Looks like colliding header for sure. I can’t make everything out to see specifically what is wrong, but there is a lot of piping that doesn’t make sense. It appears it might be counterflow, which could explain some of the piping.
That contractor needs to stop working on steam.2 -
@Pinec0ne Please post more pictures of the boiler and piping from multiple angles, the plate on the boiler itself that has the name of the manufacturer and model number, and any main vents you might have. I agree with the above. It was not piped correctly. Steam should not be piped in copper either.0
I can add more pictures, but what should I do about the installation contractor? Should I contact them. I just had this done in april0
Also most of the piping is legacy, the only changes to the system I inherited in regards to piping is where you see the copper0
It really doesn't matter what was there prior. When the boiler is installed the contractor should look at everything and pipe the boiler properly. It appears to be a colliding header which is a strict no no, and should be common knowledge for any contractor installing steam. Peerless has a document they published that shows why. With more pictures we will be able to comment further.Pinec0ne said:Also most of the piping is legacy, the only changes to the system I inherited in regards to piping is where you see the copper
For me, yes I'd go back on the contractor, but if you've already paid I doubt you will get much out of them, but I've been wrong before.
2 -
Not yet. Get all your ducks in a row first. Threaded steel pipe is preferred over copper, because copper has a greater coefficient of thermal expansion. There have been a few instances where the expanding copper piping has actually ripped the sections of the boiler apart. That's rare, and there are copper piped boilers that work OK. There are also other reasons to use steel over copper.Pinec0ne said:I can add more pictures, but what should I do about the installation contractor? Should I contact them. I just had this done in april
You likely have other deficiencies in the way this was piped that do not meet the boiler manufacturer's minimum standards. Could cause a safety or warranty issue. It may be loud and bang, because the steam collides with the condensate returning from the radiators. You might not even have a Hartford Loop, which is a pipe routing practice on the condensate return that has been used for over 100 years.
https://en.wikipedia.org/wiki/Hartford_Steam_Boiler_Inspection_and_Insurance_Company
We can tell if you have that from a picture of the other side.
Once you post more pictures, the steam experts here can help you make a list, and your can take that to your contractor.
Piping a steam boiler in copper is like the contractor plastering a big sticker on the boiler that says three things:- I DON'T UNDERSTAND STEAM
- I DON'T CARE ENOUGH TO DO THE JOB RIGHT
- I DON'T OWN THE PROPER PIPE THREADING TOOLS
1 - I DON'T UNDERSTAND STEAM
Thanks I’ll add more pictures today0
adding adding more pictures here0
I bet it was not Skimmed either. How could they ? At least the way the manufacture recommends.
https://uticaboilers.com/wp-content/uploads/2023/04/240011556-UH16-SERIES-IOM-REV-L.pdf
One Pipe System0 -
Can someone please help give me a summary of items wrong with the installation
1. The installers. 2.The copper. 3. The way that the boiler piping connects to The first Tee.
Can't quite see how the boiler piping on the right side , connects to the header.0 -
Lack of skimming port.0
I'm guessing that the contractor is paid in full. Too bad.
That is your only leverage. Now you need to depend on the integrity of the contractor.
You need to contact the installing contractor at once… and ask them
1. How long is their warranty since it is not going to be operational until October. That is 7 months from the install date.
2. Does it cover improper piping design by the installer? (because it don't look like the install manual
3. What do they do about noisy banging piping due to improper piping?
4. Are they going to skim the boiler as the manufacturer’s directions state after operating for 2 weeks. Will that be completed in October?
5. Can the contractor tell you how to skim the boiler because there is no place in the near boiler piping for skimming. That is because the near boiler piping is not installed according to the instructions.
If the contractor is not cooperative, there are ways to induce cooperation if needed.
Good Luck
Mr, EdEdward Young Retired
@Pinec0ne What is the model number? It is located on the white sticker here. Or just post a pic of that. Agree with all of the above. I'm not a pro, but at minimum all the copper above the waterline needs to be replaced by threaded iron pipe, but preferably all of it is replaced. More pictures from a few other angles would help.
My first step would have been to remove old boiler and cut away all the old near boiler piping (legacy piping) to this point.
The dry return pipes would would be connected at the wet return behind the boiler (Green)
The new boiler header would be connected to the two risers (Red)
Then I would place the boiler in the basement and build the near boiler piping as shown in the manufacturers instructions (The diagram is very clear)
After the near boiler piping is finished and there is a place to take off the risers from the header. (the Blue highlighted section) I would position the boiler so the header with the risers openings are lined up just below the main elbows that are pointing down. (Yellow circle).
I would do the entire job in Black Fittings and Steel Pipe. But there are some cases where the wet returns can be copper. You need black fittings in the exact order of the manufacturer's diagram because you need swing joints in order to prevent stress on the cast iron boiler connections as the different parts expand and contract on start up. Since everything does not get hot evenly on start up, there must be room for some movement. You will be able to feel the steam move from one fitting to another as the steam travels from the boiler, to the header, to the risers, to the main, and down the main to each radiator. Since this is not happening gradually or all at once evenly, there will be stress as one part gets STEAM HOT while the next part is still cold. So you need a little give. (the technical term is Qualified Engineering Adjustment)
I hope this answers your questions about what is wrong.
Mr. Ed
I'd like to see that recommendation!The Steam Whisperer said:
You probably made the good choice. I only hope the ductwork in not in the attic... it would likely create large leaks and have very large losses since typical 42 Degree north latitudes are recommended to have r-38 in the ceiling and typical ductwork insulation is about r-3 to r-42 -
Jumper..I think Burnham comes with a Drop Header kit and the Sears (Oh how I miss My Hicksville Sears!) boilers did.. I have a Picture in my archives. Mad Dog 🐕0
I still have my Sears Hard Plastic rugged tool boxes and my genuine rubber hose from 30 yrs ago! Heavy usage ..still goin strong. Mad Dog 🐕0
The first thing Ia guy did after getting his first real job was to buy a Sears Craftsman tool kit - $39.95 for a complete kit (100 pieces including that grey steel toolbox) I still have all the sockets and wrenches from that kit but I did eventually wear out one of the ra6chets which they replaced.
Piss poor management did them in, they closed their catalog sales just before the internet took off. I still have and use the Fluke 77 meter I bought just before the catalog sales was shutteredSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
3PSI gauge0 -
I've said it many times. Sears could have been Amazon. Sears missed the boat, huge.BobC said:The first thing Ia guy did after getting his first real job was to buy a Sears Craftsman tool kit - $39.95 for a complete kit (100 pieces including that grey steel toolbox) I still have all the sockets and wrenches from that kit but I did eventually wear out one of the ra6chets which they replaced.
4
- 110 Chimneys & Flues
- 979 Plumbing
- 387 Solar
- 17 Recall Announcements