Burned wire insulation on Goodman flame sensor wire
duncans7
duncans7 Member Posts: 4
Has anyone seen a blacked/fried/burned up (whatever term you’d like to use) wire connect to the flame sensor. It is a Goodman GMS90703A unit. No heat call. Unit igniting and turning off and repeating. Flame sensor cleaned and working again but I have never seen flame sensor wire insulation being burned from the inside like that before. Any thoughts would be appreciated.
  • unclejohn
    unclejohn Member Posts: 1,833
    Flame roll out or it was laying on top of the combustion top at some point. It was not heated from the inside out if thats what your thinking. I don’t know why anyone would have a torch down there but I have hit a few wires with a torch flame.
    mattmia2duncans7
    Jamie Hall Member Posts: 27,148
    Agreed. Perhaps more to the point, that wire is toast -- both literally and figuratively -- and needs to be replaced.
    mattmia2duncans7
  • duncans7
    I replaced the wire but there are no signs of a torch or other heat source. There are other wires that are touching the burner box below that are not marked like this one and the wire seemed to have been up out of the way the entire time from what can be seen.
    ethicalpaul Member Posts: 8,552
    No signs of a torch? How about that burned wire...that seems like a sign :sweat_smile:
    pecmsg[Deleted User]EdTheHeaterManSuperTech
  • BigPerm
    BigPerm Member Posts: 1
    I may be seeing the start of the same thing. When my ignitor starts, the flame sensor wire emits a small continuous blue spark where it touches the frame supporting the gas line. There is a small amount of soot there. Furnace is only starting some of the time. I wonder if it's a ground issue. I cannot find anything online about it.
    EBEBRATT-Ed Member Posts: 20,004
    That wire got heated from something. lots of discolored insulation
    EdTheHeaterMan Member Posts: 11,875
    109A_5 Member Posts: 3,788
    Hello @BigPerm,
    Sounds like in your case the insulation is probably age related dilapidated and the high voltage is arcing to the nearest ground. The one pictured looks like a torch or other flame got to it, since it is out in the open and not near metal to arc to. In either case the wire should be replaced.
  • realliveplumber
    realliveplumber Member Posts: 354
    Different problem, someone posted on a thread, with not the same problem.
    One was the melted wire, 2nd is about a spark jumping to ground.
  • realliveplumber
    You should start your own thread.