Heat Pumps for Hydronic Baseboard Heat?
Hi Guys,
Do they currently make Heat Pumps to supply hot water to Hydronic Baseboard?
Thanks,
Pat
Dave Holdorf
Technical Training Manager - East
Taco, Inc
Peakedtoosoon said:"Don't forget your outdoor A2WHP will need Glycol"
Not if you install a split system, where the heated water is contained within the home.
https://www.literature.mestek.com/dms/SpacePak/SIS2-0421_2.pdfyellowdog said:spacepak's solstice system a2whp does not require any anti freeze.
Or the bitcoin mining farms sucking electricityWMno57 said:Apologies for the blacked out picture. Maybe all the electric cars and heat pumps have caused a rolling blackout. I'll fire up some Traditional Fuels and attempt to post a better picture.
Interesting find WMno57. Note that is for cooling mode, not heating. Typical chilled water supply temps are 4C-7C (39F-45F), somewhat above the freezing point. Anybody know is it typical for commercial chiller systems to use glycol? Does the Spacepak have poor control of LWT so they want extra safety margin?WMno57 said:https://www.literature.mestek.com/dms/SpacePak/SIS2-0421_2.pdf
"If unit is operating in a cooling capacity then the
water system must contain a mixture of inhibited
glycol and water with thermal protection sufficient
for the coldest expected temperature for the
installation. The inhibitor level can degrade over
time, and may need to be adjusted periodically.
The inhibitor is essential to prevent the glycol from
accelerating corrosion of metal components in the
system. The glycol and inhibitor levels must be
checked regularly (no less than once annually).
The minimum allowable concentration of glycol is
10% by volume in all installations."
Do you have easy access to the underside of the floor? Personally I'd be inclined to add staple-up radiant to the floor rather than removing and replacing existing baseboard.Would a good intermediate step towards eventually going to a HPWH be to replace the standard hi-temp fin-tube baseboards with new low temperature, fin-tube baseboards? I can do the plumbing myself. Would this be worth it, since I could then lower the supply temp of the current boiler down to 150F? House is a ranch - 1 heated floor - back loop is 35.66 ft of fin-tube, front loop is 38.83 feet.
Hi
Did you ever go forward with an install?
Siegenthaler is an advocate for AWHP. He has written a number of columns for Plumbing & mechanical and Plumbing and Mechanical Engineer. Propane is allowed as a refrigerant in Europe which enables AWHP to produce 175 degree water.
I'd like to see their outputs at 100 degree SWT. Then I could run it with radiant ceilings and no mixing valves.
Output is going to be directly proportional to the temperature difference between the surface and the room.
The 6" Runtal is rated at 600 BTU/hr/ft with an "average water temperature" of 180F. That means an aquastat high setting of 190F and low of 170F. A system like that will typically be designed for 20F drop so water is returning at 160F, the average temp in the radiator is 170F, or 100F above room temperature.
Typically with heat pumps you aim for lower drops because you're starting at lower temps. Let's assume 100F SWT and 90F return temp. So an average of 95F, or 25F above room temperature.
The output at 25F above room temperature is going to be 25% of the output at 100F above room temperature — 150 BTU/hr/ft.
@DCContrarian excellent, thanks! Makes for a large panel, but worth it to, in my case, run condensing all the time.
a wall can be turned into a supersized panel radiator , ideal for HP temperatures also
Siegenthaler gives the formula that heat flow from a wall or ceiling is equal to 0.71 times the difference between air temperature and water temperature (he doesn't provide a source). So if your water is leaving at 100F and returning at 90F, you get an average water temp of 95F, with room temp of 70F that's a 25F delta and 17.75 BTU/hr/sf.
So if you did the whole wall it would be close to the 150 BTU/hr/ft of the baseboard.
I'd supply the wall with 120F, a good operating temperature still for
HPs. And within the comfort range for sheetrock.
20 delta for 110AWT. The multiplier for the wall radiant is .8. I come up with 32 BTU/sq. ft.
Ceilings are a bit lower btu/ sq. output as you get some temperature stratification up against the ceiling.
I think that should be delta T divided by 0.71? I've used a slightly different constant for years — 0.6.
I would wait for the Daikin Altherma 3 due out 1st qtr 2025 is what I got from supplier. Sounds like certification is done. Or maybe Mitsubishi will finally release theirs, it would be my 1st choice.