Mitsubishi Branch boxes
gary7770
Member Posts: 9
I have a Mitsubishi system with seven cassettes that requires two Branch boxes. What I have not been able to find is do those branch boxes need to be located next to each other or can they be some distance apart?
Thx
Gary
Thx
Gary
I believe they can be anywhere, as long as the piping doesn't exceed the maximum lengths. Mitsubishi has their sizing software, Diamond System Builder, freely available at mylinkdrive.com. You'll want this to properly charge the system, it does the calculations for you; & will let you know if you're lengths are excessive as well.2
we have two within 8 feet or so, can't you space it a little bit? Or maybe loop some tubing a bit?0
Thanks for the reply guys. I'm actually wondering if the two Branch boxes can be 40 to 50 ft apart to cut down on the lengths of the line sets to the cassettes.0
There may be a limitation on the elevation difference between 2 branch boxes connected to the same ODU. I don't have the Mitsubishi specs but the brand I sell has limits on total piping, max/min individual pipe length, max elevation difference ODU->IDU, max elevation difference BDU->BDU, and max elevation difference IDU->IDU I imagine Mitsubishi has similar specified limitations1
Why math it by hand, or even guess?
https://mylinkdrive.com/USA/Software/Diamond_System_Builder?product&categoryName=Software
BTW, clever placement of the branch boxes is part of a solid design!
3 -
i just did a quick diamond system builder with the split to each branch box 50' from the condenser and each branch box 50' from there with 25 ' lengths to each head and it showed no errors. it looks like you can have 492' of total piping length on the system. what are the actual dimensions you need to have?0
This should be discussed with the installing contractor.gary7770 said:Thanks for the reply guys. I'm actually wondering if the two Branch boxes can be 40 to 50 ft apart to cut down on the lengths of the line sets to the cassettes.
Mitsubishis are great systems but the design and install phase is critical! So many feet total, so many ft above or below.1 -
- 87K THE MAIN WALL
- 115 Chimneys & Flues
- 107 Geothermal
- 983 Plumbing
- 389 Solar
