Joist Track PEX Hole Size & Position
Marvin007
Member Posts: 52
Will I get snapping sounds when the PEX expands if the PEX is touching the back of the hole when it goes through the joist to the next chamber?
I used this product to keep the pex away from the wood. It can be wrapped around the pex.
https://www.supplyhouse.com/Uponor-Wirsbo-A7250500-1-2-PEX-Suspension-Tube-Clamp-Bag-of-1001 -
No, I don’t think so. mine is exactly the same as your picture.
The only time I ever hear any expansion noise is on initial start .... very minor if at all0
I would use the clamps the jhewings suggested above. The one photo that shows the pipe in the middle of the hole looks great right now and looks like it would never make noise. However once that pipe starts to heat up, it will grow linearly. The formula is for every 10 degree rise it temp, it will grow 1.1" per one hundred feet of pipe.
The other thing I would do is to make sure the water temperature delivery system is weather compensation based. Modulate the water temp as it warms up/cools down outside makes that expansion of the pipe minimal.
Dave H.Dave Holdorf
Taco, Inc
2 -
These are specifically designed and use 1 3/8" hole. https://www.supplyhouse.com/Viega-55120-3-4-PEX-Suspension-Type-Tubing-Hanger-12441000-p"If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Do you mean foam pipe insulation like this where the pipe touches the crossing pipe. I only have a short piece of foam at the moment but I could use longer pieces.hot_rod said:some foam pipe insulation is an inexpensive way to make an isolator. No harm in doing it.
Sure, anywhere tube can run is a good use of pipe insulation
Typically 1-3/8” holes are drilled. That allows plastic isolators or thin walled pipe insulation to be used
Interesting use of a Studor air admittance device 🤭Bob "hot rod" Rohr
I drilled 1-1/4” holes. Hopefully this is ok.hot_rod said:Sure, anywhere tube can run is a good use of pipe insulation Typically 1-3/8” holes are drilled. That allows plastic isolators or thin walled pipe insulation to be used Interesting use of a Studor air admittance device🤭
The Studor air admittance device is being used as an added percaution/assistance to the vent that leads to the roof. The drain vent stretch is very long but is slopped correctly.
1-3/8" is typically the plumbers go to size drill, for some reason. Many of the insulators require that size, especially the drive in type.
When we worked with TJI type joists, an 1-1/2" hole could be drilled anywhere in the web.
So the 1-3/8" was a safe drill to use in those.
As long as the tube is free to move, not tight against the tube so the tube could expand, you should be fine.
.Bob "hot rod" Rohr
Living the hydronic dream1