I need a Gas Meter Clocking Chart PDF to reproduce.
I'm looking for a good quality, high-ish resolution gas meter clocking chart PDF or image that I can reproduce and print cleanly to hand out to my students. Everything I see with a quick search online is too small and cruddy looking. Any help is appreciated.
Best to all,
JohnNY
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
Have you tried contacting PSE&G?JohnNY said:Good morning all,
Best to all,
JohnNY0 -
I still believe the best thing to do is teach them to memorize the math, then they'll always have it with them (in their head).
3600/seconds to pass 1 Cu Ft=CFH. now multiply that by the current BTU content of 1 Cu Ft.
if medium pressure gas through the gas meter ( 2 PSI in our area) 3600/seconds to pass 1 CuFt x 1.12= CFH.
build a man a fire and he stays warm for the night, set a man on fire he stays warm for the rest of his life!2 -
I don't get it. So, if a 2 foot dial takes 34 seconds to make one full rotation, how do you apply your math?ch4man said:I still believe the best thing to do is teach them to memorize the math, then they'll always have it with them (in their head).
build a man a fire and he stays warm for the night, set a man on fire he stays warm for the rest of his life!Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Classes0 -
JohnNY said:
Good morning all,
Best to all,
JohnNY
It's actually a shame no one makes a phone app to do this.
There's the PDF! Nice link, Ed! I put that math into a google spreadsheet but it's been a few years and I don't remember the math either just like ch4man said
https://www.honeywellgasdepot.com/media/catalog/category/specifications/EAM-OM0001.pdf
Here is a spread sheet I just made up for that calculation.
Now you can google Clock Gas Meter Chart and maybe this will show up.
2 CF dial / 34 sec. x 3600 = total 211.76. CFEdward Young Retired
use 7200 instead of 3600. there are 3600 seconds in one hour, so there has to be 7200 seconds in two hours. in your example one could substitute 17 seconds instead and still keep the 3600 in the formula.JohnNY said:
this entire trade requires math, at all levels. sure we can't remember everything so cheat sheets are nice but this one I found easy to remember0 -
thanks Ed, I spout off 1.12 when doing a conversion for 2PSI gas but that reflects the local elevation above sea level where I'm at. one would need to adjust the math for their one location. or carry many cheatsheets............EdTheHeaterMan said:0 -
Here's an actual calculator that will adjust for elevation. Check it out and let me know if it works.
I added it my other Excel SS of calculations if you want the whole shebang.There was an error rendering this rich post.
See attached files. I wrote these for my guys. The worksheet correction factor is based on my local pressures.Never stop learning.0
Excellent! Thank you.Mike_Sheppard said:See attached files. I wrote these for my guys. The worksheet correction factor is based on my local pressures.
Classes0
- 117 Geothermal
