The icicle
Henry
Member Posts: 998
Reducing the outlet to 1.5 from 2, increases the exit velocity. It is supposed to prevent this. I did work in the lab around 1997 for Lennox. This was the solution and in their I & O manuals the following year. The large rectangular piece is the outlet from my Jenn-air stove. The small outlet is from my HTP modulating, condensing hot water tank.1
The table looks like someone peeled a giant oreo.MikeAmann said:Look at the cool snow pattern on the table and chair.
2 -
FYI it s PVC sch 40. There is nothing in the certified instruction manual or code that says one needs long sweep 90s. I have a steel beam going across to the left of the gas pipe. I had to be creative to bring it to the fire pit. BTW there is a sleeve going through and it is sealed. It will be covered with open ended aluminum covering as per our code in the spring. The St Lawrence valley has strange humidity and we get a lot of very cold and humid days and nights. There were a number of manufacturers that sent equipment to be tested in our environment.1
That is one beautiful dog ice sculpture"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
LOL! I noticed our concentric vent had a short ice "goatee"
To rid yourself of the ice-capade, build an enclosure around the offedng pipe work. Do not forget to heat the space so ice will not form in the enclosure,
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
Isn't it supposed to be pitched to drain back to the appliance?0
Yeah, but there is still going to be some water in the flue exhaust. Maybe enough to freeze like that? I get some frozen condensate on my exhaust plate - meanwhile my condensate drain line is a constant drippage of water.mattmia2 said:Isn't it supposed to be pitched to drain back to the appliance?
John0 -
On the same note, this is not my job, I know it has issues, this is a cool ice formation on a random house that I will not be fixing.ChrisJ said:I like how Henry just posted a "side effect" of very cold temperatures and everyone's trying to fix a problem he doesn't have.
Albert Einstein2 -
has that installation changed the maximum expected snow line and now does not meet code?0
I see a modified concentric with an uninsulated extension as well as no bird screen. It's probably too close to the window and the meter as well.
I honestly was just admiring the art. Just like the dog with the long skinny neck @Henry posted, I can't imagine how those 2 boilers produced such perfect molar teeth."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Perhaps pitched the wrong way and cond water not returning to inside unit for draining?
Never seen the screen before around the pipes near the house. Can anyone elaborate?0 -
I think they pulled apart a concentric and extended it.
Once again, we are here to view the ice artwork, not to fix someone else's system"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Bird screen is not required. There are several manufacturers of condensing equipment that will permit uninsulated exposed vents including HTP and Lennox among others. As can be seen in this picture, the exhaust gases are accelerated away from the structure. The short 1.5 inch reduction acts as a spray nozzle of a garden hose. This prevents damage to the siding.0 -
Yes but is it approved by the manufacturer?HVACNUT said:Henry said:The short 1.5 inch reduction acts as a spray nozzle of a garden hose. This prevents damage to the siding.
I personally have never seen the exhaust reduced.
Some people just can't appreciate fine art!"If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
EBEBRATT-Ed said:Reducing the exhaust pipe size was a trick by Lennox on the old pulse furnaces as I recall0
Wouldn't the unit alarm out if the exhaust was too restrictive?
Yep,their exhaust termination kits included a 2"x11/2" pvc reducer along with a short piece of 11/2" pipe.EBEBRATT-Ed said:Reducing the exhaust pipe size was a trick by Lennox on the old pulse furnaces as I recall
1
- 87K THE MAIN WALL
- 116 Chimneys & Flues
- 109 Geothermal
- 985 Plumbing
- 389 Solar
