Nest Learning Thermostat 3rd Generation
nyteacher78
Member Posts: 20
Hello! I hope someone can provide me with some guidance. I have a heating and a cooling system hooked up to my nest 3rd gen learning thermostat.
I have Y1, G and Rc and then W1 and Rh. Thermostat worked fine for about three years.
Now Nest support tells me I need a C wire.
Now Nest support tells me I need a C wire.
My question is, if I simply move the G wire to the C connection on the thermostat, can that G wire act as the C wire?
best
best
0
Comments
-
To add to this I have a Red, White and green coming from our AC panel in the attic and Red and White from the furnace.0
-
No. You will most likely need to run a new multi conductor cable from one unit or the other.0
-
At the air handler the green connects to a green the red to a red and the white to the white that goes outside.
0 -
The red in the air handler is the 24 volt power, the green is the fan call, the white coming from the stat is the cooling call, & the white coming out of the air handler (& connected to the wire going out to the outdoor unit) is the common that you need to extend to the Nest.0
-
Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.1 -
Thank you…yea Rh and W go to the boiler down stairs.HVACNUT said:
Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.I’m not following you though. Do I run a new wire from the the air handler blue dot to the whites grey dot. Then connect the green from the thermostat to the grey dot?0 -
Connect Green wire to C on the thermostat and Blue dot splice.nyteacher78 said:
Thank you…yea Rh and W go to the boiler down stairs.HVACNUT said:
Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.I’m not following you though. Do I run a new wire from the the air handler blue dot to the whites grey dot. Then connect the green from the thermostat to the grey dot?
Connect Green from air handler to grey dot splice.0 -
I think that picture is the air handler & the 3 conductor with the green wrapped around is the wire going out to the condenser. @nyteacher78, is that not the case?
If so, it's not going to where we need it.
0 -
Do a search of Issues with the NEST............Then get a different t-stat.0
-
Hi sorry I was away for thanksgiving I’m heading up into attic to take a look I’ll post a new pictureratio said:I think that picture is the air handler & the 3 conductor with the green wrapped around is the wire going out to the condenser. @nyteacher78, is that not the case?If so, it's not going to where we need it.
0 -
The the connection with the green wire wrapped around it goes outside to the condenserHVACNUT said:
Connect Green wire to C on the thermostat and Blue dot splice.nyteacher78 said:
Thank you…yea Rh and W go to the boiler down stairs.HVACNUT said:
Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.I’m not following you though. Do I run a new wire from the the air handler blue dot to the whites grey dot. Then connect the green from the thermostat to the grey dot?
Connect Green from air handler to grey dot splice.
The red from the condenser connection goes to this
The blue goes to that as well
0 -
NEST
****
! ! !0 -
Harsh. I have three others and this is the only one I’ve ever had an issue with. Their support is terrible even though this one is just two years old it’s out of warranty and they will not replace the battery. I actually bought an after market battery and replaced it but that do not help. Last ditch effort so I don’t have to drop money is to use a c wire to power it…pecmsg said:NEST
****
! ! !0 -
NEST is our biggest issue when it comes to modern equipment.Your happy fine!0
-
So I followed this exactly. From the T-stat the red goes to red at air handler, white goes to the white from the condenser and the green from the air handler.HVACNUT said:
Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.T-stat green goes to connection with the red from condenser and the white from the drip pan pump which goes to that little pump then to the blue at the air handler…..
nest recognizes the c wire….tested ac and the fan does kick on as expected and condenser…heat works as well…
did I do this right? Don’t want to damage anything…thank you!0 -
Just get a different stat!0
-
nyteacher78 said:HVACNUT said:
Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.So I followed this exactly. From the T-stat the red goes to red at air handler, white goes to the white from the condenser and the green from the air handler.
T-stat green goes to connection with the red from condenser and the white from the drip pan pump which goes to that little pump then to the blue at the air handler…..
nest recognizes the c wire….tested ac and the fan does kick on as expected and condenser…heat works as well…
did I do this right? Don’t want to damage anything…thank you!
If it works and doesn't let smoke out of something, leave it alone. Nest wiring in more complex systems borders on a black art...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 117 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements