Nest Learning Thermostat 3rd Generation
nyteacher78
Member Posts: 20
Hello! I hope someone can provide me with some guidance. I have a heating and a cooling system hooked up to my nest 3rd gen learning thermostat.
I have Y1, G and Rc and then W1 and Rh. Thermostat worked fine for about three years.
Now Nest support tells me I need a C wire.
Now Nest support tells me I need a C wire.
My question is, if I simply move the G wire to the C connection on the thermostat, can that G wire act as the C wire?
best
best
0
Comments
-
To add to this I have a Red, White and green coming from our AC panel in the attic and Red and White from the furnace.0
-
No. You will most likely need to run a new multi conductor cable from one unit or the other.0
-
At the air handler the green connects to a green the red to a red and the white to the white that goes outside.0
-
The red in the air handler is the 24 volt power, the green is the fan call, the white coming from the stat is the cooling call, & the white coming out of the air handler (& connected to the wire going out to the outdoor unit) is the common that you need to extend to the Nest.0
-
Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.1 -
HVACNUT said:Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.I’m not following you though. Do I run a new wire from the the air handler blue dot to the whites grey dot. Then connect the green from the thermostat to the grey dot?0 -
nyteacher78 said:HVACNUT said:Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.I’m not following you though. Do I run a new wire from the the air handler blue dot to the whites grey dot. Then connect the green from the thermostat to the grey dot?
Connect Green from air handler to grey dot splice.0 -
I think that picture is the air handler & the 3 conductor with the green wrapped around is the wire going out to the condenser. @nyteacher78, is that not the case?
If so, it's not going to where we need it.
0 -
Do a search of Issues with the NEST............Then get a different t-stat.0
-
ratio said:I think that picture is the air handler & the 3 conductor with the green wrapped around is the wire going out to the condenser. @nyteacher78, is that not the case?
If so, it's not going to where we need it.
0 -
HVACNUT said:nyteacher78 said:HVACNUT said:Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.I’m not following you though. Do I run a new wire from the the air handler blue dot to the whites grey dot. Then connect the green from the thermostat to the grey dot?
Connect Green from air handler to grey dot splice.The red from the condenser connection goes to thisThe blue goes to that as well0 -
NEST
****
! ! !0 -
pecmsg said:NEST
****
! ! !0 -
NEST is our biggest issue when it comes to modern equipment.Your happy fine!0
-
HVACNUT said:Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.T-stat green goes to connection with the red from condenser and the white from the drip pan pump which goes to that little pump then to the blue at the air handler…..
nest recognizes the c wire….tested ac and the fan does kick on as expected and condenser…heat works as well…
did I do this right? Don’t want to damage anything…thank you!0 -
Just get a different stat!0
-
nyteacher78 said:HVACNUT said:Assuming Rh and W go to a completely seperate appliance (you say furnace. I'm guessing boiler), then you can substitute the Green wire and connect it to Common on the thermostat and air handler.
Common on the air handler is the Blue dot.
Splice Green from the air handler to the whites (Grey dot, which should be Y at the thermostat) to energize the fan relay on a cooling call.
The drawback of course is you won't be able to run the fan only.So I followed this exactly. From the T-stat the red goes to red at air handler, white goes to the white from the condenser and the green from the air handler.
T-stat green goes to connection with the red from condenser and the white from the drip pan pump which goes to that little pump then to the blue at the air handler…..
nest recognizes the c wire….tested ac and the fan does kick on as expected and condenser…heat works as well…
did I do this right? Don’t want to damage anything…thank you!
If it works and doesn't let smoke out of something, leave it alone. Nest wiring in more complex systems borders on a black art...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements