Radiant ceiling water temp question...
jad3675
Member Posts: 127
My house had a CI boiler that struggled to send 120F water through the single zone radiant system - embedded 3/8 copper in the scratch plaster of the ceilings.
The CI boiler is no longer in the picture, and the house has been re-zoned at each floor.
The new mod-con boiler (TT Instinct) has ODR and a dozen or so pre-programmed curves to choose from; I'm wondering what is the best target temp for radiant ceilings?
Is it trial and error? I'm thinking that too high of a water temp would lead to cracked plaster and too low would lead to a cold wife.
FWIW, the 120F water temp of the CI boiler was...ok. It could keep the house at 67 or so, but left a lot to be desired on the gas consumption front.
You've pretty well tagged it -- too high and your plaster will crack -- and your wife will be upset. Too low and your wife will be cold -- and be upset.
You are going to have to experiment -- but you've got a good starting point. You know what worked, at least after a fashion, with the old boiler, and I'd be inclined to start right there.Br. Jamie, osb
Unless you have a huge heat load, that ceiling should not need to run much above 83-85° surface temperature. 120F supply from the boiler should be plenty to get that ceiling warm.
One nice thing with ceiling radiant is you can run them a bit warmer then floors, as you typically do not stand on ceilings.
90F ceiling in a 70° room would get you around 40 BTU/ sq ft output.
The very best first step would be to do heat load calculation, determine exactly what the system needs to accomplish.Bob "hot rod" Rohr
Living the hydronic dream1 -
Are you planning to run outdoor reset?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I'm glad HR bumped this thread, I have a little bit of data now!Zman said:Are you planning to run outdoor reset?
It is running ODR. I have the current curve set to a max of 140, with the warm weather cutoff set to 68. Boiler is also de-rated to 55%.
On Oct 27th I had it running during the morning (both 1st and 2nd floor zones) - outdoor temp was upper 30's, the boiler setpoint was called at 112F. It ran for a bit over 3 hrs with an avg firing rate of 16%. Avg supply temp was 105F and avg return temp was 94F. A thermal camera on the living room ceiling showed the ceiling @87F in the coil areas.
John0 -
Depends on ceiling height. Tall bald guys can feel too warm.0
Even though it is mostly radiant transfer, radiant ceilings do tend to stratify a bit, It will generally be warmer at the ceiling, which does limit the output some. If 87F covers the load on a 30F day, you may not need SWT over 100-115F at design dayBob "hot rod" Rohr
hot_rod said:Even though it is mostly radiant transfer, radiant ceilings do tend to stratify a bit, It will generally be warmer at the ceiling, which does limit the output some. If 87F covers the load on a 30F day, you may not need SWT over 100-115F at design day
Cincinnati is due for some low temps these week - I may knock the ODR curve down to 120 and see how it does.0 -
If you are running a conventional cast iron boiler it needs to run hot enough to avoid condensing. Typically 150 or so to assure 130 return
most often the boiler runs 150or more and a mix valve supplies the low temperature to the radiantBob "hot rod" Rohr
hot_rod said:If you are running a conventional cast iron boiler it needs to run hot enough to avoid condensing. Typically 150 or so to assure 130 return