Radiant ceiling water temp question...
jad3675
Member Posts: 127
My house had a CI boiler that struggled to send 120F water through the single zone radiant system - embedded 3/8 copper in the scratch plaster of the ceilings.
The CI boiler is no longer in the picture, and the house has been re-zoned at each floor.
The new mod-con boiler (TT Instinct) has ODR and a dozen or so pre-programmed curves to choose from; I'm wondering what is the best target temp for radiant ceilings?
Is it trial and error? I'm thinking that too high of a water temp would lead to cracked plaster and too low would lead to a cold wife.
FWIW, the 120F water temp of the CI boiler was...ok. It could keep the house at 67 or so, but left a lot to be desired on the gas consumption front.
The CI boiler is no longer in the picture, and the house has been re-zoned at each floor.
The new mod-con boiler (TT Instinct) has ODR and a dozen or so pre-programmed curves to choose from; I'm wondering what is the best target temp for radiant ceilings?
Is it trial and error? I'm thinking that too high of a water temp would lead to cracked plaster and too low would lead to a cold wife.
FWIW, the 120F water temp of the CI boiler was...ok. It could keep the house at 67 or so, but left a lot to be desired on the gas consumption front.
0
Comments
-
You've pretty well tagged it -- too high and your plaster will crack -- and your wife will be upset. Too low and your wife will be cold -- and be upset.
You are going to have to experiment -- but you've got a good starting point. You know what worked, at least after a fashion, with the old boiler, and I'd be inclined to start right there.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Unless you have a huge heat load, that ceiling should not need to run much above 83-85° surface temperature. 120F supply from the boiler should be plenty to get that ceiling warm.
One nice thing with ceiling radiant is you can run them a bit warmer then floors, as you typically do not stand on ceilings.
90F ceiling in a 70° room would get you around 40 BTU/ sq ft output.
The very best first step would be to do heat load calculation, determine exactly what the system needs to accomplish.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Are you planning to run outdoor reset?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I'm glad HR bumped this thread, I have a little bit of data now!Zman said:Are you planning to run outdoor reset?
It is running ODR. I have the current curve set to a max of 140, with the warm weather cutoff set to 68. Boiler is also de-rated to 55%.
On Oct 27th I had it running during the morning (both 1st and 2nd floor zones) - outdoor temp was upper 30's, the boiler setpoint was called at 112F. It ran for a bit over 3 hrs with an avg firing rate of 16%. Avg supply temp was 105F and avg return temp was 94F. A thermal camera on the living room ceiling showed the ceiling @87F in the coil areas.
John0 -
Depends on ceiling height. Tall bald guys can feel too warm.0
-
Even though it is mostly radiant transfer, radiant ceilings do tend to stratify a bit, It will generally be warmer at the ceiling, which does limit the output some. If 87F covers the load on a 30F day, you may not need SWT over 100-115F at design dayBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
hot_rod said:Even though it is mostly radiant transfer, radiant ceilings do tend to stratify a bit, It will generally be warmer at the ceiling, which does limit the output some. If 87F covers the load on a 30F day, you may not need SWT over 100-115F at design day
Cincinnati is due for some low temps these week - I may knock the ODR curve down to 120 and see how it does.0 -
If you are running a conventional cast iron boiler it needs to run hot enough to avoid condensing. Typically 150 or so to assure 130 return
most often the boiler runs 150or more and a mix valve supplies the low temperature to the radiantBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:If you are running a conventional cast iron boiler it needs to run hot enough to avoid condensing. Typically 150 or so to assure 130 return
most often the boiler runs 150or more and a mix valve supplies the low temperature to the radiant
I replaced all that with as zoned modcon (Caleffi controls, of course) that will hopefully be a bit more efficient.1 -
One thing to remember too, if possible, make sure that the ceiling/attic space above is adequately insulated to drive the heat into the conditioned space.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements