PH Level in steam boiler
normal PH level. Also looking for help in adjustment of this level. Thanks!!
Consensus seems to be around 8 is good; 7 to 9 is certainly reasonable. Higher seems to give foaming, and lower may result in more corrosion (may not, too).
There are several products which one can add -- in small quantities -- to buffer the pH in a reasonable range.
As a general sort of rule, the feedwater pH is what determines the pH level, assuming one isn't adding treatment. There isn't much happening inside a boiler which will alter pH.Br. Jamie, osb
This article may help: https://heatinghelp.com/systems-help-center/the-importance-of-ph-in-steam-boiler-water/
President
HeatingHelp.com1 -
I like to go higher than Jamie said. 10-11. You can even go way higher without foaming in a clean boiler, but there's probably little benefit.
If you twist my arm I'll tell you that the ph isn't nearly as important as making sure you don't have any steam or water leaks in your system.NJ Steam Homeowner.
I'd rather leaks with a pH of 9+ over no leaks and a pH of 4.............ethicalpaul said:I like to go higher than Jamie said. 10-11. You can even go way higher without foaming in a clean boiler, but there's probably little benefit.
But that's me.
I also feel 7 is too low and 8 is iffy. I like 9, 10 is fine.
In my experience, very high pH is corrosive to bronze pump parts.
In my days as a service tech at Nash Engineering, anytime we had a vacuum pump or gas compressor with a high pH carryover, ALL IRON construction was specified. This meant no copper alloy to be present.
I have also seen this corroded bronze parts in condensate and vacuum pumps used for steam heating systems. Again, this was traced to condensate pH being too high.
Never was able to determine what the pH limit was, but I like to say maybe 9 or so.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
I believe it also etches glass.Pumpguy said:In my experience, very high pH is corrosive to bronze pump parts.
But my opinion has been I'd rather replace the gauge glass than the boiler.
So far.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
I guess we don't know if this is a residential application, but there's nothing a typical home boiler situation can do about the PH of condensate...how high could condensate be anyway?Pumpguy said:In my experience, very high pH is corrosive to bronze pump parts.
Never was able to determine what the pH limit was, but I like to say maybe 9 or so.NJ Steam Homeowner.
I honestly thought condensate, in a perfect world would have a low pH, of 4 or 5.ethicalpaul said:
I can't tell you how many times I have seen cast iron pump castings turned to graphite paste due to low pH.
Sometimes this graphite layer can be 1/8" or more deep .
The acidic condensate leaches out the iron, leaving the free carbon behind.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
But you've also seen condensate with a high PH?Pumpguy said:I can't tell you how many times I have seen cast iron pump castings turned to graphite paste due to low pH.
If it has a high pH it's probably due to how clean the condensate is. It likely doesn't take much to buffer the solutionChrisJ said:
The acidic condensate leaches out the iron, leaving the free carbon behind.You can have it good, fast or cheap. Pick two0 -
Me: In my time I found ph levels at 9 & 10 worked best in boilers.
Some jobs where ph levels reached above 10 foaming occurred.
Other chems to add were amines to prevent oxydation.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
Yes, In one memorable case at a high school, the condensate had a yellowish tinge to it, irritated my hands, and had a slippery feel.ChrisJ said:
The iron pump parts were fine but the bronze parts were all shot.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
