PH Level in steam boiler
normal PH level. Also looking for help in adjustment of this level. Thanks!!
Comments
-
Consensus seems to be around 8 is good; 7 to 9 is certainly reasonable. Higher seems to give foaming, and lower may result in more corrosion (may not, too).
There are several products which one can add -- in small quantities -- to buffer the pH in a reasonable range.
As a general sort of rule, the feedwater pH is what determines the pH level, assuming one isn't adding treatment. There isn't much happening inside a boiler which will alter pH.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
This article may help: https://heatinghelp.com/systems-help-center/the-importance-of-ph-in-steam-boiler-water/
President
HeatingHelp.com1 -
I like to go higher than Jamie said. 10-11. You can even go way higher without foaming in a clean boiler, but there's probably little benefit.
If you twist my arm I'll tell you that the ph isn't nearly as important as making sure you don't have any steam or water leaks in your system.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I'd rather leaks with a pH of 9+ over no leaks and a pH of 4.............ethicalpaul said:I like to go higher than Jamie said. 10-11. You can even go way higher without foaming in a clean boiler, but there's probably little benefit.
If you twist my arm I'll tell you that the ph isn't nearly as important as making sure you don't have any steam or water leaks in your system.
But that's me.
I also feel 7 is too low and 8 is iffy. I like 9, 10 is fine.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
In my experience, very high pH is corrosive to bronze pump parts.
In my days as a service tech at Nash Engineering, anytime we had a vacuum pump or gas compressor with a high pH carryover, ALL IRON construction was specified. This meant no copper alloy to be present.
I have also seen this corroded bronze parts in condensate and vacuum pumps used for steam heating systems. Again, this was traced to condensate pH being too high.
Never was able to determine what the pH limit was, but I like to say maybe 9 or so.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
I believe it also etches glass.Pumpguy said:In my experience, very high pH is corrosive to bronze pump parts.
In my days as a service tech at Nash Engineering, anytime we had a vacuum pump or gas compressor with a high pH carryover, ALL IRON construction was specified. This meant no copper alloy to be present.
I have also seen this corroded bronze parts in condensate and vacuum pumps used for steam heating systems. Again, this was traced to condensate pH being too high.
Never was able to determine what the pH limit was, but I like to say maybe 9 or so.
But my opinion has been I'd rather replace the gauge glass than the boiler.
So far.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
I guess we don't know if this is a residential application, but there's nothing a typical home boiler situation can do about the PH of condensate...how high could condensate be anyway?Pumpguy said:In my experience, very high pH is corrosive to bronze pump parts.
In my days as a service tech at Nash Engineering, anytime we had a vacuum pump or gas compressor with a high pH carryover, ALL IRON construction was specified. This meant no copper alloy to be present.
I have also seen this corroded bronze parts in condensate and vacuum pumps used for steam heating systems. Again, this was traced to condensate pH being too high.
Never was able to determine what the pH limit was, but I like to say maybe 9 or so.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I honestly thought condensate, in a perfect world would have a low pH, of 4 or 5.ethicalpaul said:
I guess we don't know if this is a residential application, but there's nothing a typical home boiler situation can do about the PH of condensate...how high could condensate be anyway?Pumpguy said:In my experience, very high pH is corrosive to bronze pump parts.
In my days as a service tech at Nash Engineering, anytime we had a vacuum pump or gas compressor with a high pH carryover, ALL IRON construction was specified. This meant no copper alloy to be present.
I have also seen this corroded bronze parts in condensate and vacuum pumps used for steam heating systems. Again, this was traced to condensate pH being too high.
Never was able to determine what the pH limit was, but I like to say maybe 9 or so.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I can't tell you how many times I have seen cast iron pump castings turned to graphite paste due to low pH.
Sometimes this graphite layer can be 1/8" or more deep .
The acidic condensate leaches out the iron, leaving the free carbon behind.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
But you've also seen condensate with a high PH?Pumpguy said:I can't tell you how many times I have seen cast iron pump castings turned to graphite paste due to low pH.
Sometimes this graphite layer can be 1/8" or more deep .
The acidic condensate leaches out the iron, leaving the free carbon behind.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
If it has a high pH it's probably due to how clean the condensate is. It likely doesn't take much to buffer the solutionChrisJ said:
But you've also seen condensate with a high PH?Pumpguy said:I can't tell you how many times I have seen cast iron pump castings turned to graphite paste due to low pH.
Sometimes this graphite layer can be 1/8" or more deep .
The acidic condensate leaches out the iron, leaving the free carbon behind.You can have it good, fast or cheap. Pick two0 -
Me: In my time I found ph levels at 9 & 10 worked best in boilers.
Some jobs where ph levels reached above 10 foaming occurred.
Other chems to add were amines to prevent oxydation.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
Yes, In one memorable case at a high school, the condensate had a yellowish tinge to it, irritated my hands, and had a slippery feel.ChrisJ said:
But you've also seen condensate with a high PH?Pumpguy said:I can't tell you how many times I have seen cast iron pump castings turned to graphite paste due to low pH.
Sometimes this graphite layer can be 1/8" or more deep .
The acidic condensate leaches out the iron, leaving the free carbon behind.
The iron pump parts were fine but the bronze parts were all shot.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements