Steam problem
Snowmelt
Snowmelt Member Posts: 1,428
edited March 2021 in THE MAIN WALL
I went to a job today. Not the best near boiler piping but the rads weren’t getting hot.
Things I observed was the boiler was short cycling, customer replaced pressure trol but didn’t clean out pig tail. I looked for bows or sagging pipe were water would be trapped, I didn’t see any. Then there where rads that I took the air bleeder off and the rads heated up in 3 minutes. I’m thinking pig tail clogged up but not sure? Is there anything else I should be looking for?
  • Snowmelt
    Jamie Hall Member Posts: 26,220
    Air bleeder? By which do you mean a vent on a radiator? If so, could the vent be bad?
    Pictures didn't post...
  • Snowmelt
    Vents I don’t think are bad, home owner replaced them with adjustable ones. It old him as a suggestion get new ones with the biggest hole. But at this point you may be right.
  • Snowmelt
    I’ll try pictures again
    Seen a lot worse near boiler piping...
    If radiators on a one pipe steam system aren't heating, either steam can't get to them (major sag in a pipe -- but you might also get a water hammer) or a closed valve -- or a vent which isn't venting. I'm thinking vents for starters...
    Alan Welchethicalpaul
  • Alan Welch
    Alan Welch Member Posts: 270
    Is it short cycling on pressure or water level..  If the gage is accurate you have way to much pressure for the vents to open.
    Steamhead Member Posts: 17,918
    This. Check that the pressuretrol is working, and that the wiring hasn't been altered- make sure the control actually stops the burners.
    Consulting
  • Snowmelt
    It’s shutting off on pressure, the gauge is broke. I have a a feeling it’s the vents. Also could the pig tail be plugged,
    The owner said one day he had no heat, and he swapped out the pressure trol on his own. I also noticed the pressure relieve valve went off and relieved some water
  • neilc
    neilc Member Posts: 3,032
    pressure relief went off while you were there?
    check and clean that pigtail,
    and get a working gage,
    known to beat dead horses
  • neilc
    main venting,
    what do you have for main venting?
  • neilc
    and if you went high pressure,
    rad, and main vents could be damaged closed
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,577
    The home owner may have separated the lower diaphragm chamber from the upper switch body in removing/replacing the pressuretrol, thus separating the linkage, resulting in no upper limit.—NBC
  • ratio
    ratio Member Posts: 4,075
    Lots of things to check, but if the relief valve relieved, that's an over pressure event. After you check out the pressuretrol & piggytail, the vents may have been damaged—I don't think they can take 30 lbs pressure.
    ethicalpaul Member Posts: 7,786
    I don't think that was good vent advice.
    You should be able to see the pressuretrol shut down the boiler on pressure while you are there--it seems like the boiler is building plenty of pressure to show you that. And personally I wouldn't leave until it does so, else red-tag the boiler (if I'm using the correct term)
    It's this information that confuses me:
    If the pressuretrol is shutting it down on pressure, then how did the PRV go off? It's not like a water PRV I think. If it goes off, it will vent all the steam and although I've never seen it in person, it should be a pretty shocking event because once the pressure gets high enough to blow it, then a lot more steam is going to get generated and released as the pressure is relieved.
  • Alan Welch
    Steam should relief at 15 lbs.
    Deltat210
    As a final safety, yes, but in operation, it should never get to that point (because there should be an operational pressuretrol.