I went to a job today. Not the best near boiler piping but the rads weren’t getting hot.
Things I observed was the boiler was short cycling, customer replaced pressure trol but didn’t clean out pig tail. I looked for bows or sagging pipe were water would be trapped, I didn’t see any. Then there where rads that I took the air bleeder off and the rads heated up in 3 minutes. I’m thinking pig tail clogged up but not sure? Is there anything else I should be looking for?

Comments

  • Snowmelt
    Snowmelt Member Posts: 1,425
    Picture
  • Jamie Hall
    Jamie Hall Member Posts: 24,674
    Air bleeder? By which do you mean a vent on a radiator? If so, could the vent be bad?

    Pictures didn't post...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • Snowmelt
    Snowmelt Member Posts: 1,425
    Vents I don’t think are bad, home owner replaced them with adjustable ones. It old him as a suggestion get new ones with the biggest hole. But at this point you may be right.
    ethicalpaul
  • Snowmelt
    Snowmelt Member Posts: 1,425
    I’ll try pictures again



  • Jamie Hall
    Jamie Hall Member Posts: 24,674
    Seen a lot worse near boiler piping...

    If radiators on a one pipe steam system aren't heating, either steam can't get to them (major sag in a pipe -- but you might also get a water hammer) or a closed valve -- or a vent which isn't venting. I'm thinking vents for starters...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Alan Welchethicalpaul
  • Alan Welch
    Alan Welch Member Posts: 270
    Is it short cycling on pressure or water level..  If the gage is accurate you have way to much pressure for the vents to open.
  • Steamhead
    Steamhead Member Posts: 17,357

    Is it short cycling on pressure or water level..  If the gage is accurate you have way to much pressure for the vents to open.

    This. Check that the pressuretrol is working, and that the wiring hasn't been altered- make sure the control actually stops the burners.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    ethicalpaul
  • Snowmelt
    Snowmelt Member Posts: 1,425
    It’s shutting off on pressure, the gauge is broke. I have a a feeling it’s the vents. Also could the pig tail be plugged,
    The owner said one day he had no heat, and he swapped out the pressure trol on his own. I also noticed the pressure relieve valve went off and relieved some water
  • neilc
    neilc Member Posts: 2,814
    pressure relief went off while you were there?
    check and clean that pigtail,
    and get a working gage,
    known to beat dead horses
    ethicalpaul
  • neilc
    neilc Member Posts: 2,814
    main venting,
    what do you have for main venting?
    known to beat dead horses
  • neilc
    neilc Member Posts: 2,814
    and if you went high pressure,
    rad, and main vents could be damaged closed
    known to beat dead horses
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    The home owner may have separated the lower diaphragm chamber from the upper switch body in removing/replacing the pressuretrol, thus separating the linkage, resulting in no upper limit.—NBC
    ethicalpaul
  • ratio
    ratio Member Posts: 3,777
    Lots of things to check, but if the relief valve relieved, that's an over pressure event. After you check out the pressuretrol & piggytail, the vents may have been damaged—I don't think they can take 30 lbs pressure.
  • ethicalpaul
    ethicalpaul Member Posts: 6,513
    Snowmelt said:

    Vents I don’t think are bad, home owner replaced them with adjustable ones. It old him as a suggestion get new ones with the biggest hole. But at this point you may be right.

    I don't think that was good vent advice.

    You should be able to see the pressuretrol shut down the boiler on pressure while you are there--it seems like the boiler is building plenty of pressure to show you that. And personally I wouldn't leave until it does so, else red-tag the boiler (if I'm using the correct term)

    It's this information that confuses me:
    Snowmelt said:

    It’s shutting off on pressure, the gauge is broke. I have a a feeling it’s the vents. Also could the pig tail be plugged,
    The owner said one day he had no heat, and he swapped out the pressure trol on his own. I also noticed the pressure relieve valve went off and relieved some water

    If the pressuretrol is shutting it down on pressure, then how did the PRV go off? It's not like a water PRV I think. If it goes off, it will vent all the steam and although I've never seen it in person, it should be a pretty shocking event because once the pressure gets high enough to blow it, then a lot more steam is going to get generated and released as the pressure is relieved.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Alan Welch
    Alan Welch Member Posts: 270
    Steam should relief at 15 lbs.
    Deltat210
  • ethicalpaul
    ethicalpaul Member Posts: 6,513
    As a final safety, yes, but in operation, it should never get to that point (because there should be an operational pressuretrol.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/