Steam problem
Things I observed was the boiler was short cycling, customer replaced pressure trol but didn’t clean out pig tail. I looked for bows or sagging pipe were water would be trapped, I didn’t see any. Then there where rads that I took the air bleeder off and the rads heated up in 3 minutes. I’m thinking pig tail clogged up but not sure? Is there anything else I should be looking for?
I’ll try pictures again
Seen a lot worse near boiler piping...
If radiators on a one pipe steam system aren't heating, either steam can't get to them (major sag in a pipe -- but you might also get a water hammer) or a closed valve -- or a vent which isn't venting. I'm thinking vents for starters...Br. Jamie, osb
Is it short cycling on pressure or water level.. If the gage is accurate you have way to much pressure for the vents to open.0
This. Check that the pressuretrol is working, and that the wiring hasn't been altered- make sure the control actually stops the burners.Alan Welch said:Is it short cycling on pressure or water level.. If the gage is accurate you have way to much pressure for the vents to open.
Consulting1 -
It’s shutting off on pressure, the gauge is broke. I have a a feeling it’s the vents. Also could the pig tail be plugged,
The owner said one day he had no heat, and he swapped out the pressure trol on his own. I also noticed the pressure relieve valve went off and relieved some water0 -
main venting,
what do you have for main venting?known to beat dead horses0 -
and if you went high pressure,
rad, and main vents could be damaged closedknown to beat dead horses0 -
Lots of things to check, but if the relief valve relieved, that's an over pressure event. After you check out the pressuretrol & piggytail, the vents may have been damaged—I don't think they can take 30 lbs pressure.0
I don't think that was good vent advice.Snowmelt said:Vents I don’t think are bad, home owner replaced them with adjustable ones. It old him as a suggestion get new ones with the biggest hole. But at this point you may be right.
You should be able to see the pressuretrol shut down the boiler on pressure while you are there--it seems like the boiler is building plenty of pressure to show you that. And personally I wouldn't leave until it does so, else red-tag the boiler (if I'm using the correct term)
It's this information that confuses me:
If the pressuretrol is shutting it down on pressure, then how did the PRV go off? It's not like a water PRV I think. If it goes off, it will vent all the steam and although I've never seen it in person, it should be a pretty shocking event because once the pressure gets high enough to blow it, then a lot more steam is going to get generated and released as the pressure is relieved.Snowmelt said:It’s shutting off on pressure, the gauge is broke. I have a a feeling it’s the vents. Also could the pig tail be plugged,
The owner said one day he had no heat, and he swapped out the pressure trol on his own. I also noticed the pressure relieve valve went off and relieved some waterNJ Steam Homeowner.
As a final safety, yes, but in operation, it should never get to that point (because there should be an operational pressuretrol.
See my sight glass boiler videos: https://bit.ly/3sZW1el0