Furnace not working
simp50
Member Posts: 2
in Gas Heating
Combustion air inducer runs continuously when power is on and thermostat off on a Lennox 80 uhh furnace
Disconnect the thermostat wires at the furnace and see if the inducer shuts down. If it does t stat or tstat wiring is defective.
If it does shut down the control board or relay taht starts the inducer is probably defective0 -
Inducer fan relay is stuck or shorted closed. Need a new circuit board.0
Does switching the T-stat to "fan on" turn the blower on?0
Thanks guys looks like I’m gonna have to get a control board0
It's probably not the board, but an open limit or flame rollout switch.Bob Boan
Bad ignitor.....0