Furnace not working

Options
simp50
simp50 Member Posts: 2
Combustion air inducer runs continuously when power is on and thermostat off on a Lennox 80 uhh furnace

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,525
    Options
    Disconnect the thermostat wires at the furnace and see if the inducer shuts down. If it does t stat or tstat wiring is defective.

    If it does shut down the control board or relay taht starts the inducer is probably defective
  • ratio
    ratio Member Posts: 3,626
    Options
    Open limit?
    SuperTech
  • SuperTech
    SuperTech Member Posts: 2,164
    Options
    ratio said:
    Open limit?
    That would be my first thought.  Open rollout or limit switch.  The control board on the furnace should indicate a fault code by flashing the LED, that should point you in the direction of the cause of your problem. 
  • HVACNUT
    HVACNUT Member Posts: 5,835
    Options
    Inducer fan relay is stuck or shorted closed. Need a new circuit board. 
  • mikeapolis
    mikeapolis Member Posts: 46
    Options
    Does switching the T-stat to "fan on" turn the blower on?
  • simp50
    simp50 Member Posts: 2
    Options
    Thanks guys looks like I’m gonna have to get a control board 
  • Ironman
    Ironman Member Posts: 7,376
    Options
    It's probably not the board, but an open limit or flame rollout switch.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Seabee5701
    Seabee5701 Member Posts: 19
    Options
    Bad ignitor.....