Boiler issues
Options
Nicoletitti
Posts: 2
I am having issues getting my Utica Mgb series biker to ignite. Replaced the thermocouple today. The pilot stays lit, can hear the thermostat click and then nothing. Any ideas for a very green repair woman with two young kids who is freezing?
0
Comments
-
Do you have just one thermostat? Does your boiler also make hot water for your showers? Oil or gas? Pictures of the boiler might help.0
-
-
-
If a standing pilot with thermocouple, perhaps no ignition control module.
Pictures needed.0 -
If a standing pilot with thermocouple, perhaps no ignition control module.If it's an older model, you may be right.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
If it is a standing pilot, with a Basso control, I have noticed that the sheet metal cover can bind with the button, preventing the button from popping out completely as you light the pilot.
I replace the thermocouple a couple of times before I figured that one out!—NBC0 -
Pictures??0
-
Sorry everyone. Turned out that after replacing the aquastat next the burner is bad. New heater installation tomorrow0