Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Boiler issues
Nicoletitti
Member Posts: 2
I am having issues getting my Utica Mgb series biker to ignite. Replaced the thermocouple today. The pilot stays lit, can hear the thermostat click and then nothing. Any ideas for a very green repair woman with two young kids who is freezing?
0
Comments
-
Do you have just one thermostat? Does your boiler also make hot water for your showers? Oil or gas? Pictures of the boiler might help.0
-
-
-
If a standing pilot with thermocouple, perhaps no ignition control module.
Pictures needed.0 -
If a standing pilot with thermocouple, perhaps no ignition control module.If it's an older model, you may be right.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
If it is a standing pilot, with a Basso control, I have noticed that the sheet metal cover can bind with the button, preventing the button from popping out completely as you light the pilot.
I replace the thermocouple a couple of times before I figured that one out!—NBC0 -
Pictures??0
-
Sorry everyone. Turned out that after replacing the aquastat next the burner is bad. New heater installation tomorrow0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements