Lineset Leaks

Options
245

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,544
    Options
    I just see those systems being a nightmare. Time will tell........it always does
    SuperTech
  • ChrisJ
    ChrisJ Member Posts: 15,706
    Options
    > @EBEBRATT-Ed said:
    > I just see those systems being a nightmare. Time will tell........it always does

    Yeah but hindsight is useless.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    So, like, i need a chiller but i'm too cheap to buy one?
  • hvac
    hvac Member Posts: 6
    Options
    Good Afternoon all, I just wanted to chime in for a minute. My name is Rick and i work with as a manufacturers rep in which we rep a manufacturer that produces the white insulated line sets. I have seen many cases of corroded line sets from every manufacturer (mostly because guys assume that all white line set is the same when in fact there are many different manufacturers). We also had concerns as a rep firm and had some of the leaking pipe tested at a lab to check copper quality as well as the possibility of the insulation reacting with the copper. We were happy to see that the copper quality was far better than the standard for ACR copper as well as no traces of chemical properties of the insulation on the copper. What we did learn is this is no different than what is happening with a/c coils. This is known as formicary corrosion or "ants nest" corrosion, this happens when you have copper, water, oxygen and an organic acid (ex. salt and many other airborne contaminants). Everyone always asks "how come we didn't have this problem before?" and what i try to explain is when we ran line sets with armorflex or kflex insulation and it was exposed to uv the insulation would break down and the moisture on the pipe had no place to get trapped. This was obviously not efficient for the equipment so going to white line set insulation which holds up better to uv when treated properly and better R-value made the system more efficient but if we are in an environment where we have high humidity the pipe will still sweat and the water will now get trapped in the insulation. That and with the addition to salt in the air especially near the shore you make the perfect storm for formicary corrosion and the copper will deteriorate in no time. I am not sure what other manufacturers are doing to combat this but i know we went back to ours and worked very hard to come up with a product that we believe will hold up and stop this from happening. Anyone looking for more info on this topic i would be more than happy to continue the conversation. Send me a message and I'll give you my contact info.
    Rick Koester
    Wales Darby Inc.
    Walesdarby.com
    Rkoester@walesdarby.com
    ratioSolid_Fuel_Man
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    What did you go back and do?

    Is your linset the same thickness as standard tubing from the 1980's?
  • Ironman
    Ironman Member Posts: 7,376
    Options
    @hvac,
    Im having trouble reconciling some things with what you've stated as the cause of the linesets leaking.

    First, you state that the old linesets with Armorflex didn't leak because UV rays broke it down and it couldn't hold moisture. How do you explain the thousands of feet of linesets that I've installed or come across that weren't exposed to UV because they were inside or covered? If what you're stating is correct, then all of them should have been exposed to formicary corrosion just like the white ones because they would have held in moisture.

    Second, you blame salt in the air getting through the white insulation even though water can't get out. Is this to be understood as the same as O2 diffusion with non-barrier PEX? Salt can get in but moisture can't get out? I think you'll find this problem exists in areas far from the coast that don't salt their roads because of their warmer climate.

    I'm not sure what the cause really is, but after 48+ years in this trade I can tell you that it didn't happen until the white Asian linesets came along. I can also tell you that most of the ones that I've used have inferior copper that kinks more easily - even in a bender.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2
  • ChrisJ
    ChrisJ Member Posts: 15,706
    Options
    > @Ironman said:
    > @hvac,
    > Im having trouble reconciling some things with what you've stated as the cause of the linesets leaking.
    >
    > First, you state that the old linesets with Armorflex didn't leak because UV rays broke it down and it couldn't hold moisture. How do you explain the thousands of feet of linesets that I've installed or come across that weren't exposed to UV because they were inside or covered? If what you're stating is correct, then all of them should have been exposed to formicary corrosion just like the white ones because they would have held in moisture.
    >
    > Second, you blame salt in the air getting through the white insulation even though water can't get out. Is this to be understood as the same as O2 diffusion with non-barrier PEX? Salt can get in but moisture can't get out? I think you'll find this problem exists in areas far from the coast that don't salt their roads because of their warmer climate.
    >
    > I'm not sure what the cause really is, but after 48+ years in this trade I can tell you that it didn't happen until the white Asian linesets came along. I can also tell you that most of the ones that I've used have inferior copper that kinks more easily - even in a bender.

    Bob, what do you think of the Mueller Streamline linesets?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Ironman
    Ironman Member Posts: 7,376
    Options
    @ChrisJ,

    I'm not sure if we've used any. We basically have two or three supply houses that we get linesets from and they keep using whichever vendor is the cheapest that month.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • clammy
    clammy Member Posts: 3,112
    Options
    I will say I have used the white coated line sets w no issue as of yet . But I will agree w iron man on that the copper may have a acr rating it does seem thinner walled and some seem to have a temper to it , some contractors I work for insist on using cheaper pre insulated line sets for standard ac split system and I find both the 3/8 and what ever size suction line to be garbage that mostly out of round and not soft extremely easily kinked w Mandabell benders and forget about a spring bender you will never get it on . I’m old school I buy a roll of standard acr and how ever much 1/2 wall armoflex and slide it on glue ends and tape down . I also in all my years have not seen pin holes form from condensate because of vapor leakage due to insulation and acr tubing start to leak but that just me .i also didn’t just get in the business yesterday I ve been doing phvac for close to if not more then 35 years . I love that non rip insulation and I though it was a improvement over armoflex but I guess I was wrong . Like other on my own work I’m back to armoflex and regular rolls of copper I would be embarrassed to try and explain the products failure and the expensive the customer or I would have to foot so I have discontinued specing and using it on my mini split installs but this is just me Peace and good luck clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating
    mattmia2
  • realliveplumber
    realliveplumber Member Posts: 354
    Options
    So I have had over 25 coils in the last 5 or so years leak.

    All were replacement systems in existing houses, most of the houses were 50 years of age or older. The vast majority of the equipment being replaced was 20 years old, or older. Some were 30 years old.

    The Homeowners were the same Homeowners of the coils that lasted 20 to 30 years. It was the same air in the house, the same cleaning products in the house. The same carpets, rugs, furniture. The same off gassing , on and on.

    Except the new coils lasted less than 5 years.

    Therefore, I call baloney about your formicary corrosion excuse, along with all of the other excuses I’ve heard.

    And I’ve heard excuse after excuse.

    The coil manufacturers used and made cheap junk.

    The installer and the contractor are the ones that are suffering and paying for it.

    I can’t wait until it happens to some lawyer, and he decides to file a class action lawsuit.

    At least he’ll get rich off of it, and the coil manufacturers will have to pay.
    ChrisJ
  • Ironman
    Ironman Member Posts: 7,376
    Options

    So I have had over 25 coils in the last 5 or so years leak.

    All were replacement systems in existing houses, most of the houses were 50 years of age or older. The vast majority of the equipment being replaced was 20 years old, or older. Some were 30 years old.

    The Homeowners were the same Homeowners of the coils that lasted 20 to 30 years. It was the same air in the house, the same cleaning products in the house. The same carpets, rugs, furniture. The same off gassing , on and on.

    Except the new coils lasted less than 5 years.

    Therefore, I call baloney about your formicary corrosion excuse, along with all of the other excuses I’ve heard.

    And I’ve heard excuse after excuse.

    The coil manufacturers used and made cheap junk.

    The installer and the contractor are the ones that are suffering and paying for it.

    I can’t wait until it happens to some lawyer, and he decides to file a class action lawsuit.

    At least he’ll get rich off of it, and the coil manufacturers will have to pay.

    IDK our exact numbers, but they're probably similar. We just replaced the coil in a Maytag (Nordyne) AHU that we installed in 2012. This is the 3rd coil. It's straight a/c and the same couple has lived there for 50+ years. The old Carrier R22 coil lasted for over 20 years.

    I personally believe that the manufacturers created the problem by using thinner copper with R410a so they could sell us the solution which they already had in store: aluminum coils.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    I suspect it was just the cost of copper skyrocketing.

    How many of these old coils that were replaced after 30 years were replaced because the coil itself leaked?
  • GW
    GW Member Posts: 4,693
    Options
    The conversation jumped to indoor coil leaking?

    Anyway, if it’s not corrosion, what is it? The braze joints blowing out? No, the thinner copper corroding right?
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • realliveplumber
    realliveplumber Member Posts: 354
    Options
    The OP had mentioned coils in his original post.

    The linesets have the same problem as the coils do.
  • realliveplumber
    realliveplumber Member Posts: 354
    Options
    mattmia2 said:

    I suspect it was just the cost of copper skyrocketing.

    How many of these old coils that were replaced after 30 years were replaced because the coil itself leaked?


    None. Not one. They were replaced as a matter of course, with a furnace replacement.

    The old coils (and linesets) simply did not leak.

    The new ones do.
    mattmia2
  • pecmsg
    pecmsg Member Posts: 4,861
    Options



    I can’t wait until it happens to some lawyer, and he decides to file a class action lawsuit.

    At least he’ll get rich off of it, and the coil manufacturers will have to pay.

    The manufactures are going to shift the blame to the feds for there stricter energy requirements.
  • ChrisJ
    ChrisJ Member Posts: 15,706
    Options
    I'm far from an engineer, but from what I've noticed to gain efficiency you want to reduce head pressure. All of the higher SEER units run much cooler than their older, much smaller outdoor units.

    If that's the case all that's needed is a physically larger condenser and a larger TXV.

    Why do the coils need to be thinner?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    A larger coil uses more tubing so in order to pay the same for the metal, you have to stretch it thinner. There is a little bit of an argument that thinner metal transfers heat better but I suspect that is negligible compared to increasing the overall surface area of the coil.
    ratio
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Options
    I think, like most things, it comes down to price.

    Copper is expensive, so the manufacturers use it as sparingly as possible. They have figured out how thick the copper must be to satisfy their design pressures with a decided margin of error.

    We also have to remember that old R22 ran at lower pressures, and was generally in thicker copper coils etc.

    I also wonder if the quality (purity or alloy) of copper has more to do with it. Most of the copper we are using has likely been recycled at least 5 times now. 30 years ago, it may have been through the furnace 3 times, I dont know.

    Think of the old R12 days, when we could use rubber hoses and clamps for refrigeration!
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • ChrisJ
    ChrisJ Member Posts: 15,706
    Options

    I think, like most things, it comes down to price.



    Copper is expensive, so the manufacturers use it as sparingly as possible. They have figured out how thick the copper must be to satisfy their design pressures with a decided margin of error.



    We also have to remember that old R22 ran at lower pressures, and was generally in thicker copper coils etc.



    I also wonder if the quality (purity or alloy) of copper has more to do with it. Most of the copper we are using has likely been recycled at least 5 times now. 30 years ago, it may have been through the furnace 3 times, I dont know.



    Think of the old R12 days, when we could use rubber hoses and clamps for refrigeration!

    Why do you think any of the copper used in refrigeration has been recycled at all? Have you seen a manufacturer claim this?

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    If it is freshly smelted from ore or melted down scrap probably has little to do with quality (other than assorted other metals alloyed in), how well you remove slag and separate oxides when you process it probably has a lot more to do with quality.
    Solid_Fuel_Man
  • ChrisJ
    ChrisJ Member Posts: 15,706
    Options
    > @mattmia2 said:
    > If it is freshly smelted from ore or melted down scrap probably has little to do with quality (other than assorted other metals alloyed in), how well you remove slag and separate oxides when you process it probably has a lot more to do with quality.

    I have a feeling metal is like water and can be recycled forever.

    I'm just curious why @Solid_Fuel_Man felt they were using recycled copper.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ratio
    ratio Member Posts: 3,627
    Options
    It's a lot harder to distill metal than water…

    :smiley:

  • JUGHNE
    JUGHNE Member Posts: 11,062
    Options
    The recycled copper and brass we sell goes somewhere. It probably can't all go to China.
    The quality control of reusing it probably varies greatly.

    As far as thinner copper coils, maybe milk a little more heat transfer to raise the SEER. And to milk a little more profit.

    I think it is all involved in the race to the bottom.
  • Stormlasher
    Stormlasher Member Posts: 1
    Options
    Ok I’m chiming in here from cape cod MA. It’s been 3 weeks now and I have condemned about 7 houses with white line set insulation. Find the middle of the pipe if accessible and stick a leak detector in there I get about 40-60% failure rate between pipes. Some of the houses are our customers some are not. I would say this do not use anymore of the white linesets (no the copper is copper the insulation is white) best of luck out there.
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    Now that they've been out there a while, has anyone seen the Rheem aluminum coils leak?
  • realliveplumber
    realliveplumber Member Posts: 354
    Options
    Only if you replaced a copper coil and reused the casing, without replacing the insulation, or installing their retrofit kit.

    It seems the aluminum coil can’t touch anything that the copper touched..

    Learned that the hard way too.
  • Ironman
    Ironman Member Posts: 7,376
    Options
    I never heard that. Am.Std./Trane is sending aluminum replacement coils where you have to re-use the drain pans and the TXV from the old coil.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Ironman
    Ironman Member Posts: 7,376
    Options
    Getting back to the line sets: we haven't heard back from the rep (hvac) about what I questioned.
    @hvac
    Rick, are you still out there?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2
  • GW
    GW Member Posts: 4,693
    Options
    No more white lines for us. I’ve bought 6500 feet of black stuff so far, and just ordered another 3280’ this morning. #savedoughbuybulk
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • realliveplumber
    realliveplumber Member Posts: 354
    Options

    Ironman said:

    I never heard that. Am.Std./Trane is sending aluminum replacement coils where you have to re-use the drain pans and the TXV from the old coil.

  • realliveplumber
    realliveplumber Member Posts: 354
    Options
    Read 3.7

    The cases coils don’t have the sheet metal shields. I tear out the old foil lined insulation and use the new insulation from the new cased coil if we don’t change the casing.
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    maybe is there someone just making the aluminum as thick as it was on those refrigerators from the 30's that are still working?
  • GW
    GW Member Posts: 4,693
    Options
    I'm unaware, what is the issue? The aluminum can't touch the skinny insulation in the cabinet, if the copper touched it?
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Options
    I'm still curious if it's the wall thickness, or the quality of the copper.

    As to my recycled comment, it's my understanding that pretty much all copper, steel, iron, etc. are recycled in mass quantities. And most of it goes to China, where, as we all know, when it comes back some is good quality and some not so much.

    In the electrical industry, copper conductors, must meet a purity standard to be sold as copper conductors. I'm just questioning what standards manufacturers have for coils/line sets. I'm sure @hot_rod can tell us that raw material quality control is something manufacturers have to keep a close eye on.
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    mattmia2
  • ChrisJ
    ChrisJ Member Posts: 15,706
    edited July 2020
    Options

    I'm still curious if it's the wall thickness, or the quality of the copper.



    As to my recycled comment, it's my understanding that pretty much all copper, steel, iron, etc. are recycled in mass quantities. And most of it goes to China, where, as we all know, when it comes back some is good quality and some not so much.



    In the electrical industry, copper conductors, must meet a purity standard to be sold as copper conductors. I'm just questioning what standards manufacturers have for coils/line sets. I'm sure @hot_rod can tell us that raw material quality control is something manufacturers have to keep a close eye on.

    I'm curious what they use as well but I highly doubt anyone would say.

    Mueller says right on their website what they use for their linesets I believe.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • realliveplumber
    realliveplumber Member Posts: 354
    Options
    GW said:

    I'm unaware, what is the issue? The aluminum can't touch the skinny insulation in the cabinet, if the copper touched it?

    Yes.
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    I wonder if the actual issue is that the copper connected to the aluminum, the steel of the furnace and ductwork, and the condensate are setting up a battery that is dissolving the aluminum tubing. I can see where the facing of the insulation or residue on it could be part of the circuit as well.
  • ChrisJ
    ChrisJ Member Posts: 15,706
    Options
    > @mattmia2 said:
    > I wonder if the actual issue is that the copper connected to the aluminum, the steel of the furnace and ductwork, and the condensate are setting up a battery that is dissolving the aluminum tubing. I can see where the facing of the insulation or residue on it could be part of the circuit as well.

    Don't know, but when I swapped the TXV in my ahu in noticed the copper tubing for it was wrapped in foam. Turns out this wasn't for insulation but to make sure they didn't touch the aluminum evaporator.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    mattmia2SuperTech
  • ratio
    ratio Member Posts: 3,627
    Options
    That page that @realliveplumber posted above said the problem is galvanic corrosion between the copper and aluminum. I suppose it wouldn't take much to cause a pinhole in Al, esp. if the copper isn't eroded at the same rate.
    mattmia2