Imagine That
They installed the new boiler and suddenly a condensate tank was required to return the condensate.
I wonder why....
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com
STEVEusaPAmattmia2HVACNUT
  • JUGHNE
    JUGHNE Member Posts: 11,546
    Nice blocks.....cheaper than extending risers! :o
    EBEBRATT-Ed Member Posts: 20,065
    Maybe they didn't want the flood water to fill the boiler!!!
    pecmsg Member Posts: 7,020
    My knees say thankyou for raising it up that high.
    JUGHNEBobC
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,529
    You’d think the pit would have caused them to contemplate a bit...
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,919
    I notice the p'trols aren't protected from steam. Wonder which one will fail first.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • ChrisJ
    ChrisJ Member Posts: 17,282
    People often say that, but...
    How can steam get to them?
  • STEVEusaPA
    New boiler and kept the ancient burner?
  • Hap_Hazzard
    Convection.
  • ChrisJ
    > @Hap_Hazzard said:
    > (Quote)
    > Convection.
    Steam doesn't fill voids via convection.
    I'm betting the Ptrols on the ends will stay cold. The one in the center not sure about, it's kind of close.
    My own boiler has two sets of controls, the ones I actually use and care about do not have a pigtail or trap of any kind. Just 18" of vertical pipe with air trapped in it. It gets hot maybe a few inches up and that's it. Most of the 1/2" black iron pipe stays room temp
    mattmia2 Member Posts: 16,412
    i guess that is one way to raise the water line...
  • Hap_Hazzard
    Really? I seem to recall a few weeks ago people were trying to convince me that my dry return was filling with steam even though it's full of air and pitched downwards, so, apparently, steam can overcome gravity AND an air-filled void to travel some 20 or 30 feet downhill back to the boiler, but it can't rise a few inches to reach the pressuretrol? Fascinating.
    edited March 2020
    I meant back in the day when it was initially installed. It’s not new any longer.
    I am sure the condensate tank wasn’t in the bid.
    STEVEusaPA
  • ChrisJ
    Was I one of those people?
    Wonder if they buried the old boiler under that??
  • retiredguy
    retiredguy Member Posts: 1,086
    Was the old boiler an old coal unit with a very large steam chest with a very large water content that steamed much slower than the newer boiler?
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,315
    I also like that jacked up 67.... and no blow down for the lower piping to keep it clear.