I am working on a project where we would like to run threaded gas pipe up through an egress stairwell to the roof and then back down a multi fireplace chase to each fireplace. The building is a 7 story concrete structure.
I realize that there a millions of local codes that can be considered. I am working out of the 2018 IBC, IMC, and IFGC.
I am looking for actual code sections that allow or disallow this installation.
Thank you in advance,
Carl
Carl
Albert Einstein
Albert Einstein
It's a little early in the year for crickets
Albert Einstein0 -
You kind of jinxed yourself tbh: I realize that there a millions of local codes that can be considered.
I don't have a copy of the code book handy, but Minneapolis code allows schedule 40 steel, type L copper, or CSST in any indoor gas piping installation (threaded or welded steel joints, flared or brazed copper joints) UNLESS it runs through a return air plenum, which cannot have any joints unless welded steel or brazed copper.
If I were doing that job, it would be all sch 40 black through the stair, galvanized or painted sch 40 steel on the roof, with a brazed copper drop through the chase.
No, it's not what you asked for but it may be useful in some way.0 -
Through a building is one thing
In an Egress Stair I don't think its going to fly!0 -
I have read my local code amendments and it is not addressed. Therefore I am trying to limit the conversation to the 2018 IBC, IMC, and IFGC. As hotrod mentioned, I may need to dig into the dreaded NFPAethicalpaul said:You kind of jinxed yourself tbh: I realize that there a millions of local codes that can be considered.
Albert Einstein1 -
What's a "multi fireplace chase"? A flue that served multiple fireplaces or an actual chase? If there are going to be gas connections to the fireplaces (for like gas logs) is that chase going to be the vent space? If that's correct I would imagine no code would allow the gas supply in sounds like effectively the venting flue.0
@BobHarper
You are correct, the AHJ sent me to this:
713.8.1 Prohibited Penetrations
Penetrations other than those necessary for the purpose of the shaft shall not be permitted in shaft enclosures.
I believe they are going to allow it mostly because we are tearing out unsafe wood burners.