Lochinvar boiler pump
ultra
ultra Member Posts: 8
I have an older lochinvar boiler and it works great but the pump runs continuous. I have wiring But it does not show a timer or a delay. Does anyone know if there is an aftermarket one I could install so that the pump would shut off after so many minutes once the water has reached temperature
  • Ironman
    Ironman Member Posts: 7,849
    What model do you have? Can you post some pics including the controls?
    Bob Boan
  • delta T
    delta T Member Posts: 884
    Is this the variable speed pump that ships with the boiler? Need some more info, likely either connected incorrectly or there are control settings that need changing....
  • Zman
    Zman Member Posts: 7,611
    @ultra
    Lochinvar makes a lot of boilers with even more ways to control a pump.
    Can you post a picture of the boiler including the terminals that the pump in question is tied to?
    Albert Einstein
  • ultra
    Rbn 500.
    There is nothing in control panel.
    Flow switch, high limit, operating limit, transformer, I just put a pump relay in and the ignition module
  • delta T
    edited February 2020
    I'm curious why you want to do this? Are you trying to turn the pump off mid cycle once the water temp is reached (but during a call for heat), or does the pump run all the time, and you want to shut it off between calls for heat?
  • ultra
    The pump is running 24 /7 when I have power to the unit. What I want to accomplish is after the heat cycle is completed I would like the pump to turn off 3 to 4 minutes after. And then when the temperature decreases and it’s called for heat it will turn back on
    hot_rod Member Posts: 26,538
    The pump should run after the burner is off to purge that heat and prevent running to high limit
    Shop for a time delay relay, delay on off cycle
    Looks like a relay inside us disconnected? What does the boiler wiring diagram show?
    delta T
  • ultra
    According to Lochinvar they have a post purge relay that will let the pump run for 30 seconds after the burn is done. I want something to run longer than that. There weren’t any wires disconnected. I just took a picture of it that way because I’ve been playing with other timers trying to get it to work
    ultra
  • ultra
    I ordered a delay timer on line today. I’ll see if that works but I’m not hopeful at this point
    Looks like a batch DHW boiler?
    If so is that tank the only load? Seems like a lot of hp, short cycling and over shooing temperature?
  • ultra
    It is in a car wash. The water is used for undercarriage, all soaps and wax and some for rinse. 1 storage tank . Yes the circulation is just the holding tank and unit.
    a time delay relay should help. There are different types, I think you want one that keeps the contacts closed after power is removed from the coil, not just an intermittent break.
  • Zman
    I have met engineers that swear your setup should run constant circulation to keep the tank mixed.
    I don't agree and recommend what you are proposing. You will get more tank stratification and you may need to move the tank sensor. You may not have a tank sensor and may be running off the boiler aquastat.
    Albert Einstein
    When those copper tube boilers age they tend to scale the tubes. Then when the burner goes off the overshoot, sometimes kicking limit switches. You may need to descale it at some point also
    Large pumps and high velocity helps scrub the tubes, compared to heating boilers
    ultra