GPM, is this going to be a problem?
JackW
My boilers BTU/h specs. are 15,000 min and 120,000 max. If I did my math right that's 1.5 gpm min and 12 gpm max. My manifolds max gpm is 1.3, is this going to be a problem?
Thanks,
Thanks,
The boiler will have a minimum flow rate through the HX listed somewhere in the manual, Usually upwards of 4 for a 120k unit but yours may be an exception- what model boiler do you have? The majority of mod con boilers are supposed to be piped primary secondary to maintain proper flow across the HX while allowing whatever flow is necessary through the loads with the hydraulic separation created by primary secondary piping. I'm guessing the 1.3 GPM mentioned is "per loop" of your radiant manifold, how many loops are in your smallest zone and how long are they, in what size tubing?1
My system is a two zone layout. Zone 1 is 30'x30' with 4 circuits of 1/2" pex, 229'-230'-230' and 229'. Zone 2 is 15x30 with 2 circuits of 1/2" pex, 212' and 214'.
The Boiler is a Hydro Smart 120 Condensing Gas Micro Boiler.
BTU/h is 15,000 min. - 120,000 max.
The manifolds are Rifeng 3 and 4 loop manifolds. The supply side is 3/4".
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Rifeng-RHM04-User-Guide.pdf0 -
Your are talking about this setup, correct? https://forum.heatinghelp.com/discussion/172466/rough-layout-design-input-please#latest
With primary/secondary piping, the manifold flow rate is not an issue."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
DZoro what does that mean? Is that a good thing or a bad thing?
Thanks.0 -
Thanks Dzoro I'm glad to hear that. I hope post a picture of what I've done so far for critique. Appreciate your help.0
Thanks hot_rod I appreciate your input. Good to know.0
The thumb screws at the top of automatic air eliminators are to be open at least 1/2 turn. If closed ... no air will be released.
The reason for the cap is when they fail... if the float fails to completely close the air vent... you can close the cap (thumb screw) to stop the leak until such time as you can repair or replace the leaking air vent valve.
Since you do not have a dedicated water feed line to constantly add water as air is vented over the course of the first few weeks of operation, you will want to closely monitor your water pressure. if there is any drop in pressure that results from venting air, you will need to replace that with something (like water).
This system looks professional! Nice job! I don't see a Low Water Cut Off... Since this boiler requires the activation of a water Flow Sensor to initiate the burner ignition cycle, is there a need for a LWCO? Thoughts anyone?Edward Young Retired
Thanks @EdTheHeaterMan, I'll keep an eye on the water pressure. I'll also keep an eye on the thread concerning a LWCO. I thought that is what the flow sensor would do.
Thanks for the compliment.
@hot_rod I threaded and bent a 3/8" HR rod that's just to the right of the tank, you can see it coming out from the wall. If I need to support it from underneath I will, let me know. Thanks.
@JackW Looks good. I've seen a lot of "professional" jobs that would not measure up to your quality.
Do you have a condensate neutralizer?
I think this system will work very well for you. I bet you can run your boiler pump on low speed and still feed both zones.1 -
@Jolly Bodger Thank you I appreciate the compliment.
I am running the circulators at low speed, my manifolds are set at .8 gpm and the boiler is running at 2.33 gpm, don't know if that is a problem or not.
I don't have a neutralizer, is neutralizing the acidic condensate important?0 -
@JackW , .8 gpm per manifold or .8 gpm per loop? Not that it makes much difference. The primary secondary piping you have provides you hydronic separation. This way your zones and your boiler can run different GMPs without a problem.
Neutralizing the acid is important depending on where the drain is going. If you have any cast iron pipes or it is going into a sepic system I would recommend it. Does not have to be fancy.1 -
@Jolly Bodger it's .8 gpm per loop. I can run it up to 1.3 gpm if needed. I just got it running today and at this point everything seems to be working well. Is there a way to tell what it should be?
I don't have any plumbing in my building so right now I just have it going into a small bucket. I might look at plumbing it outside later but for now I'm going to leave it as is. I went ahead and ordered a neutralizer anyhow, want to make sure everything is done right. Thanks for your help.0 -
@JackW GPM per loop is dependent on loop length, spacing, supply water temp, BTU output needed of the slab. You can do a simple test to dial it in. Get the system running and stable. measure the temp going out to a loop and the temp coming back. Adjust the GPM to about 10 degrees Delta-T. .5gpm is common for 1/2" PEX.1
> @JackW said:
> Thanks@Hot_Rod. I have it set at .8 now I'll dial it down a touch and see what happens. @Jolly Bodger suggested that I measure the Delta_T of a loop and dial it in that way.
The delta t in a system changes based on the load, the flow rate is a constant number you see and set. Expect to see a wide delta on start and narrowing as the room approaches set point, regardless of what delta you designed for, it will and should move around a bit to best match the changing load conditions.
Trying covering the load at the lowest possible settings, flow rate and SWT if you are chasing best efficiencyBob "hot rod" Rohr
Living the hydronic dream1 -
Yes open the ports where the actuators attach. Then adjust flow by turning the flow meters. Some of the flowmeters have locking rings that need to pop off first. Good to adjust them sooner than later as those plastic windows tend to get dirty and hard to see the float insideBob "hot rod" Rohr
I love this thread. Such neat craftsmanship
I don't see a Low Water Cut Off... Since this boiler requires the activation of a water Flow Sensor to initiate the burner ignition cycle, is there a need for a LWCO? Thoughts anyone?''
My W-M Ultra 3 boiler says its controls are such that no LWCO is necessary, but my contractor put one in anyway because the AHJ around here insists on it.0 -
> @JackW said:
> @hot_rod I took these measurements at the manifold.. The SWT at the manifold 98 degrees, the RWT is 78, I have the manifold set at .8gpm. That makes the Delta-T a 20 degree difference, if I'm understanding this correctly. So is that a good or bad thing?
If you are warm and comfortable, that’s a good thing☺️Bob "hot rod" Rohr
It's all down to a complex selection method that takes into account tube spacing, btu/ft2 demand, SWT, circuit length, and final flooring selection. My systems are designed for 90 SWT, 10 Delta-T, and .42 GPM per loop. your system may be designed Different.
Low RWT makes your boiler more efficient but may make your floor uneven or fall behind in cold weather.
This is where you can play with it.
Hot_Rod is right. As long as your comfortable it is working0 -
@hot_rod and @Jolly Bodger yes the rooms are very comfortable. The floor is warm, the room is warm and the circs shut off when the set temperatures are reached.
When is the difference between the SWT and the RWT too much? I would think if your boiler is putting out enough heat and once the slab heats up that there shouldn't be to big of a difference between the two.0 -
Page 20 talks about delta T in a circuit, how and why it varies https://www.caleffi.com/sites/default/files/file/idronics_23_na.pdfBob "hot rod" Rohr
- 87.8K THE MAIN WALL
- 133 Chimneys & Flues
- 79 Pipe Deterioration
- 396 Solar