Electrical? What's this
CBRob
Member Posts: 283
I'm guessing it is sone sort of delay switch?
It's in a enclosure box along with a 120-volt relay that goes to the zone switch relay. When I turn off power to the boiler and it's components it seems to take an extra three or four minutes before the boiler powers back up.
Triangle two boiler, SR50110 switching relay
Looks like a time delay relay.Bob Boan
Solid state time delay relay.
May have been put there due to frequent short term power outages.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
Thanks guys.0
Probably a delay on restart, will start normally but if powered down will not restart for perhaps 5 minutes. Prevents short cycling. Often built into stat for AC protection.
Then there is delay on start, during normal operation if called to start there will be a delay for starting. Power companies like these as it staggers the starting load during a power outage of more than 5 minutes.0 -
The MCBA3 series controllers had trouble with brownout conditions. Triangle tube had a service bulletin for this delay-on relay fix.JUGHNE said:Probably a delay on restart, will start normally but if powered down will not restart for perhaps 5 minutes. Prevents short cycling. Often built into stat for AC protection.
Then there is delay on start, during normal operation if called to start there will be a delay for starting. Power companies like these as it staggers the starting load during a power outage of more than 5 minutes."If you can't explain it simply, you don't understand it well enough"
Albert Einstein3 -
I remenber seeing a delay like that used on a triangle tube the owner said they installed for when the generator was running said it some how steadied the hertz out and prevented the unit from getting a error code ,but I had also seen some one do the same thing using a small resistive load like a small ceramic heater to give a small load on the generator to stead the hertz made sense to me but I have seen that same elsewhere Peace an$ good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1 -
Ahh
I was having a oh **** moment when I turned the boiler back on after s small repair.0 -
- 87K THE MAIN WALL
- 112 Chimneys & Flues
- 106 Geothermal
- 980 Plumbing