Boiler short cycling and problematic radiator
Comments
Are there any main vents on the steam pipes in the basement? You would find them near the end(s) of the steam main(s), after the last radiator takeoff. if so, what are they? If not.. there's more than half your problem with the cycling on and off.
The piping right in the area of the boiler ("near-boiler piping") isn't what it should be in several respects -- as I'm sure others will notice -- but I think we can let that go with a nervous laugh for the moment.
That is one big radiator. I suspect -- and will wait for your comment on main vents -- that the real problem, though, is that the other radiators may have slightly bigger vents than are really needed, starving that one of steam until they are all closed. However, without main vents -- or with inadequate ones -- there's no point in working on that. In the meantime, make sure that that one problem radiator is pitched slightly to the inlet end, and that the valve is fully open, and that the pipe in the basement feeding it has a good slope back to the main.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
Side outlet boilers are very sensitive to the piping, and generally need both risers installed.
The water looks a bit dirty in the sight glass, and so a good drain and refill could remove any chemicals which may have been put in to clean the boiler, as a substitute for skimming. Skimming is best if you can find a suitable outlet.
A low pressure gauge, (0-3 psi), Tee’d off the Vaporstat, would enable you to be sure the vaporstat is properly calibrated.
Check the main vents on the dry returns to see if they are adequate. Generally, a Gorton #2 is good for 20 feet of 2 inch pipe. The radiator vents need to be more restrictive, like Hoffman 40’s—NBC
You should have 1 on each main leaving the boiler,
perhaps at the ends.
You have some piping issues in the basement, but start with the steam main air vents.
I will look in to adding a low pressure gauge next to the Vaporstat and draining the water in the radiator.
The one to the right looks like a parallel with a dry return.
(The steam and condensate water are flowing in the same direction and all the condensate returns thru the smaller pipe sloped back to the boiler)
Is this the case for the steam mains?
The main air vents should be at the end of the mains or where the return drops down to the boiler.
Which main has the offending rad connected?
So tell us what the other vents are and check for main vents and any possible place main vent might have been in the past.
Bob
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge
either that glass is dirty, all the way,
or the water level is up past the top, too high, and neds to be drained to 2/3s glass, or that line on the boiler.
what do you see at the boiler?
or are you filling manually?
I see the water line now,
and I see the fill level marked on the boiler jacket,
no need to be above that line, nor desirable,
above that line is so close to the steam riser outlets that you're boiling is carrying water out with the steam,
the dirty water is contributing to the carry out also,
drain the boiler again, WHILE IT"S COOLED,
and refill again, WHILE IT"S COOLED, only to that marked water line,
Take advantage of that drain by the make up water line, where it meets the condensate return, you'll get ugly water from both the boiler, and the return line there.
and yes, you can see clean water, when you get there,
I think the boiler is just loaded up a bit, and can stand for a couple drains and fills,
and or a skimming also, do you see a skim port, I don't.
Does the water line bounce much in the sight glass when the boiler is firing?
more than an inch , or violence, is too much,
again, dirty water, and skimming as a solution.
you don't want high pressure, under 1 is good,
no need for 1-1/4, 1-1/2, or higher,
low = good, lower = better,
post a picture of your pressure control showing its settings,
finally, that rad, does that vent, vent ?
is it working?
might just need a faster vent there.
however, the active sight glass begs for skimming,
dirt and oils on the boiler water surface make the little steam bubbles angry,
skimming removes that surface layer,
you can search here for other threads on skimming, or,
that high brass hose bib valve on the back is as close as you're going to get,
ideally that reducing bushing would be a full size nipple, capped or valved, for better cross sectional water flow as you skim there, but that will work, just take longer.
You can't really skim thru that valve,
ideally, remove that valve, and add a short nipple, (and cap),
the valve restricts flow pattern, and makes it darn hard to be sure of the water line*, as that valve is constructed to turn down,
A nipple is easier to look into, and determine that precise fill setting, and flow rate, to optimize your skimming,
the cap closes the nipple when you're done.
*If the water level gets above the height of the nipple (valve) then the oils floating on top can't get out, so water level here is critical.
So, with the boiler off, remove that valve, add your nipple, and let it drain to your bucket,
the nipple (valve) is above your normal water line,
so you will open, ever so slightly open, the water feed, so you only allow a slow trickle out of the nipple, (high valve), the oils and scum on the top of the water will flow out this way,
this will take a while, hours, of painfully slow and precise filling, you want the water flowing out thru only half the cross section of the nipple (small valve),
You can also manually fire the boiler while skimming to warm / heat the water.
You're turning the service switch on, and off, you don't want to get to boiling, just hot, not steaming.
When you feel you're done, set the water level back down to that line on the boiler jacket, no higher.
Skimming can be a multiple session activity, you'll know your good when the sight glass stays calm,
or as a cool trick science project,
take some of that first skim water, and go boil it in your wife's least favorite pot, it will be all frothy.
then as you're a hour or 2 into it, boil another pot, less frothy.
Same thing is happening in the boiler.
and yeah, I don't see any main vents there either,
that problem radiator, is it close or far from the boiler?
the safety valve above the skim valve,
it should be mounted with the valve stem vertical,
less chance for crap to jamb or get stuck under the valve disc and seat if it was to open,
I think I see that you could reuse the fittings and parts there to get to proper orientation.
Vaporstat settings look,
the pigtail under it needs to be checked for clean and clear
(yearly) but the boiler isn't getting over your settings so you're good there for now.
As far as your suggestion to add the nipple, could you show me on one of the pictures where exactly you mean? My current understanding is that I should remove the red valve on top of the sight glass?
Regarding the safety valve, this is what you are saying should be vertical?
The large, problematic radiator is probably the closet or second closet to the boiler. I think this pipe runs directly to it? The radiator is on the front wall of the house on the ground level, boiler is roughly in the middle of the house.
The garden hose bib up high on the left side of the boiler would be your skim port.
You need to remove the hose bib, if any reducer bushings come out with it so much the better.
Put about a 4" pipe nipple in that port, add a 90 to point down and another 4" nipple to direct water to the floor. Get a cap for that pipe size for when you are done. The hose bib will not flow water correctly for skimming.
Follow the instructions for skimming as above.
You are trying to float oil off the top of the boiler water, this has to be done slowly so as not to mix the oil and water.
Draining your boiler from the bottom might seem to clean it, but the oils will cling to the internal walls inside of the boiler and when you fill it again the oil is washed back to the top.
The pressure relief safety valve is on the top left rear corner of the boiler. That device should be such that the lever with the pin is on the top of the fittings. You want to keep the bottom of it down so as not to get junk under the sealing seat.
Then the discharge would point towards the rear wall, you need a nipple to clear the boiler jacket and use the 90 to point down.
It should then be piped to with in 6" of the floor.
If you read the tag/label on it, it should indicate 15# of pressure.
If it opens it will pass steam at that pressure and you need to direct it down to the floor. That looks like a plastic drop pipe on it now. Should be black pipe or copper. No threads on the lower end.
Leave the right side of the boiler alone for now.
I think we may be making progress here because there is a definite improvement after just draining the boiler, and skimming sounds like it will only help matters.
While the safety relief valve should be corrected, am I safe in assuming it's not contributing to my problems at the moment? The tag on the back does indeed say 15psi.
Easy fix....2 pipe wrenches needed....minimum of 14" long.
Economy ones will work OK until they don't.
Unscrew the drop pipe, unscrew the relief valve from the horizontal nipple, unscrew the 90 from the boiler nipple.
Do not loosen the boiler nipple.....the reason for 2 wrenches.
Make sure the boiler nipple is clear, install the relief valve so it is pointing to the wall. The nipple in the 90 might be long enough to go into the valve with the drop pipe pointing down. Replace the drop pipe if it is plastic with black pipe length you buy at a big box store. Threaded on one end only, reamed on both ends.
Is your troublesome rad the last connection on the left main??
I believe the rad in question is the last on the left main. Looking at the piping it almost seems like it could be the only radiator on that main. It does seem to be working somewhat better after the multiple drains I did, but is definitely slow to heat up still.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
it doesn't need much,
but it should pitch back to the supply valve.
Does that vent get hot, and close to steam ?
and do you hear air releasing prior?
I'll pay attention tomorrow when I run it again but haven't heard much venting with the system at 1psi and a Gorton 4/5 on it. It does eventually heat up but it's very noticeable that the right side is heating up first and slowly. I'll check how level it is tomorrow as well. Interestingly it seems to be the only one in the house that isn't propped up on the far end, and it's also the only radiator of that style.. the rest are silver color.
Once I get the boiler properly cleaned I'll revisit the vents on all the rads. Are rads only affected by incorrect vents from others on the same main?
What diameter and how long are your mains? The main venting before any radiator issues should be addressed.
Sorry I also forgot to mention @nicholas bonham-carter and @BobC were also going down the main venting track as well.
@Nurb that radiator is not suffering from lack of pitch or sag. If you don't vent your mains steam can't reach your radiators evenly. Main vents should be placed 18" back from where your dry returns drop to wets or after your last run out leaves the main and be on a nipple at least 10" high. I recommend Barnes and Jones Big Mouths, biggest bang for the buck and great quality.
Venting the mains should also reduce you short cycling significantly. You should be able to set the vaporsat at 1psi or lower, my system runs at 12oz cut out 4oz cut in.
Depending on were your are located there should be a good contractor on here that can help you out, Check find a contractor.
Can you post a photo of the side of that radiator? Also the height from the floor to the top. The valve looks like it says "1 1/4" on the side from the photo. Can you verify?
There's a chance that radiator is just too big for it's connection, which could be contributing to the problems it's having.
18 Ounce per Square Inch Gauge
Time Delay Relay in Series with Thermostat
Operating Pressure 0.3-0.5 Ounce per Square Inch
The problematic radiator is 19" tall, to me it looks like there was a repair previously on the top.
As far as installing main vents, do you just drill and tap holes in the mains?
The header is so low, especially for a single-fed side supply, I expect a ton of water is getting into the main
From the look of it that radiator doesn't appear to be the original with all the new plugs, etc. Do the other radiators in the house look similar in terms of design and dimensions? The connection is the right size, though. So that's not the problem.
Although, compact radiators like this tend to not work well with steam. They don't have much internal volume or wide internal spaces for the steam to move uniformly through. The steam generally races along the bottom over to the vent instead of heating along the top, or they heat up unevenly.
18 Ounce per Square Inch Gauge
Time Delay Relay in Series with Thermostat
Operating Pressure 0.3-0.5 Ounce per Square Inch
and should be thought about, and installed.
Was it ever decided that saddle clamps were steam compatible?
or does Nurb need to break into his mains?
Now take another look at the basement pictures,
it seems the main is relatively small(not that venting won't help)
and that there are rather long(ish) runouts to the rads,
The newer problem rad is boiler close,
either it isn't venting fast enough,
or is it venting too fast, and the steam is shooting across and closing that vent, too soon?
Nurb, Does that vent get steam hot?
and if it does, is it before, or after the rad finally heats?
As the boiler fires, how long before the other rads start to heat up
Why no main vents? in the days of slow steady coal fired boilers the air would get slowly pushed out of the rad vents and maybe stay out most of the season. The dead men who installed your system may have cut their teeth on coal boilers....or the entire system was repiped by someone who didn't know better.
IIWM, I would not use the BJ Big Mouth main vents; although the biggest and best, they may spit water in your system.
Your boiler piping is such that you probably are delivering wet steam. Especially on the left counter flow main that is not dripped anywhere.
Gorton #2's would be enough IMO.
1 on the left main and 2 on the right dry return at the end of steam main.
A 1/4" tapping for each would suffice for each vent.
The G2's have 1/2" threads. You will need reducing couplings.
Be sure to get a 1/4" NPT ....National Pipe Thread.....tap.
And the correct drill bit for that tapping. Drill on the top of the pipe. At least 6" from a fitting and 6" between multiple taps.
Use a minimal amount of cutting oil as this will have to be skimmed out of the water afterwards.
The vents must be as vertical as possible.
On the left main you may have to add swing fittings to get the vent vertical. You could try without, might not be a problem.
On the annoying rad, it looks to be a replacement.
They may have pushed the riser with the valve on it down to line up the rad valve spud. You could try raising the valve end up 1/2" and the vent end up 3/4", this might correct the sag under the floor that you cannot see. You could add 1/4" shims as needed.
If this eventually solves the problem you could come up with better looking wood risers.
You well may be beyond the pipe size and length minimums for that size of rads. I have a couple of them in a church and with the slowest air vent on them they keep under control.
Here are the rest of the radiators in the house, they all work well (although a couple have noisy vents)
[Downstairs]
Second largest radiator and closest to thermostat (problematic radiator is larger and a few more feet from the thermostat).
Needs a new valve cap
[Upstairs]
There is another of these thin radiators not pictured.
Even today I have only seen brass goods made in Thailand, and they are surprisingly of fair quality about matching Taiwan materials....but better than Chinesiem materials.
But some of your steam piping in the basement, the main pipes and runouts....not just at the boiler....was from Thailand?
There may have been some main air vent taps that someone had just put plugs into and the next pipe fitter just left out those tees.
As Dan has said in his books......"plugs are a lot cheaper than vents"
Look above in the store for books.....We Got Steam Heat and The lost art of steam heating......well worth the money for you.
> Thanks, Is this what you're referring to when you say header?
Yep
I was also able to sort out the LWCO needing an artificially high level by cleaning up the probe. Now on to the skimming and main vents install.